What guage wire to use

/ What guage wire to use #1  

jimmyj

Elite Member
Joined
Aug 28, 2007
Messages
4,126
Location
Ontario Canada
Tractor
Allis Chalmers 616 (Two) and a Kioti CK30 HST with loader and backhoe
Hi all. I have to power a new hot tub. The tub comes with a 40 amp GFCI and the wire run will be 55 feet. What do you guys think for the correct guage? Should I go #8? The wire has to come through the wall of the house from the panel, and will run in a zig zag route around the landscaping underground to the tub so I figure I will get direct burial rated wire and also put it into conduit.

(My neighbour is an electricial so I will be getting a professional opinion but always find TBN'ers to have good ideas too.
 
/ What guage wire to use #2  
I'd use multi strand wire, whatever size you get. It's a lot easier to deal with than single strand. May not be able to get single strand for that amperage anyway.

Ralph
 
/ What guage wire to use #3  
Yes. 8 gauge is good for that moderate distance. Note that conduit does protect somewhat, but due to insulating the wire from earth cooling effects, will derate the cable slightly. If youre using direct burial cable you might as well take advantage of direct burial.
 
/ What guage wire to use #4  
What I think is irrelevant! It's your area electrical code that counts.
 
/ What guage wire to use
  • Thread Starter
#6  
Good comments. I think it is #6 by memory actually now that you say it. Nobody seems to be able to tell me what the code is at the hot tub place or local hardware. My electrician pal will be back in a few days so I better check.
 
/ What guage wire to use
  • Thread Starter
#8  
So the electrician advises #6 - 3 wire. Expensive stuff!
 
/ What guage wire to use #9  
#8 copper is rated for 50 amps or more, depending on the type of insulation. Doesn't that hot tub require 4 wires? That would be two hots, a neutral and a ground.
 
/ What guage wire to use #10  
#8 copper is rated for 50 amps or more, depending on the type of insulation. Doesn't that hot tub require 4 wires? That would be two hots, a neutral and a ground.
Itll carry it for sure, but for 3 wire its rated for 40 by NEC. You dont count ground.
 
/ What guage wire to use
  • Thread Starter
#11  
Yes, there are 4 wires in total, red black white and ground. I'd rather be a bit over than a bit under too.
 
/ What guage wire to use #12  
8-3 UF wire si good for 40A.

Wondering why your electrician is suggesting 6-3? (which is good for 55A). Maybe because he already has some on had?

Also, not sure what type of breakers you have, but it may be a bit difficult putting 6ga on a 40A breaker.

As far as length, you can go to 125' pulling 40A on 8ga before you exceed 3% voltage drop. So I dont see that being a reason to upsize wire either.

Now you may want to see if there is anything you can do to get the circuit length to 50'. Wire comes standard in 25', 50', 125', 250, etc rolls. See if you can make 50' work and not have to buy 125' of wire, and not use 70' of it.

BTW, 50' 8-3UF is ~$90
.......125' 8-3UF is ~$190
 
/ What guage wire to use
  • Thread Starter
#13  
I bought the 6 3 yesterday. Actually needed 18 meters and it cost 244.00. Everyone I talk to says use #6, I assume it's a local standard.
 
/ What guage wire to use #14  
Wow, thats pricey. Can get 50' here for ~$110 and 125' for about $300
 
/ What guage wire to use #15  
Usually a good idea to run a 12/3 out there at the same time to power a pair of 20amp T-slot GFI plugs in the yard.
Either net for wifi too.
 
/ What guage wire to use
  • Thread Starter
#16  
Wow, thats pricey. Can get 50' here for ~$110 and 125' for about $300

Welcome to Canada, the land of the overcharged.
 

Marketplace Items

MULTIQUIP LIGHT TOWER (A60736)
MULTIQUIP LIGHT...
500 BBL FRAC TANK (A58214)
500 BBL FRAC TANK...
1003 (A61166)
1003 (A61166)
iDrive TDS-2010H ProJack M2 Electric Trailer Dolly (A59228)
iDrive TDS-2010H...
2016 Kubota SVL75-2 (A53317)
2016 Kubota...
JLG 20MVL MANLIFT (A58214)
JLG 20MVL MANLIFT...
 
Top