There is a lot of info on motor starting methods such as this one:
Ron
Ron
You could try to reduce the inrush current. Most compressors have an unloader. The problem is that the pipe between the compressor and check value is short and the compressor quickly gets loaded while it's still ramping back up to speed. You could take it a step further by having the compressor just vent to atmosphere for a few extra seconds with an electric valve before closing so the motor starting up and the load of compressing air are separated.
As the title says, would here is running a 3 phase air compressor with a phase converter.
I acquired a joy twistair ta010. Not sure the cfm but it's pretty good. It will charge it's 80 gallon horizontal tank from 0 paid to 120 paid in about one minute flat.
But ran low on oil and locked up. So I am gonna look into a rebuild as it is a nice compressor.
It has a 10 hp motor.
I am no stranger to phase converters and vfd's.
I have a 10hp rotary that is running a mill and lathe currently. And another 15 hp rotary not used now. And a 5 hp vfd I use for the log splitter.
If I need to use the mill or lathe, it's no problem to just push the button and start the rotary.
However....the compressor I just want to be like my current one. Plugged in ready to do it's own thing whenever it needs to charge. Don't want to have to worry about starting a phase converter Everytime I want a little air, or Everytime it needs to kick on. But also don't want to leave the rotary running 24/7 either.
So those that are running a 3phase compressor off a converter.....what setup are you using?
What motor and pulley setup did you go with? And can you measure cfm? I need a bare MINIMUM of 28cfm, and probably 40cfm is better in my situation. But, Pretty sure running my 20hp spindle on the MILL (VMC) when the compressor kicks on will be bad, if I keep the compressor 3ph, as suggested. Sent a couple PM's. Did you get them?
I dont remember the motor I used. I think it was a marathon. But that dont really matter.
It was a 10HP 3450rpm motor. Same as the 3-phase that came off but just 240v single phase.
Forget all the talk of changing pulleys. I only was contemplating that because the airend (compressor head) is the SAME joy used on 3 different models. Ranging from 29 cfm when paired with 7.5hp, 40cfm when paired with 10hp and 60cfm when paired with 15HP. The ONLY difference in the three compressors other than more HP was changing pulleys to make the pump spin faster.
I was gonna drop to 7.5hp and change pulleys to basically have a TA007 compressor @ 29cfm. Because 7.5HP motors were cheaper.
You could go the other route and get a 15HP motor and spin the pump up to get 60cfm. Thats all the MFG did for their TA015 model.
And my 3m25s was from 0psi to 110
3m25s is ~23cfm. What kind of inrush amps are you measuring? What size breaker are you running it off of?
Best thing! I bought a BIG Lincoln Welder at an Auction by accident that was only three phase. I built a nice 10HP 600 Volt phase converter. Then got a drill/milling machine. What a pain to stop and start a phase converter. I sold everything 600 volt and bought a Lincoln 220 volt MIG. I don't even know how you would stop and start a rotocon for a compressor.