Thanks everyone for the input. Back to Lou's list:
I'm confused by step 3) and step 7). Would step 7) be "turn on the breaker in the house for the generator"?
The normal acceptably method of powering your house with a pto generator generally would be as follows;
1) switch your transfer panel from utility to generator
2) connect your tractor to your generator
3) check that the generators main breaker is off
4) engage your pto and start rotating your generator
5) monitor the Hz reading and voltage reading from your generator, looking for 60Hz and close to 240Volts
6) while it stabilizes shut down all circuits in your main panel you don't want to energize, keeping in mind the max power you can generate
7) close your generator main breaker
8) you have now loaded your generator
9) you now need to verify your Hz and voltage adjusting your tractor throttle as necessary.
10) as your load changes you may see some variation in Hz or volts and it may require throttle changes depending on your tractor and the load.
11) if you overload your tractor you will see that the Hz and volts will be going lower and your tractor does not have the power to bring the rpm back up
I'm confused by step 3) and step 7). Would step 7) be "turn on the breaker in the house for the generator"?