Yet another building on fill thread

/ Yet another building on fill thread #1  

5030tinkerer

Gold Member
Joined
Dec 27, 2005
Messages
457
Location
Iowa
Tractor
Kubota GL3830/GL5030
Hey guys -

I am building a 50x80 gambrel barn/shop using structural insulated panels (thermocoremo.com). The trouble is that the building site needed to be brought up about 4'. While the required footing will be resting on virgin soil, the 6" thick interior concrete slab will not be.

An early thought is to incorporate a concrete brick ledge on the inside perimeter of the stem wall (which is going to be constructed using insulated concrete forms) and then let the slab rest on that. As this only supports the perimeter, though, I was toying with the idea of installing 10' O.C. 12" diameter concrete piers for the slab to be further supported on. Though the first two feet of fill was installed in lifts, compacted properly, and even has benefited from a freeze/thaw cycle, the remaining two feet was taken from a wet part of the property which made it impossible to put down in proper lifts. Essentially muck just dumped out of the dump truck and was 'spread' in as thin of lifts as possible (sometimes 12" or more). When it got dry enough a few days later, a vibratory roller was used. Given the slope of the original site, as much as 3' of fill was placed this way. Sigh.

The question is whether I should at least wait another freeze/thaw cycle after final grading of the newly elevated pad before building or whether there is another way. Of course, I am not at all convinced that waiting 'just' a year will be sufficient. The pad will have two inches of roller and/or plate compacted 1" clean limestone gravel, then two inches of pink rigid foam, and then six inches of 4000psi concrete reinforced with 20 pounds/yard of Helix, a 'micro-rebar' that when used in this dosage is equivalent to #4 rebar placed 12" OC (http://www.helixfiber.com/sites/g/files/g605716/f/files/Application Guide - Slab on Grade_1.pdf).

Thoughts? I desperately want that building up, but don't want a floor that will need to be torn out later either. Of course, I want the floor to be able to support a 12,000# automotive lift and the periodic driving on it from a 21,000# LULL and similarly heavy tandem axle dump truck. Am I completely crazy or just mostly?
 
Last edited:
/ Yet another building on fill thread #2  
The most important thing is that the footing for the main structure is resting on virgin soil. Many a times the inside must be built up once the foundation wall are poured. A few examples my garage is built up 3' in the front and 5' in the back. My inlaws garage had the be filled 8' in the back and 1' in the front.
One thing is to make sure your filling with good material nothing organic that will decay later creating voids. Where you plan on putting your lifts i would do piers under your lifts post. When i need to use alot of fill i like to flood the interior. At my inlaws we used a water truck. In my own garage once i had gutters up i diverted many leaders to drain inside the "filled" garage. Water is a very very good tool to use in "compacting" fill material. Sounds like a nice building your putting up.:thumbsup:
 
/ Yet another building on fill thread #3  
Another thing i would like to add is. I like to take a garden hose and run it down inbetween the foundation wall and interior fill turn it on and just let it run. This should be done in all the corners and all along the perimeter. Just an example, look at when a house is backfilled or any excavations is done for that matter, Once the sheathing is put on the roof and after it rains when you walk around the drip line of the roof you'll see the ground has sunk due to the cracks in the soil. Water and lots of it is your friend in setteling soil. Even areas that have been compacted in lifts could benefit from water.
 
/ Yet another building on fill thread #4  
You can either pay to have a sheepsfoot compactor put the material in with 12" lifts with a compaction to refusal or you can wait several years for the materials to settle naturally. Its your money and time though!
 
/ Yet another building on fill thread #5  
A plate compactor is just for homeowners to compact patio's and walkways. It's just about worthless for dirt work. As mentioned, a sheepsfoot is the ideal tool for building up a pad. It vibrates AND mixes up the clay. Proper moisture content is also important since it allows the clay to bind with itself. Too dry and nothing happens, too wet and it's just mud. Moisture content is critical. I worked a season running a water truck and would spend day after day hosing the dirt pile that was being mixed with a wheel loader that went to the fill areas on jobs. Sometimes it was an area being built up, other times it was for filling trenches. The operator gave the signals, I just held the hose and sprayed where he pointed. No way would they attempt to work the dirt without water. And when the tank was empty and I had to get more water, they sat and waited.

Do not use a dozer. If you have something really heavy, you can use that instead of a sheepsfoot. I have a full sized backhoe with a one yard front bucket. When I'm filling a hole for a stump, or building up a pad, I go over that soil with a full bucket and cover ever inch multiple times. I'll have my dad stand there with the hose keeping it wet.

It is better to build up a pad that slopes away from the building that gives you great drainage.

I would want my footings do go below the virgin soil. How deep you go would depend on your area, but no matter how much you build up the pad, the place you measure from for your footing depth is the top of the virgin soil, and go down from there.

Eddie
 
/ Yet another building on fill thread
  • Thread Starter
#6  
Thanks for all the replies, guys. It is GREATLY appreciated.

So what I am hearing is that the fact that my footing will be atop (and actually technically just a bit under to Eddie's point) virgin soil is the big life saver in this deal and to not sweat as much about the interior pad. That is HUGE news. Thank you!!

It has rained ALOT here in Iowa this Spring. Essentially I get 10 dump truck loads in, spread as best I can while its still muck or sticky (though trying hard to keep the yellow clay out of the equation using it just for external-to-the-pad slope drainage), wait overnight for it to dry some, then vibratory roll it. Then it rains for three days it seems. Then I wait for it to dry enough to be workable again, vibratory roll it again, check the elevation, sigh heavily when it's only gone up the slight bit it did (sure, the building footprint is 'only' 50x80, but the area to be raised is more like double that not to even mention the copious dirt needed to slope it out so that it can look more natural), and move more dirt/muck to start the process all over again. The dirt at this point is coming from an area that is generally wet where my pond is being expanded. Per the county extension office, the dirt is a Sharpsburg silty clay loam.

The tandem axle dump truck empty weighs something 25,000#. It of course has been driving over the pad over and over. The padfoot vibratory roller is a smaller one, though, at only 6' wide with a weight of about 10,000. I'd have to look up the centrifugal specs. It never 'feels' like anything is happening when I use it, but driving over the pad with the dump truck later tells the story with the lack of deeper than 1" ruts even with the truck loaded to the gills (the box is 14', but I am very guilty of over loading it on property).

The plate compactor would only be used for final compaction of the two inches or so of 1" clean limestone just before the foam went down.

All ideas on how to mitigate the risks of a sinking slab appreciated!
 
/ Yet another building on fill thread #7  
The heavily loaded dump truck will allow you to proof the soil.
If the soil does not pump or deflect significantly when the truck drives over it, the soil will support the concrete slab
 
/ Yet another building on fill thread #8  
The heavily loaded dump truck will allow you to proof the soil.
If the soil does not pump or deflect significantly when the truck drives over it, the soil will support the concrete slab

That is not entirely true. It is however why material is placed in lifts and not mass fills. The effectiveness of compaction is lost at a certain depth based on its weight and soil type. The soil could still settle even if it has been "proofed" on the surface.
 
/ Yet another building on fill thread
  • Thread Starter
#9  
From what I understand, compaction in lifts is the preferred route. If the lifts are too high, you end up with a compacted upper layer and an uncompacted lower layer.

With padfoot vibratory rollers, the lift height is evidently the length in inches of the pads. In my case, that is 6".

With the dump truck, I'd think it able to get deeper than just 6", but still not the height that some of the lifts were placed in.

It seems that the only way to get the compaction other than to wait for umpteen years is to remove all of the soil and re-place it in the proper lifts that should have existed from the start.

At that point, though, it's less expensive to just install piers on some interval and accept the fact that certainly some compaction has occurred. Ten foot on center 12" piers at 48" in a grid would burn 2 yards of concrete. No big deal. I'd think I could put in the piers at 5'OC intervals and really be set.

The question is how to do the piers as I had planned on having 2" of gravel and then 2" of foam under the concrete. What do you guys think? Are the piers the way to go? If so, should the top of the pier be at the bottom of the compacted gravel or should I lose insulation value and have the piers come up through the gravel and through the foam for a monolithic pad/pier pour?
 
/ Yet another building on fill thread #10  
That is not entirely true. It is however why material is placed in lifts and not mass fills. The effectiveness of compaction is lost at a certain depth based on its weight and soil type. The soil could still settle even if it has been "proofed" on the surface.

My statements were based on previous statements that the material was being placed in lifts.
If placed in lifts over the stated 12" it is possible for the surface to bridge over uncompacted material and settle later. Excess moisture can cause problems for a clay soil, even if it was previously well compacted
 
/ Yet another building on fill thread #11  
That is not entirely true. It is however why material is placed in lifts and not mass fills. The effectiveness of compaction is lost at a certain depth based on its weight and soil type. The soil could still settle even if it has been "proofed" on the surface.

My statements were based on previous statements that the material was being placed in lifts.
If placed in lifts over the stated 12" it is possible for the surface to bridge over uncompacted material and settle later. Excess moisture can cause problems for a clay soil, even if it was previously well compacted
 
/ Yet another building on fill thread #12  
Perhaps a higher density of piers, tied together with a "grade beam"+ extra rebar where you expect higher load concentrations (wheel tracks, lift pads) and a little more spread out (or even none at all) in the general shop/workbench/storage areas?

It's not like you're going to jockey all the vehicles into all the corners of the building, you're mostly just going to drive them straight in from the doors, right?
 
/ Yet another building on fill thread #13  
Be careful with over engineering and complicating the process. When building, always figure out what it will take to accomplish the task in the most cost effective method using time tested, proven methods. While there is always some benefit to more materials in your footings, there is a point where you are just throwing money away. If the soil is of good quality, compacted with proper drainage, there is no reason to go into a complex foundation design. Spend the time and money on getting the dirt right, and the rest is easy.

Eddie
 
/ Yet another building on fill thread #14  
Hey guys -

I am building a 50x80 gambrel barn/shop using structural insulated panels (thermocoremo.com). The trouble is that the building site needed to be brought up about 4'. While the required footing will be resting on virgin soil, the 6" thick interior concrete slab will not be.

An early thought is to incorporate a concrete brick ledge on the inside perimeter of the stem wall (which is going to be constructed using insulated concrete forms) and then let the slab rest on that. As this only supports the perimeter, though, I was toying with the idea of installing 10' O.C. 12" diameter concrete piers for the slab to be further supported on. Though the first two feet of fill was installed in lifts, compacted properly, and even has benefited from a freeze/thaw cycle, the remaining two feet was taken from a wet part of the property which made it impossible to put down in proper lifts. Essentially muck just dumped out of the dump truck and was 'spread' in as thin of lifts as possible (sometimes 12" or more). When it got dry enough a few days later, a vibratory roller was used. Given the slope of the original site, as much as 3' of fill was placed this way. Sigh.

The question is whether I should at least wait another freeze/thaw cycle after final grading of the newly elevated pad before building or whether there is another way. Of course, I am not at all convinced that waiting 'just' a year will be sufficient. The pad will have two inches of roller and/or plate compacted 1" clean limestone gravel, then two inches of pink rigid foam, and then six inches of 4000psi concrete reinforced with 20 pounds/yard of Helix, a 'micro-rebar' that when used in this dosage is equivalent to #4 rebar placed 12" OC (http://www.helixfiber.com/sites/g/files/g605716/f/files/Application Guide - Slab on Grade_1.pdf).

Thoughts? I desperately want that building up, but don't want a floor that will need to be torn out later either. Of course, I want the floor to be able to support a 12,000# automotive lift and the periodic driving on it from a 21,000# LULL and similarly heavy tandem axle dump truck. Am I completely crazy or just mostly?

A couple of freeze thaw cycles will not be sufficient to settle poorly compacted material. You have two choices to do the job right:

1. Build the foundation walls and then bring in crushed stone and use it to backfill the hole. This material should be consistent in size (3/4 to 1-1/4) and could be compacted in 12" lifts with a walk behind compactor.
2. Use a non-organic dirt material which is free of large rocks and compact it in shallow lifts using a ride-on compactor. The bigger the compactor you get, the thicker the lift can be. These can be rented from a commercial outfit.

With a proper moisture content and some good material option #2 will work and won't settle. You'll spend more on the compactor, but will save on material. You'll have to do the math to see which way you will want to go. If you do go with option #2, try to proof roll the area using a fully loaded dump truck. If it makes ruts you did a poor job of compacting and have to start over.
 
/ Yet another building on fill thread #15  
Quote Originally Posted by Streetcar
The heavily loaded dump truck will allow you to proof the soil.
If the soil does not pump or deflect significantly when the truck drives over it, the soil will support the concrete slab

That is not entirely true. It is however why material is placed in lifts and not mass fills. The effectiveness of compaction is lost at a certain depth based on its weight and soil type. The soil could still settle even if it has been "proofed" on the surface.

Streetcar was talking about proof rolling the fill and his statements were spot on correct. The truck is not being used to compact the material, that's the job from a drum compactor, but to verify the compactor has done a sufficient job. You're statements that the compaction is lost in mass fills is also correct. Shallow lifts must be utilized, usually 12" is the standard when using heavy equipment, but shallower lifts are a sure bet when a geotech isn't on site.
 
/ Yet another building on fill thread
  • Thread Starter
#16  
Excess moisture can cause problems for a clay soil, even if it was previously well compacted

I'm helped on the moisture front I'd think by the fact that the building site is the highest thing around it. The site has a 4 degree sloped drop off on the west, south, and east for 800+ feet. 100 feet to the east is my home, the grade of which is 3' higher than the building, but there will be a 2 degree downward slope for a 40 foot concrete apron from the building, which will intercept a 3.6 degree slope from the 56' long apron from the house. I could potentially raise the building pad up another 17" to get matching 2 degree slopes from each building, but doing so would necessitate making my frost walls another foot deeper to ensure that I hit virgin soil on the spread footing.

I am considering raising the building the 17" and NOT extending my frost wall despite the virgin soil concern though, given that the earth 2.5 feet below current grade (four feet below future grade) has been there more than two years already, was properly compacted unlike this fill I am using now which is only 'somewhat' properly compacted, and the fact that I am more than just a little concerned about hitting an electrical service that runs under the pad which SHOULD be deep enough, but hitting it is beyond just bad. Ultimately, I want the ability to have a basketball hoop on the far end of the concrete pad and don't want people to 'feel' like they are playing on a slope. I'm not at all sure that 3.6 degrees would 'feel' that way, but know that we've had visitors have trouble on the more slippery days even getting through the 4.4 degree slope on the county's road with their 2WD vehicles.

Removing all of the 200+ dump trucks of fill already placed to get this area built up again strikes me as more expensive than just installing piers with perhaps grade beams at this point.

Am I on track?
 
/ Yet another building on fill thread
  • Thread Starter
#17  
The other option, I suppose, would be to install a new electrical service that goes around the building, abandon the existing one (two 200 amp feeds), build a basement under the building and install a formed beam system for the floor on the main level like what the folks at liteform (LiteForm | Concrete Deck Forms - LiteForm) offer, but the price now just WAY up.
 
/ Yet another building on fill thread #18  
Quote Originally Posted by Streetcar
The heavily loaded dump truck will allow you to proof the soil.
If the soil does not pump or deflect significantly when the truck drives over it, the soil will support the concrete slab



Streetcar was talking about proof rolling the fill and his statements were spot on correct. The truck is not being used to compact the material, that's the job from a drum compactor, but to verify the compactor has done a sufficient job. You're statements that the compaction is lost in mass fills is also correct. Shallow lifts must be utilized, usually 12" is the standard when using heavy equipment, but shallower lifts are a sure bet when a geotech isn't on site.

I agree to a point. I was stating that "proofing" the soil as you guys are putting it, only checks the surface and not the entire fill depth like you seem to be implying. Th e pressure of the truck is spread out easily with enough depth that it looses effectiveness. This is exactly why they put in 12"-18" lifts based on material and roller size for examples.

I also agree that moisture is pretty critical for compaction and is hard to eyeball for a novice. Over saturation after compaction also causes severe problems.
 
/ Yet another building on fill thread
  • Thread Starter
#19  
So what would you guys do in my situation? I've got about 1400 yards of dirt already spread, some by me, some by others, that is not properly compacted but the footings will go to virgin soil or extremely close to it. Ride on vibratory roller compaction DID occur, just in likely too high of lifts. Remember also that there is an electrical service about 66" below current grade.

Options are:
1. Install a pier or pier and beam system to support the floor along with an interior to the foundation wall brick ledge and go.
2. Use more rebar/microbar to strengthen the slab and pour anyway.
3. Build the foundation stem walls, backfill around them as usual, and repeatedly flood the interior to promote settling.
4. Do a combination of the above.
5. Remove the 1400 yards and replace it in proper lifts, compacting as we go now that things are drier.
6. Hire a geotech and have the compaction measured to get his recommendations since maybe things are better compaction wise than we think they are.
7. Let it settle a freeze/thaw cycle and then do one of the above options.
8. Other

For tools, I have a full sized 42,000 excavator (an old Koehring 6620), an old IH175C track loader with a 4n1 bucket, a tandem axle dump truck, and a ride-on vibratory pad foot roller. I also have the phone book to 'just' hire one of these solutions done, but that strikes me as the spendiest option of them all! I'm tempted to pay the money to have a geotech report done.

I am kicking myself for not ensuring that the dirt was placed properly to begin with, but such are life's lessons. I guess I had to pee on the electric fence for myself this time. Sigh. At least we're having the conversation before things get REALLY expensive.
 
/ Yet another building on fill thread #20  
I'd get a small cat in there and scrape the site clean. Start pushing the material back in the proper lifts while simultaneously using a drum compactor. You can do it once right or do it twice. You already need to remove the improperly compacted material so the sooner you can start doing the job right, the less pain there will be. If that's not happening then I see two choices: Roll the dice and beef up the floor slab or hire a geotech.

Geotechs are not horribly expensive, but if you can compact the material well you can put that money back into the bank. The last contract I signed was $11,500 for 16 borings. You won't need as many holes, but the trip charge alone will put you in the $1500+ range.

I just finished a project which had improperly compacted fill. The geotech was guessing it had been compacted with a dozer. That material had been down for 25 years and only had 1500 psi of bearing capacity and the potential differential of movement was in the 3" range.
 

Marketplace Items

3PT 10' Rolling Cultivator (A60462)
3PT 10' Rolling...
Landhonor SAD-12-23C Skid Steer Mount Auger (A62679)
Landhonor...
2026 NORSTAR IRONBULL T/A 25FT GOOSENECK TRAILER (A59914)
2026 NORSTAR...
100 gal L Portable Fuel Tank (A66408)
100 gal L Portable...
2018 Navigator RT-6500 6,500lb Piggyback Forklift (A61567)
2018 Navigator...
2020 Can-Am Commander XT 1000 R (A62679)
2020 Can-Am...
 
Top