Hi all. I have to power a new hot tub. The tub comes with a 40 amp GFCI and the wire run will be 55 feet. What do you guys think for the correct guage? Should I go #8? The wire has to come through the wall of the house from the panel, and will run in a zig zag route around the landscaping underground to the tub so I figure I will get direct burial rated wire and also put it into conduit.

(My neighbour is an electricial so I will be getting a professional opinion but always find TBN'ers to have good ideas too.
 
   / What guage wire to use #2  
I'd use multi strand wire, whatever size you get. It's a lot easier to deal with than single strand. May not be able to get single strand for that amperage anyway.

Ralph
 
   / What guage wire to use #3  
Yes. 8 gauge is good for that moderate distance. Note that conduit does protect somewhat, but due to insulating the wire from earth cooling effects, will derate the cable slightly. If youre using direct burial cable you might as well take advantage of direct burial.
 
   / What guage wire to use #4  
What I think is irrelevant! It's your area electrical code that counts.
 
   / What guage wire to use
  • Thread Starter
#6  
Good comments. I think it is #6 by memory actually now that you say it. Nobody seems to be able to tell me what the code is at the hot tub place or local hardware. My electrician pal will be back in a few days so I better check.
 
   / What guage wire to use
  • Thread Starter
#8  
So the electrician advises #6 - 3 wire. Expensive stuff!
 
   / What guage wire to use #9  
#8 copper is rated for 50 amps or more, depending on the type of insulation. Doesn't that hot tub require 4 wires? That would be two hots, a neutral and a ground.
 
   / What guage wire to use #10  
#8 copper is rated for 50 amps or more, depending on the type of insulation. Doesn't that hot tub require 4 wires? That would be two hots, a neutral and a ground.
Itll carry it for sure, but for 3 wire its rated for 40 by NEC. You dont count ground.
 

Tractor & Equipment Auctions

2013 Freightliner Bucket Truck (A55973)
2013 Freightliner...
2020 PETERBILT 567 (A58214)
2020 PETERBILT 567...
2014 Jeep Grand Cherokee (A56859)
2014 Jeep Grand...
2008 New Holland B110 MFWD Loader Backhoe (A57024)
2008 New Holland...
DEUTZ MARATHON 60KW GENERATOR (A58214)
DEUTZ MARATHON...
2020 KUBOTA RTV X1100C UTV (A51406)
2020 KUBOTA RTV...
 
Top