Going 540', I would consider upsizing the conductors to reduce losses, but more than that, I would think about DC.
If you have no shade, you might want to consider running the DC back to the house, and converting it there, if you can arrange your DC to be as high as possible for your inverter input, but below, 600V. (I think that is from a common insulation limit on wires, but there is also an NEC burial limit for depth, as in you have to deeper if at, or over, 1000V.) You will have lower power loss in the transmission. (Loss goes as current squared times resistance, so doubling the voltage quarters your losses) I would check your local codes and AHJ to be sure.
I'm not a solar expert, but that's the advice we were given, and it made sense to me.
YMMV
All the best,
Peter