Not to highjack the thread, but for the guys that do (have done) this for a living, when calculating distance for voltage drop, is it linear distance from source panel, or do you double that for the length of the circuit?
You dont know what your talking about. Each leg carries 30 amp.When running 240vac the current load is shared by both hot legs so factor that into your wiring choice. For example if welder pulls 30 amps each leg supplies 15 amps so wiring can be determined by that and wire run length.
wire it and use welder for 240vac and forget about using it with 120vac IMO.
39? Typo?You dont know what your talking about. Each leg carries 39 amp.
nothing like the internet to pass on wrong info.
I was going by the Cerrowire chart.
I’d use 6 ga in Romex, but if I’m reading the chart right, I could use 8ga 90C THHN in EMT up to 55 A. Wouldn’t run a continuous load like a Tesla charger off 8ga, though
Copied and pasted from the bottom of the chart in the link.I was going by the Cerrowire chart.
I’d use 6 ga in Romex, but if I’m reading the chart right, I could use 8ga 90C THHN in EMT up to 55 A. Wouldn’t run a continuous load like a Tesla charger off 8ga, though
Thanks. I have an older copy of the NEC. Be interested in the 60C citationCopied and pasted from the bottom of the chart in the link.
WARNING! Installation of electrical wire can be hazardous if done improperly, and can result in personal injury or property damage.
For safe wiring practices, consult the National Electrical Code ®, your local building inspector, or a qualified electrician.
#8 THHN is only rated for the ampacity in the 60°C column due to a code requirement in article 110 of the NEC. It would be good for ampacity of up to 40 amps according to the ampacity table in the attachment.
Be safe!
Thanks! I see where you’re coming from. I always thought “equipment” terminations applied to stuff like pumps, motors, etc. I took that into account when I had to upsize my wire to my irrigation pump due to high ambient temperature and the temperature rating of the terminals on the pump.From the 2020 NEC the section you would like to look at in article 110.14.(C) is titled "Temperature Limitations".
Also, along with article 110.14.(1) titled "Equipment Provisions".
You will want to flip between the "Equipment provision" section and the Ampacity Tables at article 310.16 and pay attention to the columns of "temperature ratings for conductors".
Good point! I looked up the specs on the 6-50 outlet (Leviton IIRC but might have been Hubble) and it was 75C. Other ones from Home Depot, Lowes, Amazon may not be 75C rating so you do have to check! Same with the breaker!Unless the termination point has printed 75c rating stamped on it, you have to assume its 60c rated.
it is not the welding heat that is the issue it is the resistance of the wire in combination with the thermal insulating/conduction of the insulation. welders are not as big of an issue do to the fact that most do not support 100% duty cycle (duty cycle for a welder is the percentage of time in a 10 min window that the welder can perform at a specific load, most being 60% or less at full load so most circuit breakers are 80% rated leading to some engineering margin.Thanks! I see where you’re coming from. I always thought “equipment” terminations applied to stuff like pumps, motors, etc. I took that into account when I had to upsize my wire to my irrigation pump due to high ambient temperature and the temperature rating of the terminals on the pump.
So I was thinking that a receptacle that’s 6’ away from a heat source like a welder would be rated on the temperature of the receptacle (=ambient as long as the connections are properly torqued) vs the connection of the power cord to the welder, which would get hot. But hopefully the manufacturer took care of that
I didn’t wade through the whole chart in 310.16, but at least for 8ga wire, it looks the the Cerrowire chart. Not looking at it right now, but I don't think the Cerrowire chart accounted for ambient over 86F. I try to avoid welding any time it’s over 86F, but I’ll ponder that
Interesting stuff. Terminal temperature might explain some of the the code stuff around hard wired EV chargers, cause for sure they’re “equipment” and all that power conversion magic is bound to generate some heat
Thanks again!
This particular Lincoln 50 amp welder has a 20% duty cyle. The instructions below say to use 10 ga wire with a 50 amp breaker. I looked at section 630 of the NEC, and that’s allowed because of the arc welder duty cycle adjustment. Would be a disaster waiting to happen if an EV got plugged into that installationit is not the welding heat that is the issue it is the resistance of the wire in combination with the thermal insulating/conduction of the insulation. welders are not as big of an issue do to the fact that most do not support 100% duty cycle (duty cycle for a welder is the percentage of time in a 10 min window that the welder can perform at a specific load, most being 60% or less at full load so most circuit breakers are 80% rated leading to some engineering margin.
EV chargers are not subject to this and operated at rated power for hours on end so a 50A EV charger outlet is a lot more serious than a 50 welder outlet