Trenching for Utilities...
/ Trenching for Utilities... #1
ultrarunner
Epic Contributor
SF Bay Area-Ca Olympia WA Salzburg Austria
Cat D3, Deere 110 TLB, Kubota BX23 and L3800 and RTV900 with restored 1948 Deere M, 1949 Farmall Cub, 1953 Ford Jubliee and 1957 Ford 740 Row Crop, Craftsman Mower, Deere 350C Dozer 50 assorted vehicles from 1905 to 2006
I'm in the county in Washington State.
As some here know I have been unsuccessful in getting Comcast to run 500' from the pole to the rent home I have...
Also, the direct bury electric cable installed by the utility has been repaired twice at no charge by the utility and I have been told it is at the end of its useful life and they no longer direct bury and require the owner to provide conduit.
Third... I've been thinking it might be nice to have a camera/intercom and a hose bib at the start of the driveway.
Comcast is supposed to be sending the requirements and a sketch... from what I can tell they really only care that I install 2" conduit.
Thinking about doing my own trenching and would like to kill all birds with one trench/excavation...
The previous owner told me they had trouble with a trench that went straight to the house channeling water and suggested I not go down the driveway and instead go down the property line and make a 90 sweep to the house with a concrete vault because water doesn't flow uphill...
I realize utilities often don't play nice when it comes to sharing... on the other hand adding a couple of empty conduits seems like a win/win for me even.
/ Trenching for Utilities... #2
What is it you want Comcast to run ... just cable TV or Internet?
If it is Internet and/or On Demand TV they are probably needing a "Hard Line" to go that far (unless they run fiber all the way to your house) - a Hard Line is a much larger cable (insert more expensive) and does not always insure working Internet so they shy away from those long runs.
If all the Utilities are asking for Conduit, you should be able to dig one ditch, run all the conduits with some space between them, fill the trench back in and then call them.
/ Trenching for Utilities... #3
I can see them not playing nice if THEY were doing the trench, but if it is YOUR trench and if you are providing them what they require as far as conduit ,it should not be up to them what else you put in there ,unless codes prevent it.
Moss...
Just had a big install of Comcast here for the Hospital... had to bore under the State Highway etc... they use 1.5" orange corrugated flex pipe in California
In WA it has to be 2" rigid conduit... with at least one concrete vault midway...
My thought is if I do it myself... I will add extra conduit runs for future... might even run PEX through one for a hose bib out by the gate.
Never taken on a trench project this big alone...
Maybe GRStheGreat will see this thread and add to it?
My house panel is 400 amp with a small pedestal transformer out in the yard... don't know for sure what the feed voltage is... heard 600v but don't know.
/ Trenching for Utilities... #6
Aren't there some code about water lines, communications lines and electric lines in same trenches, distances apart, etc...? Are you going to have to dig multiple trenches? Are you going to use a trencher or a backhoe? How deep do you have to go? Are you allowed to dig your own? Man, I'm a pest. :laughing: I ask because I went through similar questions back around 1989 with our rural property. We never did it due to cost. Now, I wish I would have done it back then due to the price increases in everything today. Close to 5X as much now. :(
Comcast started this and other than the 2" conduit requirement it seems on end user private property to cover it.
The closed circuit TV, PEX well water hose bib and intercom I would think I'm pretty much on my own.
Comcast even said if a suitable conduit just happened to be there we would be good to go.
No idea on electricity other than the conduit is suppose to be on me...
The last thing I would want is a trench running down my drive... I have many places with drainage tile and and geo fabric... digging that all up I would imagine would cause problems.
/ Trenching for Utilities... #8
Ultra, if you have a transformer feeding your 400A house panel at that location, who owns the transformer? Normally the utility owns up to the secondary side of the transformer. Seems they would not want to have you run the conduit if it is their side of the system. Normally only industrial customers own or install any of the primary side as they are metered on the primary feeders.
Idea, why not get the Power Co and Com Cast together and develop an grade plan. Power may let you dig the ditch and lay pipe for ComCast and they lay there pipe in foryou to cover; or some variation. Primary power work is expensive that is why hook up fees are so high. At least talk to their install engineers for guidance. As far as I can remember the governing codes there is no separation required between conduits of the two systems other than common sense.
When I was a facility/utility planner for the Navy we never installed less than 2" for UG comm and 4" for primary power and secondary feeders. Those long pulls are murder and some times impossible in smaller pipe and/or the stretch limit is exceeded. The vault requirement is a code thing, Power Company will do the same and the vaults have to be separate.
Ron
/ Trenching for Utilities... #9
I havnt done much work in wash state for many years, but the utility company has always been responsible for all work between transformer and their meter. Customer is responsible for enverything after the meter. That being said, the utilities sometimes do require the homeowner or contractor to provide a trench. Ive run into this a few times in the past.
As far as utilities laying in common trench, we do that all the time. here in Idaho, we dig a 24" wide trench 4-5' deep and put water at bottom of that, then cover with 1-2' of fill. Then we place all other utilities except for electric on one side and place electrical on other side and cover trench. This leaves 18"+ separation between all utilities. We place water so deep due to our frost zone issues here. Wash will be different. Ive also seen people trench 3' wide common trench with water on one side, power on other and all other utilities in middle. NEC does not have any rules governing this, it will be a city/state issue.
/ Trenching for Utilities... #10
Power is generally required to be buried deeper and with more separation from other stuff. Gas may be the other stickler, if you have that. Low voltage stuff, nobody seems to care about much from a code standpoint. And to echo Seabee, the transformer should be the utility's, and not yours, but after the transformer is yours. I would expect thousands of volts to that transformer, not 600V. I think my current one is 4800V or 9600V I forget, and our old house was 19.2kV
A mid sized backhoe can dig the needed trench to the depths required for multiple feeds much more easily than other methods. Easier to work in an open trench than to pull individual feeds a billion times. Dig to the bottom, put the lowest stuff in, backfill a bit and level it out some, then put then next layer in, etc...
Both times the I lost a leg of power PSE came out and found the break and did a repair splice.
I was in California and found out after all was said and done... 2007 and 2012.
The last time PSE told the customer/tenant the direct burial line was at the end of life... it's 40 years old and PSE said they no longer install or maybe PSE meant direct burial?
The meter is on the house and the small pad mounted transformer is about 20 feet away and about 500 more to the pole... all underground... I'm the only one underground and the newest home by a longshot... the transformer is very small... I was surprised at how small it is... home is all electric with two water heaters and two furnaces with supplemental wood heating.
First time the tenants thought the refrigerator died and then noticed other things not working... lost a leg.
The last time the lights were flickering and bulbs burning out... tenant said the ground was sizzling at the break location.
Everything I deal with in California is overhead... no underground... just this one in Thurston County.
Thinking on a ride on trencher about 3 feet inside my property line and then a sweep towards the house...
The water line is just my idea for convenience... it can get dry a few weeks every July and dragging a couple of hundred feet of garden hose gets old.
No idea as to voltage to the transformer... I am at the end of the run distance wise... so whatever happens only effects me.
Anywhere I dig other than the gravel drive would be through the forest duff...
/ Trenching for Utilities... #12
Yeiks. If your talking about the high voltage side of the transformer, thats a whole other thing. The utilities use a special conductor to run the high voltage side, and they usually require the electrical to be buried 36" deep with no other utilities in same trench. I thought you were talking about the secondary side of the transformer (that portion feeding your house after the transformer). Ive never had a public utility ask a homeowner to supply the primary side, much less to install that. Thats always been on their end. If its reached its life, its on there nickle up here.
Good to know... everything to the meter weatherhead has always been my experience and I've done a fair amount of service upgrades in California... lots of older homes dating from the 20's and 30's...
Should I be pro-active with PSE or just wait for the next break which may never come?
The transformer just sits in the landscaped area with lots of ivy around it... not much bigger than an industrial battery if I remember correctly... strange to see it just out in the open.
The transformers I have at the hospital all have fenced and locked enclosures and all wire is underground.
I thinking I need to verify where the primary runs... was supposed to get plans and they could not be found...
/ Trenching for Utilities... #14
Ultrarunner, You may have covered this before but why is satellite internet not an option? Trenching 500' 3ft wide is going to be a large project, time consuming and expensive. Not to mention the mound of dirt 3ft high you have to settle, re-compact and replant.
/ Trenching for Utilities... #15
I can't speak for Ultrarunner exactly, but generally, satellite is quite expensive for much much slower speeds. Last time I dismissed it, the cost was 2-3 times the price (about $100 for only Internet) and about 700kB (about 6 times slower).
Now, if your mean DSL, which often gets bundled with satellite TV, well, that comes in on phone lines and I'd assume he would still need to trench.
/ Trenching for Utilities... #16
I don't know about your state, but here and everywhere else I have lived, the power company owns and maintains up to the transformer. At my house here in Arkansas, the power company will run for free overhead lines to the meter if you want. If you want underground lines then you have to pay to have them installed. I found that the power company had the cheapest rates for wire so I had them pull the wire in. I had my house contractor dig a trench and install the size conduit (plastic) that the power company required. Power company wanted $5 per foot to dig the trench and install the conduit which was about 120' in length but my building contractor did it for free then power company pulled the wire and terminated it at the meter. They furnished, pulled and installed the wire cheaper than I could have purchased the wire. They would have still had to do the termination at each end even if I had installed the wire in the conduit leaving the required pigtail length at each end.
One thing to remember is that data lines (internet) need to be at least 12" from any high voltage line to prevent interference. I have never seen anything in Code that prevents water line from running in the same trench as electrical.
The only issue with doing that is if you have to repair the water line, you will have to hand dig and be very careful that you don't cut into the electrical. With water line repair where I know there is nothing but water, I just dig with the backhoe till I hit the line then dig the hole big enough to fix the damage, don't want to do that with electrical in the same hole.
If your winter temps are such that you can put the water line a foot or more above the electrical then you would be ok to do that. 3 feet or more for the electrical and then 12-18" deep for the water. Here I can get by with 12" and have no freezing issues.
/ Trenching for Utilities... #17
This is what I found on the internet for satellite internet service.
#1 – HughesNet
HughesNet has been in business for over 30 years and has over 2.5 million customers across 100 countries. HughesNet’s monthly download capacity ranges from 20GB to 40GB. Bonus data is available between the hours of 2am to 8am. HughesNet offers generous download speeds and monthly bandwidth capacity when compared to the competition. They include a free standard installation from one of their authorized professional installers.
HughesNet offers 24×7 technical support to their customers via phone, chat and email. They also provide instructions to walk you through various technical issues via their system control center available on their website.
Advantages
Up to 15 Mbps Download
Up to 20GB Anytime + 20Gbps Bonus per month
Pricing
Starting at $39.99
Free Standard Installation
Granted not the fastest but trenching and burying conduit can buy a lot of satellite service.
I used to use DSL, it was ok at the time not sure where it is now but ATT is offering gigabit service here over existing lines.
My son uses his 4LGT phone as a hot spot for his internet. Doesn't use it a lot but still an option.
The geography makes it a cell free zone... no cell service.
DSL isn't available as it is too far out in the county.
There is no TV reception over the air.
Satellite has been there before... Tenant got a quote for HD Satellite and provider said it was not possible unless a number of trees came out... I had already paid $3,800 to have trees removed for regular Satellite over the years.... HD would mean a $11,000 in added tree removal costs.
All the neighbors had Comcast via utility poles... some of the homes go back to the 1920's... my home is the newest dating from 1977 and has underground utilities.
Power Company was paid to do the underground install of power in 1977... they used direct burial and now that line is showing it's age.
My only thought was IF I was going to trench... get the most bang for the buck... make a provision for a spare conduit for power... although this might not be feasible as the power is high voltage to a small pad mounted transformer.
What makes it all kind of ironic is I'm only 10 minutes from the steps of the State Capital in Olympia Washington...
/ Trenching for Utilities... #19
Ultra, so far you seem to be getting valid info from all us rocking chair experts.
OK guys, I found it. Underground power and communications is goverened by the rules in the National Electrical Safety Code published by the Institute of Electrical and Electronics Engineers. It is the industry accepted standard by utility companies and Authorities Having Jurisdiction. Mine is an old 2002 version left over from when I was a planner for the Navy and then as a Contractor Quality Control manager on Military construction. The language leaves a lot of things up to designers and cooperation between installers/utilities. There is language about separation of utilities and induced interference in communication systems. Too technical to deal with in this forum. 2012 is the latest edition and available on Amazon for a substitute for "counting sheep".
Thurston County area; I would bet that the Primary is 12,470 primary volts. That is the most common voltage until you get out away from civilization and they still have old systems. Power companies have pretty well standardized on 12470 as the transformers are cheaper and lend to several voltages and configurations. It is nasty when a backhoe hits it and shorts across phases. I have seen part of the bucket destroyed.
TRIVIA; old Navy bases had 4800 V Delta distribution but the transformers still work on 12470 Y.
Thanks Seabee...
Do you have underground electric from PSE?
Any thoughts how PSE handles a situation where the direct bury line they installed goes bad after 40 years?
So far they have made repairs twice I know of without cost.
If I have the chance, I still plan on adding a couple of smaller spare conduits for intercom/hose bib/security... no reason to add a 120 line as there is already one there for the gate.
I will plan NOT to run primary voltage in my Comcast trench.
Also thinking it would be good to know exactly where this 12,470 volt buried line runs...
I would hate to dig into it!!!