wiring for welding

   / wiring for welding #41  
SPIKER said:
I suggest not listening to some of the posts here. You HAVE to by code wire the (in this case welder) per the plug being used. MOST welders use the 220v 3 prong 50 amp plug. (hot lead hot lead and ground no neutral.) also used to be referred as a stove plug. This is a 50 amp plug and the wiring feeding that plug MUST be approved to handle 50 amps continuous! if the welder needs it or not!

depending on the wire used you more than likely will need to use 6 GA wire. 8 ga is rated usually to 45 amps ONLY...

Mark M

p.s. I guess you don't HAVE to do anything, but if there is a fire and the insurance finds that there is something wired wrong that YOU did you are finishing paying the mortgage not them :(. also if you were ever SELL the place and the next inspector found this plug (this is a place that most home inspectors see a 50 amp plug they will WILL look to make sure the wiring to that plug was correct. it is same if you put in 20 amp outlets you have to by code use 20 amp rated wire (12 gauge that is)
so if you want to risk burning down the place then by all means wire the plug as you see fit. I say this only because most people think that doing electrical work is some thing that any tom dick or harry can do. and that is why every home needs to have an independent inspection done by the people LOOKING at buying it not the person selling it or the Realtor as the Realtor only gets paid if the place sell...


BUBKUS!!
 
   / wiring for welding #42  
Inspector507 said:
First, I think it's wrong for a manufacturer to include a plug that will fit into a range outlet. One is a NEMA 6-50R the other is a 10-50R. The 6-50R is the correct one. Most welder supply houses will have it if you ask for a welder outlet. Is it more convenient to install a range plug? Yes. Because they are more readily available. And people don't know there is one dedicated for a welder.

If you look at Table 310-16 of the current NEC, there is an asterick on #10 wire. The asterick directs you to Article 240-4(D) which directs you to 240-4(G) for Special Conductor Appilcations. That in turn says to look at Article 630 for Electric Welders, which says for one welder on the circuit, you can fuse the feed for the welder at 200% of the conductor ampacity. #10 THHN/THWN is actually rated for 40 amps, so if I fuse it at 200%, it's good for 80 amps for a welder.

But we can agree to disagree. :D

BTW I didn't make a recommendation in this thread on the receptacle, just the previous ones.


I love it! Imagine the confusion if the discussion were on motors!:D
Have a Happy New Year Inspector507!
 
   / wiring for welding #44  
Iceman65 said:
Hmmm, interesting reading here. :D

Yes indeed, verrrrrrry interesting but...

Lets see if I can put out the flames with a dash of gasoline and some breeze.

Let me assure everyone I am not a licensed electrician or an electrical inspector but have gained a little experience being around electrons for a few decades (have made living as electronic engineer for a while.) My take on this thread is pretty close to Gemini's.

While it is theoretically possible (I have done it) to use two separate 120 vac circuits to produce 240vac it is NOT recommended.

Q: What is a 240 VAC breaker?
A: Two 120 VAC breakers mechanically ganged to "KILL" both legs if either one meets the "trip" specs.

The idea stated about 120VAC running through the welder's transformer to neutral and then the other leg of 120 running through the transformer to neutral is one way to design a welder BUT it is not the way any of the welders I have ever seen are designed. Common welders like a Lincoln tombstone has 240 VAC applied across the primary which is NOT center tapped for a neutral connection.

There are two areas of concern in sizing the wire for a welder. 1. the wires from the breaker to the outlet and 2. the wire from the plug to the welder. Wire #1 is to be sized to meet code and prevent a fire in the wall or wherever and as Gemini pointed out should never be undersized compared to the breaker, NO MATTER WHAT!!!

The wire (called #2 above) from the plug to the welder, supplied by the maker (often with plug) may and often is of lesser size than the wire needed in the wall.
Q: Why is that?
A: the wire is short and exposed to cooling air and is big enough for such a short run and saves the mfg a buck.

Long wires drop more voltage at any given size (waste power/make heat) short wire may drop more volts per unit of distance but thankfully are short so do not ordinarily cause a problem in the case of the power cord of UL approved equipment. The manufacturer has covered his backside liability wise and his choice of wire size for the short power cord supplied is OK. (well, OK enough)

Do not even begin to think if it is good enough for the manufacturer it is good enough for you and run the same size in the wall. BAD IDEA!! (see above)

I didn't note for sure if the original poster was wiring in the basement and welding elsewhere or welding in the basement. If welding in the basement the ventilation is most likely woefully inadequate and as others pointed out, a respirator will help the weldor but not anyone sharing the house. IF there is a basement window AND it were fitted with a powerful exhaust fan AND the welding took place so that the fumes were immediately exhausted and not mixed into the basement air then maybe it would be acceptable.

Readers Digest version: Don't weld in the basement without proper ventilation. Use a wire size approved for what you are doing and IN NO CASE rated for less amps than the breaker, hopefully more.

Saving money by reducing the size of wiring in the wall is not safe or smart as several posters mentioned.

Is playing Russian roulette with your fire safety worth saving a few bucks? OK, honey, so the house burned down but I saved almost $20 on wiring and when I get out of inhalation therapy if the insurance doesn't find the reason for the fire we can...

Pat
 
   / wiring for welding #45  
I haven't read every post,but I've said this before on TBN. There are somethings that should left to the professionals. I'd hire an electrician to install it, that way if something does happen you have certification that it was done right.
I'm not sure if you can (or should for that matter) put a welder in your basement. I dont weld but I had my brother weld something for me over the Christmas break. We were in a 30x40 garage and I was standing at the opposite end of where he was welding. After three days I still had black stuff coming out of my nose. Not sure I'd want this in my basement, and don't think the little misses would either.

Wedge
 
   / wiring for welding #46  
The wire rating in the wall has to deal with being completely buried in insulation, bundled with other wires, and if it catches on fire in the wall, you might not notice rright away, or even be able to easily find the smoldering area and put it out.

If the the cord on the appliance gets too hot while you are using it, you likely notice right away. Like the other day I had a cheap extension cord end go up in smoke while using a circular saw (the end must have had a bad connection). There was little danger, but a lot of smoke and smell and I simply tossed the thing out into the snowbank Same thing happen in the wall? Could have burned down the whole house.

Another issue with a basement for welding is fumes from other sources that can collect in low areas. Make sure you don't have any paint thinner or gas cans stored down there.

- Rick
 
   / wiring for welding #47  
Guys let me point out something here. Inspector 507 is quoting what the NEC says. He has years and years of experience as a licensed electrician he is currently an electrical inspector. I am very sure that what he is quoting is correct and is acceptable practice. The reasons behind it are very sound. You dont leave your welder on making an arc for hours and hours at a time. You strike the Arc melt the rod for a bit then stop and see where you have to grind down( or at least if you weld like me you do).The posters that say hire an electrician to do the work are probably the most correct posts in this thread. If you hire a licensed electrician to do the work and something happens that your house burns down due to an electrical fire the insurance company is going to pay off with minimum questions asked. The insurance comapny might have a long talk with the electrician but you are going to be covered. If my house burns down due to an electrical fire since I am not an licensed electrician I am going to have to do some serious arguing about my wiring practices. I have enough experience as a commercial electrician and I try to exceed the minimum NEC requirements when I wire something so I am not worried about that arguement in the event it happens. I went back and checked the wiring going to my welder it is 10 gauge which covers the input current on my welder. I have my welder on a 30 amp breaker. My own personal opinion is that breakers are a protective device, as a protective device I believe they should match the device they are protecting. I dont think the weakest link in the power chain should be the wire going through the wall. But that is my personal opinion. The one thing that I think everyone will probably agree on is that there is nothing keeping you from exceeding the minimum requirements of the NEC. If the minimum requirement is 10 gauge there is nothing stopping you from using 8 gauge. If the NEC says you can use a 50 amp breaker there is nothing stopping you from using an 30 amp breaker. I think Patrick g's sentiment sums it up pretty well. Gee dear I know the house burned down and we lost all the pictures of the kids and our family, I know that we lost the desk that had been in your family for 24 generations but I saved a couple of hundred dollars on the wiring for my 2000 dollar welder.
 
   / wiring for welding #48  
gemini5362 said:
The one thing that I think everyone will probably agree on is that there is nothing keeping you from exceeding the minimum requirements of the NEC. If the minimum requirement is 10 gauge there is nothing stopping you from using 8 gauge. If the NEC says you can use a 50 amp breaker there is nothing stopping you from using an 30 amp breaker.

I agree completely.

The original poster was concerned with the 12/3 cord on the welder. I would say he is okay.
 
   / wiring for welding
  • Thread Starter
#49  
Man, this is a hot topic, no pun intended. Let me state a few things and hopefully this thread can be put to bed. The difference between paying an electrician and doing it myself is the difference between getting to use the welder and not, at this point I cannot afford to pay someone to do it. I have done electrical work for 20+ years and the final outcome is usually better than if I paid someone, I never scrimp on this stuff just don't want overkill. BTW, my existing welder is in the basement right near the walk out door so that I can weld outside or if needed open the door wide and weld just inside out of the weather with a fane blower out. Any new wire I run will not be within the wall and will be removed if I move. Attached is a picture of the current plug on the welder. Thanks for all the posts.
 
   / wiring for welding
  • Thread Starter
#50  
The picture is on this post. Now that I look at it and google the 6-50R one they look to be the same. So no range plug.
 

Attachments

  • plug2.JPG
    plug2.JPG
    391.7 KB · Views: 274
   / wiring for welding #51  
KubotainNH said:
The picture is on this post. Now that I look at it and google the 6-50R one they look to be the same. So no range plug.

Yes that is a welder plug, a NEMA 6-50P which mates to the NEMA 6-50R that welders should be using.
 
   / wiring for welding #52  
Inspector507 said:
Yes that is a welder plug, a NEMA 6-50P which mates to the NEMA 6-50R that welders should be using.

Ah, Yup! That is what comes on the Lincoln Buzz boxes. I think I recall they are rated for up to 250 volts and 50 amps so they are "T H E T H I N G" for your application.

Basement door to the outside. Good deal. Fan... good deal.
Wiring you can take with you.. Good deal.

Depending on the length of the wiring run you still don't want to cut the "ampacity" too close.

I have started a few fires in my time while welding and witnessed several others. The guy in the dark helmet looking through a glass, darkly, doesn't have a clue that he has started a fire. Once I was standing in a grass fire my sparks started and didn't know it till the heat built up enough to make an impression. I am reminded every time I look at the "customized" cord on my MIG.

Sounds to me like you have the situation scoped out for getting started. Go for it but BE SAFE.

Pat
 
   / wiring for welding
  • Thread Starter
#53  
Yeah, I started some leaves on fire once before. They were under the ramp to my shed, that'll get the adrenaline flowing. I now have an auto-darkening helmet so when I pause I can actually see stuff. Very good investment.
 
   / wiring for welding #54  
I have one of the cheap autodarkening helmets from Harbor Freight, they are about 49.95. I use one of the expensive ones that we have at work they are 150 + to be honest I cannot see any difference between the two except the harbor freight helmet you can adjust the darkness intensity with a knob.
 
   / wiring for welding #55  
gemini5362 said:
I have one of the cheap autodarkening helmets from Harbor Freight, they are about 49.95. I use one of the expensive ones that we have at work they are 150 + to be honest I cannot see any difference between the two except the harbor freight helmet you can adjust the darkness intensity with a knob.

I have had two of them. I loaned one of them to a friend a few years ago. I have the battery operated kind rather than the solar powered kind. Eventually you have to change the batts (a couple AAA) but not very often so it is no big deal. I get a few years out of a change. It is adjustable from #9 to #12 and is about a #4-5 when in the light state.

I have only two minor complaints:

1. if you turn it off to try to use it for a #4-5 for plasma cutting the LCD does not "play nice" and soon gets all mottled. It snaps back into proper condition as soon as it is switched on but I wish its "off" state were more stable.

2. If you want to leave the helmet on for protection for a bit of grinding the sparks cause the unit to darken, then it relaxes back to its clear state then a spark will darken it and so forth. Not ideal.

I guess a good thing would be a flip up window with protective glass that stayed in place. You'd have the best of both worlds, protection with a good view for grinding and then when you lowered the auto unit back down you'd have automatic welding protection.

Pat
 
   / wiring for welding
  • Thread Starter
#56  
Hmm, I think mine is a Hobart. It has 2 adjustments, one for darkness and one for sensitivity I think or maybe it's speed of darkening. I never tried it for grinding but I may have to just for curiousity sake. Mine has solar cells that charge the batteries. It's so much better than my flip up.
 
   / wiring for welding #57  
Usually an auto welding helment is not used for grinding because its too expensive to mess up by grinding with it.

I figured the wiring part of this discussion would finally come to a conclusion. What worries me is that arc welding generates a lot of fumes and a fair amount of sparks. So I'm not a fan of welding inside a basement. At least with an arc welder, you can weld outside although I'm not sure what else you have outside that might catch fire. For me, I see better outside to weld anyway. I've read where some people say they won't leave an area where they've welded for at least 30 minutes just in case a spark got behind something and could start a fire.

The poster who cautioned about not welding around gas or other flammable items makes a good point, too.
 
   / wiring for welding #58  
2manyrocks said:
Usually an auto welding helment is not used for grinding because its too expensive to mess up by grinding with it.

Any GOOD welding protection type filter such as the auto darkening unit or gold plated glass for TIG or whatever should be itself protected by a protective cover. These clear protective covers take all the abuse of sparks and are changed out when they interfere with a good view. With a disposable protective cover over your auto-darkening unit there is no particular reason not to use it for grinding except the reasons I listed in my previous post.

Regarding the adjustments on auto-darkening units. None have adjustable switch times (how long they take to get dark.) Faster is ALWAYS better. The adjustments are shade (darkness) and delay time (the time the unit stays dark after it no longer detects welding.)

One curious thing I have noted is that sometimes if I point the unit toward the sun it will "flutter" switch back and forth between dark and light several times a second. Doesn't hurt anything and it always resumes normal ops again when not aimed at the sun.

Pat
 
   / wiring for welding #59  
I bought the wire for my second welder plug installation, different houses, just last night. The code allows small wire but I choose to exceed code and use 6 gauge wire on a 50 amp circuit. This not only exceeds code but allows me to use 50 amps someday should I decide to add a subpanel, an air compressor, or something else to the circuit. 10 gauge wire is about a third of the cost per foot and I bought a roll of that too for running a 30 amp generator backfeed circuit. Lots of copper in the truck.
 
   / wiring for welding #60  
Highbeam said:
The code allows small wire but I choose to exceed code and use 6 gauge wire on a 50 amp circuit. This not only exceeds code but allows me to use 50 amps someday should I decide to add a subpanel, an air compressor, or something else to the circuit.

The peace of mind from a safe and efficient installation is a GOOD THING and easy expandability without obsoleting a (just barely meets code) installation is actually more economical of your time as well as $. Like you I don't want to have any, "it probably won't catch on fire" circuits that won't support any likely upgrades. I have watched this same sceanario a couple times... Get welder, jury rig the power, get a bigger welder (didn't buy enough welder the first time) re-jury rig the power, etc. Lather rinse repeat. In the effort to "save money" it turned out as much or more money was spent, more time was wasted, and the final result was still a jury rig.

How do projects go so wrong? A little bit more every time, never taking the time or spending the $ to do it well so you get to do it again.

Pat
Pat
 

Tractor & Equipment Auctions

2016 INTERNATIONAL PROSTAR TANDEM AXLE DAY CAB (A59904)
2016 INTERNATIONAL...
2021 Polaris Ranger Electric Utility Bed UTV (A56859)
2021 Polaris...
5th Wheel Hitch (A59230)
5th Wheel Hitch...
2014 Ford Fusion Passenger Car, 2.5L Engine - Only 90,875 Miles (A56438)
2014 Ford Fusion...
2019 DRAGON ESP 150BBL ALUMINUM (A58214)
2019 DRAGON ESP...
500 BBL FRAC TANK (A58214)
500 BBL FRAC TANK...
 
Top