Generator in a outside building and powering the panel...

   / Generator in a outside building and powering the panel... #81  
Can you site the code please? Thank you.

Howdy,
So even without citing code, you think its ok to send a live feed in both directions when on generator power?

So in real world use, the barn sub-panel will be energized while on generator, as you now have multiple neutral+ ground locations

Stop getting your panties in a bunch. He has existing conduit under the driveway, like I said before, just run the separate lines and proper interlock and be done.
 
   / Generator in a outside building and powering the panel... #82  
I don't understand the panties comment. I simply politely asked for the code site since you said it would be contrary to code.

If you really can't site the code that's OK just say so. If you can site it it would be good to know.
 
   / Generator in a outside building and powering the panel... #83  
Gpin, why bother. He is going with the cobb job no matter what he is told.
 
   / Generator in a outside building and powering the panel... #85  
What we have going on here is the layman's standards for electrical equipment and the NEC requirement's endorsed and used by professionals in the electrical field.
The pro understands the electrical theory why those silly rules are written and enforced by law. The layman figures if the equipment works without immediately exploding into a sparking ball of flames that the installation is satisfactory.

Site the code.
 
   / Generator in a outside building and powering the panel...
  • Thread Starter
#87  
Gpin, why bother. He is going with the cobb job no matter what he is told.
Riiiiight, that is why I am asking what code is, vs just going and doing it...
You claim to be an expert, cite some code to back up your assertions or explain why it is a bad idea.

Howdy,
So even without citing code, you think its ok to send a live feed in both directions when on generator power?
So in real world use, the barn sub-panel will be energized while on generator, as you now have multiple neutral+ ground locations
Can you explain a little what you mean? I am not quite following you. Yes, the barn subpanel will be hot while the generator is on. It feeds the barns where the critters are and the critters need to be kept from freezing...

Show me where it is against code and I will happily follow the code, this WILL be done right the first time.
But at the same time, I am not going to go and spend $500+ to get the same effect as I could for $40-150 (as buickanddeere suggested I do when he suggested that I install a Reliant interlock panel ahead of the current panel).

Aaron Z
 
   / Generator in a outside building and powering the panel... #88  
Howdy,
OK, your barn sub-panel is connected and working properly? OK, that means it has a master circuit breaker at the main service panel. That means all the wires are correct. You want to add a 50amp dual pole breaker with a interlock. OK but, you only want to use 2 wires. OK, in theory it sounds good, but when you switch over the interlock, (shuts off main, turns on generator breaker), the 2 wires are feeding the main panel, and the neutral and ground are still attached to the main service panel ground bar, and somehow connected to the sub-panel and generator. I understand what you want to do. It would be like saying use 2 separate 50 amp breakers, one at location 3 and the other at location 18 for your dual pole breakers. It's just not done.

Because of the limited draw at the barn sub-panel, because you have conduit in the ground, get the interlock for your panel, get you dual pole 50 breaker, and run 4 wires properly. Your not gonna break the bank with adding those 2 wires to a 100ft run. move on
 
   / Generator in a outside building and powering the panel... #89  
"It's just not done."

"... out of code for electricity flow" (whatever that means).

So you really don't have a site to offer. That's ok. No one else does either.
 
   / Generator in a outside building and powering the panel... #90  
"It's just not done."

"... out of code for electricity flow" (whatever that means).

So you really don't have a site to offer. That's ok. No one else does either.

700.19 Multiwire Branch Circuits Prohibited

A new 700.19 has been added addressing multiwire branch circuits used in emergency systems. This new provision prohibits multiwire branch circuits protected by common trip circuit breakers to serve emergency lighting and power circuits. Emergency lighting and power could be unavailable during ordinary line to ground faults and other problems where common trip circuit breakers or handle ties are employed. Continued reliability of emergency circuits requires this change. [ROP 13-118]
 
   / Generator in a outside building and powering the panel...
  • Thread Starter
#91  
700.19 Multiwire Branch Circuits Prohibited

A new 700.19 has been added addressing multiwire branch circuits used in emergency systems. This new provision prohibits multiwire branch circuits protected by common trip circuit breakers to serve emergency lighting and power circuits. Emergency lighting and power could be unavailable during ordinary line to ground faults and other problems where common trip circuit breakers or handle ties are employed. Continued reliability of emergency circuits requires this change. [ROP 13-118]
Are you sure that applies? I looked at that section last night and as I understand it, that section only applies to things like emergency lighting that are considered critical to life and health. This genset would be classed as an optional backup genset (702.9) rather than an emergency system.

Aaron Z
 
   / Generator in a outside building and powering the panel... #92  
Are you sure that applies? I looked at that section last night and as I understand it, that section only applies to things like emergency lighting that are considered critical to life and health. This genset would be classed as an optional backup genset (702.9) rather than an emergency system.

Aaron Z

Here's a link to a nice booklet that explains it all.... ANnnnnddd.... It looks like you're good to go. ;)

http://www.google.com/url?sa=t&rct=...E-kvNQssECVnvrZzf4OLq4g&bvm=bv.77880786,d.aWw
 
   / Generator in a outside building and powering the panel... #93  
Are you sure that applies? I looked at that section last night and as I understand it, that section only applies to things like emergency lighting that are considered critical to life and health. This genset would be classed as an optional backup genset (702.9) rather than an emergency system.

Aaron Z

I agree Aaron. That section is for emergency power like at hospitals exit lighting at public places like theaters etc.

Your situation is optional backup power.
 
   / Generator in a outside building and powering the panel... #94  
Geesh! I'm on the side that says he can do it, but Lord Mercy, let me offer those who say he can't some fodder, cause ya'all need some help: Argue this: Article 300.3 (B). So when running genny power, where is the neutral conductor for subpanel neutral current now? (I'm making a better argument for your side and I don't even agree with myself! :laughing: :confused2:)
 
   / Generator in a outside building and powering the panel... #95  
I'm going to have to eat 1/2 a crow here . While drawing out the wiring plan with the existing conductors and using a Kirk-key on the generator breaker and a Kirk-key at the house 200amp main breaker for the electrical Code Inspector this morning. Well darn, I realized that I missed something . It is legal.
The plan B however to pull generator powered conductors into the same conduit as the regular supply to the barn. This made the Inspector growl and say no d@mmed way.
 
   / Generator in a outside building and powering the panel...
  • Thread Starter
#96  
I'm going to have to eat 1/2 a crow here . While drawing out the wiring plan with the existing conductors and using a Kirk-key on the generator breaker and a Kirk-key at the house 200amp main breaker for the electrical Code Inspector this morning. Well darn, I realized that I missed something . It is legal.
Good to know, might have to look into prices on one of those.

The plan B however to pull generator powered conductors into the same conduit as the regular supply to the barn. This made the Inspector growl and say no d@mmed way.
Can you (or the inspector) elaborate on what section of the NEC forbids it (assuming that it is not a separately derived system and as such, the neutral and ground are always connected to both the generator and the mains power)?
It would seem that this would be classed as an optional standby system and fall under 702.9 which states the following:
http://freenec.com/T581.html said:
702.9 Wiring Optional Standby Systems. The optional standby system wiring shall be permitted to occupy the same raceways, cables, boxes, and cabinets with other general wiring.

Thanks

Aaron Z
 
   / Generator in a outside building and powering the panel... #97  
Becomes a separately derived source in the same conduit so it's not considered safe or legal.
 
   / Generator in a outside building and powering the panel...
  • Thread Starter
#98  
Becomes a separately derived source in the same conduit so it's not considered safe or legal.
Can you explain why that is?
Everything I have read says that if the neutrals and grounds are unbonded at the generator and then run separately to the main panel (where the generator neutral is then bonded to the system neutral and the generator ground is bonded to the system ground) it is NOT considered a separately derived system and only the 2 hots from the generator need to be switched.
If the neutral and ground were bonded at the genset and switched with the hots in a transfer switch before the main panel, yes it would be a separately derived system, but that is not what is being discussed here.

Aaron Z
 
   / Generator in a outside building and powering the panel... #99  
It's where they draw the line with the code as the exemptions become too complex.
The Inspector was not concerned about sharing the neutral or the ground.
It all revolved around the definition of two sources in the same conduit. Which can occur if the gen set is operating and energizing the wires up to the breaker at the 200amp panel even though the generator breaker is still locked open at the 200amp panel. It's due to cable insulation faults in conduit, in particular underground conduit. Now the generator and utility can cross connect via the short.
There are a number of incidents commented on this site about underground cables going" Ka-Pow" due to time and environment. So the concern is real.
 
   / Generator in a outside building and powering the panel... #100  
It's where they draw the line with the code as the exemptions become too complex.
The Inspector was not concerned about sharing the neutral or the ground.
It all revolved around the definition of two sources in the same conduit. Which can occur if the gen set is operating and energizing the wires up to the breaker at the 200amp panel even though the generator breaker is still locked open at the 200amp panel. It's due to cable insulation faults in conduit, in particular underground conduit. Now the generator and utility can cross connect via the short.
There are a number of incidents commented on this site about underground cables going" Ka-Pow" due to time and environment. So the concern is real.

Is the inspector allowed to overrule this?


702.9 Wiring Optional Standby Systems. The optional standby system wiring shall be permitted to occupy the same raceways, cables, boxes, and cabinets with other general wiring.
 

Marketplace Items

2009 Bruton T/A Enclosed Livestock Trailer (A55973)
2009 Bruton T/A...
2007 CHEVROLET SILVERADO K1500 (A60430)
2007 CHEVROLET...
(1) UNUSED 31" X 8 MM EXCAVATOR TRACK W/ PIN (A60432)
(1) UNUSED 31" X 8...
SALTYS MANFUFACTURING 500BBL FRAC TANK (A58214)
SALTYS...
THREE POINT ATTACHMENT (A58214)
THREE POINT...
2009 MULTIQUIP 25KW GENERATOR (A58214)
2009 MULTIQUIP...
 
Top