320 amp service
/ 320 amp service #1
Lazy
Platinum Member
Missouri
ford 1920 w/fel and bh, case 470, allis chalmers B 1937, JD 450 track loader, Case vac, 3 cub cadets ford lgt 125, Kubota 2230/60 inch mower.1948 farmall cub 1953 farmall cub
Hi
when installing two (2) 200 amp load centers would you run a ground wire from each load center neutral to the ground rod or connect a ground wire to the neutral in the meter socket box to the ground rod?
Charlie.
/ 320 amp service #2
Assuming your load panels are close together, you can bond the neutral to ground in a number of acceptable ways. Personally, I bonded neutral to ground in each separate panel, and drove two ground rods about ten feet apart. I ran separate #4 bare copper wire from each panel to the ground rods. Since both panels share the same neutral from the pole, this should give you a little bit better ground than just one ground rod. Over here, you also need to bond the ground to the water pipe entrance to your house. That seems a little silly to me since most of my water pipes are PVC - but go figure... The inspectors have the final say.
I believe you can also just bond the two panels together and run a single ground line to a single ground rod.
While you're at it, give some thought to installing panel-mounted surge and lightning arrestors. It will add a couple hundred bucks total to the install, but it's a great thing to have when you get power surges and/or lightning strikes. Whole-house protection just can't be beat. Check out Delta Surge Supressors and Lightning Arrestors - they mount easily to your panel via conduit knock-outs.
/ 320 amp service #3
Another idea (ie. something that I wished I would of done).
I have two 200 amp services at my house. I wanted/needed a backup generator so I found a decent midsized solution. 18KW with a 200 amp switch. It now switches and provides backup power to one of the panels.
Of course, I wish that I would of planned out the circuits between the two. Now I need to move about 8 to 10 from one panel to the other to provide the power to the desired circuits...
/ 320 amp service #4
It was my understanding that this was NOT the perfered way to wire it as you run into a ground loop issue.
It was my understanding that this was the correct way to wire it. The above (single) ground rod would service both the meter box, and both 200amp service pannels.
As my meter is more than 15' away from my "breaker box" (mounted on a pole) i was required to provide a seperate disconnect at the pole (just a 200amp breaker) with a ground rod for the meter box. A second ground rod is/was required for the "breaker box" at my barn. (as this "breaker box" is now considered a sub pannel of the main disconnect on the pole)
/ 320 amp service #6
If you have multiple ground rods, they should be tied together with bare copper underground. It's not important how deep it is, unless code says otherwise, just so it is underground. This helps protect against lightning strikes. If the ground rods are not bonded together, a lightning strike can generate a damaging differential voltage between the grounds that will feed back into your system.
In lightning country, all ground rods should be tied together this way. That includes the telephone and TV/satellite antenna grounds.
I use #6 bare copper.
/ 320 amp service #7
also known as a ground loop.