Currently working through the application for our electric coop for the approval to grid tie the solar before I finalize the purchase. One question I have for those who have done a ground mount system before is the location of the invertors and auto shutdown box? Did yours go at the panels or house? For my installation it looks like the sequence would be panels to rapid/auto shutdown box to invertors to manual disconnect to utility. Panel location is about 540 feet from the house and invertors are outdoor rated. With that said would it be better to locate the invertors & shutdown box indoors for better efficiency out of the heat? My electrical service enters the house into a utility room in the basement where my electrical panel is located. Just thinking it may be best to also place the shutdown modules and two invertors on the basement wall as well as opposed to outdoors on the house. Would make for a cleaner install as well without all of the components on the outside of the house.
I set something up something similar last year (DIY; purchased from a licensed electrician and paid him for some consulting here and there).
The trench from my ground mount to my shop, where the service entrance is, is about 600'.
My system has 10kW of panels; with the inverter action happening at the array, the cables are running 240V, a maximum of 40A.
With 4/0 Aluminum, I've got a maximum voltage drop of 1.55%. I "sized up" on the cable because if we add an electrc car or two, I may end up adding another 5kW of panels to run on the same cables; 60A on 4/0 for 600' gives 2.32% drop. "Sizing up" probably added $200 which is cheaper than an empty conduit to pull a cable later and much less effort.
My system uses a microinverter for each panel tied to a box at the ground mount; the 4/0 aluminum goes from that box to the switch in my shop (actually, there's a junction box at the end of the trench where the cable hits the shop, and it goes to #4awg through the shop at that point - the #4 for 40' is a negligible voltage drop and it's WAY easier to handle through the bends necessary in that building - and a much smaller conduit). The microinverters together with the main control brains handle rapid-shutdown; there's no separate box for it (all components are Enphase other than the panels).
That switch functions as a microgrid interconnection device (it'll automatically disconnect the grid if it senses bad things or absence, and will regulate the output of the microinverters).
As far as I know, it's not sufficient to have "integrated inverters on the solar panels" (microinverters; typically not integrated to the panel but often attached one to one at the panel) to be able to run solar without the grid. There has to be some intelligence to throttle the solar production to the load. It's possible that this only works with batteries to serve as a buffer.
[Ground vs roof mount: My house is in trees and doesn't have enough good roof for 10kW, let alone a future extra 5kW. Also, the roof is OK for now but would need replacement before you'd do something serious like put solar on it. I also wanted to be able to easily clean the panels, and not have crap fall on them from trees all the time; my ground mount is in the middle of a field with great sun in the winter and even better in the summer. Ground mounts can be pointed and tilted exactly how you want them trivially (once), vs panels are pointed where the roof points on a house roof. Ground is probably easier to DIY, but it's definitely more expensive, and typically you need more panels to get the same kW as a ground mount because of direction and heat... and I already didn't have enough room on the house (2-story house)]