Do you put an underground splice like this in a junction box of some kind? Or do you just bury it and mark the location in case you have to come back and bury it again?
I believe per code, you can bury it and walk away, but I wouldn't flag that minimal effort that as great practice. As you know that you will need to find it to splice in the wires to the shop, I would either put it in a vault, or mark it in some way that will make it easy to find and work on. I would bear in mind the minimum NEC code burial for direct burial is 24", 18" for PVC conduit, and 6" for metal conduit.
If the shop build is imminent, I would be tempted to do the splice, and run the shop feeder line in one go to save work, and leave a really solid marker adjacent to the splice point as a "just in case" for the future. (E.g. a 6" concrete plug going down 3-4', with an incision on the top to mark wire orientation, and distance from the marker, or a section of oil pipe with a metal plate on top.)