wire in plastic conduit

/ wire in plastic conduit #1  

geneP

Platinum Member
Joined
Jun 28, 2000
Messages
845
Location
Central Mississippi, USA
Tractor
Case-International 385, Kubota L5450 w/LA1150A loader
I went to the box store and bought wire and conduit to bury a lighting circuit to the new garden shed. I thought I was buying copper 10/2 w/ground underground wire, but when I got ready to install it I found it is not UG wire. I'm putting it in the water-tite UV resistant schedule 40 pipe. Can I use this wire? I'm assuming it will stay dry in the conduit.
 
/ wire in plastic conduit #2  
Unless the conduit can be sealed airtight it will fill with water due to the water in the air condensing in the colder underground conduit.

James K0UA
 
/ wire in plastic conduit #4  
Underground (direct bury) or exposed (outside) wire is called UF. I think you'll be ok with what you have in conduit. I have heard that in underground conduit it is best to use the loose wire without the jacket (thhn). But that's what circuit breakers are for!
 
/ wire in plastic conduit
  • Thread Starter
#5  
Alright, it is marked UF-B. I'm accustomed to the underground wire that is mean to skin. This wire has a vinyl/plastic jacket that encases the neutral and two insulated wires like the tuff stuff, but skins easily. Google says it's ok for direct burial, so I guess I'm OK without another trip to the store?
 
/ wire in plastic conduit #6  
UF-B stands for underground feeder with 90 deg insulation. You should be OK.
 

Marketplace Items

2025 Kivel Quick Hitch Mini Skid Steer Attachment (A61572)
2025 Kivel Quick...
2003 HRTO 14ft. Enclosed S/A Trailer (A61574)
2003 HRTO 14ft...
2015 Dodge Charger Sedan (A61574)
2015 Dodge Charger...
2020 CATERPILLAR 140 MOTORGRADER (A63276)
2020 CATERPILLAR...
2008 Ford Expedition SUV (A61574)
2008 Ford...
(2) 25X10.00-12 TIRES ONLY (A64280)
(2) 25X10.00-12...
 
Top