A newbies DIY solar install

   / A newbies DIY solar install #41  
We have postponed the build of our retirement home due to:

1. The ridiculous cost of lumber goods right now
2. The explosion of innovation in solar technology.
3. Waiting for more contractors in the area that are certified to install solar roofs.

Our house is on track to use solar as the primary source of power.
 
   / A newbies DIY solar install #42  
Currently waiting on the electrical diagrams to come back. Ended up hiring this out and is the only thing I'm waiting on to complete the application for approval to our utility. Hopefully it's a fast approval so I can get the equipment order placed.

Orezok those rates are crazy. We are .13 cents year round with no peak or off peak and that's higher than most around because we are on the local coop. My business is with evergy and rates are .09.
Because the rates are so high, that was the exact reason I went solar. Below is last months bill. As you can see, I generated 187 kWh more than I used. Many months I am in the "green" so it doesn't matter what the SCE cost is . August our hottest month which has monsoons causing us to use the regular AC and not evaporate coolers and December with additional cooking and lights are my highest months so far. From the graph this month I used a -6.23 kWh vs last year 25.17 and 2 years ago 26.38. I should receive a small rebate check next June on my anniversary date.

I really don't care what SCE charges any more and will recoup my investment in about 4 years.

My next "upgrade" is that I am installing an electric water heater to replace my 15 year old LP one. Propane is even more rediculous than electricity out here. First I have to pay Amerigas $129 per year to get a contract rate. That gives me the privilege of paying $3.50 per gallon year round. NO summer discount.

I may have to add couple of more panels and micro inverters but that is all.



Screen Shot 2021-03-27 at 11.39.00 AM.jpg
 
Last edited:
   / A newbies DIY solar install #43  
@orezok Personally, that's exactly what I love about net metering annually, and why we went solar. I can bank excess power June-September and "use" it Dec-March. Even with big batteries at the house, that's hard to do.:)

All the best, Peter
 
   / A newbies DIY solar install #44  
This is what my electricity looked like recently, set up for less expensive rate at 9pm.
Screenshot_20210327-130028.jpeg


You can see the hot tub (240v) timer go off at 4pm, which is during the most expensive electricity, so the system pulls from the battery and keeps exporting PV to the grid (export is paid at import rates, unless you end up exporting more than you use).

It'll look different in a couple days as I expect it's going to be charging after midnight since the new TOU plan is cheapest from 0000-1500. It could just recharge from morning sun, but right now it doesn't matter one way or another since grid power at 0000 costs the same as 0900 PV gets refunded, so may as well have the batteries recharge at 0000.
 
   / A newbies DIY solar install
  • Thread Starter
#45  
I received the line diagrams and plan set back today. Application has been made with our electric coop so just waiting on their approval now in order to order equipment and move forward. Plan set attached.
 

Attachments

  • PV Plan Set.pdf
    1.7 MB · Views: 224
   / A newbies DIY solar install #46  
I received the line diagrams and plan set back today. Application has been made with our electric coop so just waiting on their approval now in order to order equipment and move forward. Plan set attached.
The site plan shows the 481' trench with a 1" pvc conduit, and the SLD shows it with a 2" pvc conduit (wire tag 6).

I'd get a second opinion on that conduit sizing - I ran 2 4/0 + 1 #10 neutral in a 2" and it was snug enough; I don't want to think about 3 4/0 + #4 on that long of a run. Also I'm not sure if all of those cables may over fill a 2" conduit (Google "conduit fill").

Also I'm curious - my system was spec'd with a ground at the array and no ground in the conduit, and a pretty small neutral (the neutral was just for some auxiliary stuff at the array, my microinverters don't do neutral); check if those inverters really need a massive neutral cable?

Is there any communication necessary between the service panel area and the inverters for rapid shutdown?
 
Last edited:
   / A newbies DIY solar install #47  
Your plans remind me of my system
1617207159728.png


My distance between the house and array is smaller, only about 125'.

paul
 
   / A newbies DIY solar install
  • Thread Starter
#48  
The site plan shows the 481' trench with a 1" pvc conduit, and the SLD shows it with a 2" pvc conduit (wire tag 6).

I'd get a second opinion on that conduit sizing - I ran 2 4/0 + 1 #10 neutral in a 2" and it was snug enough; I don't want to think about 3 4/0 + #4 on that long of a run. Also I'm not sure if all of those cables may over fill a 2" conduit (Google "conduit fill").

Also I'm curious - my system was spec'd with a ground at the array and no ground in the conduit, and a pretty small neutral (the neutral was just for some auxiliary stuff at the array, my microinverters don't do neutral); check if those inverters really need a massive neutral cable?

Is there any communication necessary between the service panel area and the inverters for rapid shutdown?

Yep. Looks like I'm seeing 2" conduit with a total of 3 4/0 + #4 ground same as you on the long ac run. Could easily just jump up the conduit size. Will check on the neutral and verify no coms needed for the rapid shutdown. I do not believe they do.
 
   / A newbies DIY solar install
  • Thread Starter
#49  
Will have to do some checking on conduit. Looking at charts it seems 2" should be plenty. Hoping so as there is a significant price jump from 2" to 3" or even 2.5"
 
   / A newbies DIY solar install #50  
Yep. Looks like I'm seeing 2" conduit with a total of 3 4/0 + #4 ground same as you on the long ac run. Could easily just jump up the conduit size. Will check on the neutral and verify no coms needed for the rapid shutdown. I do not believe they do.
If there's any possibility that you may as 6 batteries to the system for microgrid/backup, you'll likely be needing to have communications to the shutdowns or to some additional control there (with a microgrid, the inverters won't see the grid go down).

At the very least I'd consider running a 1" conduit with a pull string if that's at all possible, rather than having to dig again.
 

Tractor & Equipment Auctions

1000 Gallon Water / Chemical Tank (A50860)
1000 Gallon Water...
2021 John Deere 333G Two-Speed Hi Flow Compact Track Loader Skid Steer (A50322)
2021 John Deere...
2019 HONDA PIONEER 5 1000 UTV (A50459)
2019 HONDA PIONEER...
2017 GENIE GTH-636 TELESCOPIC FORKLIFT (A51242)
2017 GENIE GTH-636...
Mitsubishi FG15 Forklift (A50860)
Mitsubishi FG15...
Misc. Office Furniture (A50860)
Misc. Office...
 
Top