I'm still a long way from buying anything, but for now, I'm thinking that a 22kw unit is what I want. But I have to get the natural gas installed and a meter installed. A residential meter is for a one-inch line. Can I run a 22kw generator from a one in natural gas line?
A 22k is about 320k BTU... my recollection is that the "length of pipe in feet" is from the regulator, and you have to consider what other requirements for gas are on that pipe if any.
For instance a few years ago I put in a tankless water heater (199K BTU) to replace a previous 80K BTU tank water heater. There's a few feet of pipe that are only for the water heater, then it connects to a bigger pipe that also carries gas to a 80K furnace, and that length of pipe goes for N feet to a bigger pipe that then goes back to the regulator. I had to do calcs on the entire system to ensure that there was enough pipe to handle the new water heater's flow needs.
If you have a pipe that will only be connected to the generator (now and forever) all the way to the regulator, the above chart should do (though connectors add "length" as well). IMO always size up from today's requirements, dig once.
Note that all the above are assuming the post-regulator pressures are usable without per-appliances regulators themselves (7" / 0.25psi). You may be able to have a higher pressure regulator at the meter (eg 2psi) and drop it down with another regulator at point-of-use or upstream of multiple points of use, in which case the calcs are very different (1" pipe carries much more gas at 2psi than at 0.25psi).