welder circuit

/ welder circuit #1  

arrow

Super Member
Joined
Dec 15, 2002
Messages
6,256
Location
Wakefield, RI
Tractor
Mahindra 3016
I have two welders. Both small because of the lack of any appreciable service out to the garage. Both welders (one stick the other wire feed) are rated for 140 amps.
I have 10/2, 30 amp 220 circuitry there now.

The small, flux core wire feed I recently acquired has only a 115 plug (daughters pitched in for Christmas and did the best they could) but the 140 stick has a 50 amp terminal end.

CAN I BETTER THE MIG/FLUX TYPE WELDER THAT FITS THIS ELECTRICAL PROFILE THAN WHAT I CURRENTLY HAVE OR AM I STUCK AT 140 AMPS? Most welding done with 1/4" metal with occasional 3/8"-1/2" that the stick can handle. It was good enough to weld a 1" thick splitter wedge on w 1/8" 7018.

What is the limit to wire feed welder amperage output on a 30 amp breaker 220 circuit?
 
/ welder circuit #2  
I have two welders. Both small because of the lack of any appreciable service out to the garage. Both welders (one stick the other wire feed) are rated for 140 amps.
I have 10/2, 30 amp 220 circuitry there now.

The small, flux core wire feed I recently acquired has only a 115 plug (daughters pitched in for Christmas and did the best they could) but the 140 stick has a 50 amp terminal end.

CAN I BETTER THE MIG/FLUX TYPE WELDER THAT FITS THIS ELECTRICAL PROFILE THAN WHAT I CURRENTLY HAVE OR AM I STUCK AT 140 AMPS? Most welding done with 1/4" metal with occasional 3/8"-1/2" that the stick can handle. It was good enough to weld a 1" thick splitter wedge on w 1/8" 7018.

What is the limit to wire feed welder amperage output on a 30 amp breaker 220 circuit?

That's a bunch of information but it doesn't help answer your question " What is the limit to wire feed welder amperage output on a 30 amp breaker 220 circuit?" The limit is clearly printed on each welder. EXACTLY what make and model are you asking about?
 
/ welder circuit #3  
Really need a 50A 220V circuit to step up to much.
 
/ welder circuit
  • Thread Starter
#4  
That's a bunch of information but it doesn't help answer your question " What is the limit to wire feed welder amperage output on a 30 amp breaker 220 circuit?" The limit is clearly printed on each welder. EXACTLY what make and model are you asking about?

Not sure Jaxs.
Right now I'm thinking that any welder is better with 220 than 115 whether it stick or wire feed.
Don't know enuf about the various machines.
I read on a review of the Lincoln 180 mig that it uses 20 amps but a 40 amp breaker is necessary with full amp usage. This was a review so who knows. I don't know what happens if I use this type of welder say at 150-160 amp limit.
Got me to thinking thus my question to the more informed.
 
/ welder circuit #6  
The modern 211 class machines use 30A service
A 10/30 is tailor made for them.
 
/ welder circuit #7  
The modern 211 class machines use 30A service
A 10/30 is tailor made for them. The manuals are confusing at best.
 
/ welder circuit #8  
Ok,so what you want to know is how many welding amps can a 220v-30a breaker deliver? First off understand most if not all hobbiest,farmer,homeowener type 220v wire welders come with a 50 amp plug from the factory although some pull less than 15 amps. Since you want to push all the amps possible off the 30a breaker,I reccomend a Hobart Ironman. The latest version is Ironman 240 which has max output of 280 amps pulling 38amps 220v. The Ironman 230 pushing 250amp while pulling 32amps 220v can still be found in stores and used. Those numbers are balls to the wall max output. You can run either up to about 240 amps off your 30a 220v breaker. One day when you have 50amp service you will own a top notch machine without trading up. The rage right now is 120/240v machines that cost extra for multi-volt option. I say put all the cost toward welding capabulity instead of the 120v option that will see little to no use. Just buy the welder you would like to have and limit amps to around 240 until you have 50 amps available.
 
/ welder circuit
  • Thread Starter
#9  
Ok,so what you want to know is how many welding amps can a 220v-30a breaker deliver? First off understand most if not all hobbiest,farmer,homeowener type 220v wire welders come with a 50 amp plug from the factory although some pull less than 15 amps. Since you want to push all the amps possible off the 30a breaker,I reccomend a Hobart Ironman. The latest version is Ironman 240 which has max output of 280 amps pulling 38amps 220v. The Ironman 230 pushing 250amp while pulling 32amps 220v can still be found in stores and used. Those numbers are balls to the wall max output. You can run either up to about 240 amps off your 30a 220v breaker. One day when you have 50amp service you will own a top notch machine without trading up. The rage right now is 120/240v machines that cost extra for multi-volt option. I say put all the cost toward welding capabulity instead of the 120v option that will see little to no use. Just buy the welder you would like to have and limit amps to around 240 until you have 50 amps available.

Solid answer Jaxs and is in the realms I was looking for.. Never thought I could run that big a welder. Thank you.

One other thing: It states its a 230v and in one of the reviews, it makes reference it is not for a typical homeowner but more for a shop because a regular homeowner type electrical system won't push 230v.
What's up with that?

Even the Hobart 190 states it's a 230v machine and that's meant for a hobbiest no? I thought 220/230/240 was kind of the same thing.
 
Last edited:
/ welder circuit
  • Thread Starter
#10  
The modern 211 class machines use 30A service
A 10/30 is tailor made for them. The manuals are confusing at best.


Sberry you talking like a 211 Miller here?
 
/ welder circuit #11  
Yes, a 211 falls in this class. It was explained why they still use 230 on the listing but I forget why at the moment but we use 120/240 in this country. I got to look at the IM230, don't recall the wire size. If it's a dedicated circuit, not shared with a dryer 10 can run many welders that require 50 breakers. There is allowance for it. Millions of them legal wired by masters for decades from old fuse panels in garages. They used 60 mainsput and 1 arm bandits on the feed thru taps for air comps usually 10 wire and used 10 cable from the range fuses for 50 service to a welder.
 
/ welder circuit #12  
The IM230 is a heavy machine. It requires 10 in pipe or 8 cable. It is a machine might be on my short list today. It wouldn't overheat a 10 with modest use, 035 c25 short circuit. But the 211 class mig are dandy on a 10/30. I have my small migs on 30 for their home circuits. With 12 or better wire they are allowed on up to 50 but lower breaker doesn't hurt.
No one really thinks the minimum wire of 14 is a great idea as it makes for complicated terminations at the recepts. If it's used with that it needs to be limited to 30. That's why a 10 is good. It's 2 sizes bigger than the machine requires and is listed as a size for a 6-50 recepts.
 
/ welder circuit
  • Thread Starter
#13  
Yes, a 211 falls in this class. .

So would the Hobart 210 also reside in this domain?
I just need something that lays a good bead on 1/4" stuff w one pass.
The 120 v 140 amp welder for this thickness seems a bit wanting to me.

These welders can get pricey but I'd like to keep it in the $700-$900 range if possible.
The good welding machines even used, are commanding over a grand and more.
 
/ welder circuit #14  
The 210 is in this class. Its minimum wire is 14 on a max 30 breaker (single circuit in pipe) so it needs to be a size larger for cable and a 10 is 2 steps up, makes it an excelent circuit for that machine. I looked for giggles and the 230 is a heavy bugger, will output way more than its rating. Needs an 8 cable (10 in pipe) A 210 is a really good machine, can turn it up to do 1/4, enough to take the ripples right out. Hobart 210. Those would wet out even a bit better if the plate had been cleaned, I should have wire wheeled them after for a better view. I hadnt intended to show them like this at the time.
 

Attachments

  • Hob set test.JPG
    Hob set test.JPG
    79.7 KB · Views: 188
  • hob hot.JPG
    hob hot.JPG
    39.5 KB · Views: 198
/ welder circuit
  • Thread Starter
#15  
The 210 is in this class. Its minimum wire is 14 on a max 30 breaker (single circuit in pipe) so it needs to be a size larger for cable and a 10 is 2 steps up, makes it an excelent circuit for that machine. I looked for giggles and the 230 is a heavy bugger, will output way more than its rating. Needs an 8 cable (10 in pipe) A 210 is a really good machine, can turn it up to do 1/4, enough to take the ripples right out. Hobart 210. Those would wet out even a bit better if the plate had been cleaned, I should have wire wheeled them after for a better view. I hadnt intended to show them like this at the time.

Yeah that's what I want in a welder. Found it for $839 shipped. Thanks S.
Just bought the Miller $200 hood so I can see.
Miller Blue Rage Digital Performance Auto Darkening Welding Helmet for sale (2821) - Welding Supplies from IOC
 
/ welder circuit #16  
A book like this is invaluable when doing home wiring or trying to figure out thinks like adequate wire size. This one isn't expensive, and address both home, shop, and farm needs.

1 a wiring.JPG

It walks you thru necessary thing to consider. Thinks like the length of wiring/cable run, amps required, and voltage drop/loss. Tables are simple to use. Includes provisions for things like starting motors, copper vs al wire, sheathed cable (romex, if you will) and conduit.

1 a wiring 2.JPG
1 a wiring 3.JPG

As a side benefit it will also explain the real world difference between neutrals and grounds, something often misunderstood.

Good luck
 
Last edited:
/ welder circuit #17  
I have two welders. Both small because of the lack of any appreciable service out to the garage. Both welders (one stick the other wire feed) are rated for 140 amps.
I have 10/2, 30 amp 220 circuitry there now.

The small, flux core wire feed I recently acquired has only a 115 plug (daughters pitched in for Christmas and did the best they could) but the 140 stick has a 50 amp terminal end.

CAN I BETTER THE MIG/FLUX TYPE WELDER THAT FITS THIS ELECTRICAL PROFILE THAN WHAT I CURRENTLY HAVE OR AM I STUCK AT 140 AMPS? Most welding done with 1/4" metal with occasional 3/8"-1/2" that the stick can handle. It was good enough to weld a 1" thick splitter wedge on w 1/8" 7018.

What is the limit to wire feed welder amperage output on a 30 amp breaker 220 circuit?

It's no longer 115 input volts, it's 120 input volts on one hot wire, 115 is on the low side, a multi-metor would show 118-121volts, standard house entrance is 240 volts to a 100-200 amp panel.

My Miller-matic 211 can run on 120 volts or 240 volts, its plugged into a 240 volt outlet on 10/2 wire, into 20-30 amp breaker. My old Miller Dialarc can run 480 but is set on 240 volts and also plugged into a 240 volt outlet on 100 amp entrance cable into a 80 amp breaker.

You small mig welder on 115- 120 volt cant be change, but if I understand you half right you want more weld heat out of it, so there is a way to get more heat out of a small mig welder by using a DC stick welder, which means you can go to a next size up mig wire. If your stick welder is a DC welder, disconnect the wire off the mig gun side, clamp the stick welder rod holder to that wire, use ground on stick welder and dont use ground on mig welder, the wire in mig welder stays hot like a welding rod so have to be careful with mig-gun placement, now you have more mig gun heat.

IMG-9083.JPG IMG-9082.JPG IMG-9081.JPG IMG-9080.JPG

IMG-9079.JPG IMG-9078.JPG IMG-9077.JPG IMG-9076.JPG
 
/ welder circuit #18  
I have an old Dialarc just like that that I don't use anymore. Have the tig gun as well. Mine has the water cooled option.
 
/ welder circuit
  • Thread Starter
#19  
It's no longer 115 input volts, it's 120 input volts on one hot wire, 115 is on the low side, a multi-metor would show 118-121volts, standard house entrance is 240 volts to a 100-200 amp panel.

My Miller-matic 211 can run on 120 volts or 240 volts, its plugged into a 240 volt outlet on 10/2 wire, into 20-30 amp breaker. My old Miller Dialarc can run 480 but is set on 240 volts and also plugged into a 240 volt outlet on 100 amp entrance cable into a 80 amp breaker.

You small mig welder on 115- 120 volt cant be change, but if I understand you half right you want more weld heat out of it, so there is a way to get more heat out of a small mig welder by using a DC stick welder, which means you can go to a next size up mig wire. If your stick welder is a DC welder, disconnect the wire off the mig gun side, clamp the stick welder rod holder to that wire, use ground on stick welder and dont use ground on mig welder, the wire in mig welder stays hot like a welding rod so have to be careful with mig-gun placement, now you have more mig gun heat.

View attachment 682586 View attachment 682587 View attachment 682588 View attachment 682589

View attachment 682590 View attachment 682591 View attachment 682592 View attachment 682593

Thanks OP (and al3 for your info)
Quite the trick there Old Path.
You are correct about wanting more heat. The puddle on the Forney Easy Weld 140 is almost non-existent. I bought a $200 Miller hood just to see it better. The Forney is prolly operational for sheet metal where you use .023 wire. Even .30 wire on 3/16th was a struggle for it.
I don't want to tell my daughters about the inadequacy of their gift for my uses as I think would be rotten of me. My stick welder produces a 10 times better bead. It was as if you had to learn to mig first to use the Forney welder in order to become a better stick welder instead of the other way around.

After seeing the quality welds of sberry's 210 Hobart, I attempted to purchase the 210 Hobart which the company said they ran out of but would give me a 190 Handler for $100 bucks off. So I took their offer of $679 for the 190.
I'm hoping that welder can produce just about the same bead as Sberry's 210 Hobart.

Anything has to be better than the Forney which you can't even use on a 220 volt circuit.
 
/ welder circuit #20  
I have an old Dialarc just like that that I don't use anymore. Have the tig gun as well. Mine has the water cooled option.

Yep can flip the bottom panel up on the Dialarc and hook a tig torch on. I dont really have a need for tig welding but wouldn't mind having one.
 

Marketplace Items

2021 Ford F-150 4x4 Single Cab Pickup Truck (A61573)
2021 Ford F-150...
1999 John Deere 7810 (A60462)
1999 John Deere...
207276 (A52708)
207276 (A52708)
2019 KENWORTH T680 6X4 T/A SLEEPER TRUCK TRACTOR (A59912)
2019 KENWORTH T680...
2016 F-250 4X4 (A56438)
2016 F-250 4X4...
2015 PALMER MACHINE WORKS 24' DUMP TRAILER (A60430)
2015 PALMER...
 
Top