Propane tankless water heater

   / Propane tankless water heater #21  
inlet filter will help some. But as the water is heated, the minerals that are in the water will separate from the water and attach it's self to the water coil. You may have to flush the coil more than normal to prevent total blockage of the water coil.

I have attended several classes where they had cut aways of water coils completely blocked from mineral deposits. so I recommend a good flush depending on water quality

I use these as a treatment before the water enters the heater:


The fitting that these cartridges screw into was purchased at the local plumbing supply house and is specifically for this purpose.
 
   / Propane tankless water heater #22  
Installed a tankless water heater for our addition/remodel. We just moved in and I am having a hard time dealing with the wait times for hot water. A hot water tap about 15 feet from the hot water heater takes 40 seconds to get hot water, that is unacceptable in my opinion. I am going to have the plumber back out to see if is a setting on the heater. With the old tank water heater we never waited more than 10 seconds at this same exact sink location. So I do not understand why there is such an issue with wait time in the new system. The house has completely new supply lines, so it could be something in the design. I plan on insulating the hot water pipes and probably in the end add a recirculation pump to drop the hot water wait times to acceptable levels. I think this is just the nature of the beast. Advice about putting it as centrally located as possible is good advice. Good luck.
 
   / Propane tankless water heater #23  
Instead of a circulation pump, I wonder if anyone has ever looked at just mounting one of those very small hot water heaters downstream of one of these, as a maintainer. Energy usage in the tank would be very low, as the initial heating is done by the tankless, and it's only maintaining a small amount of water. I'm thinking here of the type usually designed to go under a sink or under a bar, although even one of those old "Insta-Hot" under-sink faucet heaters could probably improve performance.

Theory here is that even a very tiny water heater downstream of the tankless system would ensure quick delivery of hot water, while feeding it from the tankless would ensure endless supply... which is the primary downside of the traditional water heater. Depending on how small the tank is on this system, 0.5 gallons versus maybe 5 gallons, there would be a slight dip in temperature due to initial cold water filling into the tank from the tankless, as it comes online.


Of course a recirc system is instantly hot. But it also defeats a primary purpose of a tankless, in that the heater will be running very often when there's no demand, just keeping up with the losses of the recirc loop. I predict a substantial increase in operating costs, and a substantial decrease in component lifetime, when adding a recirc loop with no tank to a tankless system.
 
   / Propane tankless water heater #24  
Instead of a circulation pump, I wonder if anyone has ever looked at just mounting one of those very small hot water heaters downstream of one of these, the type usually designed to go under a sink or under a bar. Heck, even one of those old "Insta-Hot" faucet heaters, which I think run around 0.5 gallons, would totally resolve the problem.
Yes..... I installed a 5 gallon 110v electric WH in my crawl space just for that reason. The hot piping from the tankless goes to the inlet side of the 5 gallon elec. WH, and the out side is piped back into the hot water lines to my master bath. This way, about the time my 5 gallon 110v elect. is empty, the hot water from the tankless is there .
 
   / Propane tankless water heater #25  
Yes..... I installed a 5 gallon 110v electric WH in my crawl space just for that reason. The hot piping from the tankless goes to the inlet side of the 5 gallon elec. WH, and the out side is piped back into the hot water lines to my master bath. This way, about the time my 5 gallon 110v elect. is empty, the hot water from the tankless is there .
This sounds good, I would like to hear more about this. The main disadvantage about this over a recirc system is that it only works for the master bath, not at any of the rest of the taps.
Of course a recirc system is instantly hot. But it also defeats a primary purpose of a tankless, in that the heater will be running very often when there's no demand, just keeping up with the losses of the recirc loop. I predict a substantial increase in operating costs, and a substantial decrease in component lifetime, when adding a recirc loop with no tank to a tankless system.
This is the issue I fear with the recirc system. There are 2 types of recirc systems though. The one I would install is the bypass system. With this system you install a pump and valve at the furthest tap. The water gets pumped through the system and cold water is pumped back into the cold water side until the pump recognizes hot water in the system at which time it switches off. I think with good pipe insulation and a smart outlet or timer this system could be pretty efficient. Purging the cold water in the system during times of high demand (6am-10am and 5pm-11pm) with good insulation and hot water usage during this time the pump/heater would not have to run very much to keep up. That is what I am planning at this time.
 
   / Propane tankless water heater #26  
This is the issue I fear with the recirc system. There are 2 types of recirc systems though. The one I would install is the bypass system. With this system you install a pump and valve at the furthest tap. The water gets pumped through the system and cold water is pumped back into the cold water side until the pump recognizes hot water in the system at which time it switches off. I think with good pipe insulation and a smart outlet or timer this system could be pretty efficient. Purging the cold water in the system during times of high demand (6am-10am and 5pm-11pm) with good insulation and hot water usage during this time the pump/heater would not have to run very much to keep up. That is what I am planning at this time.
The only type I've ever seen deployed is this second type, and I predict problems, namely because the power output of the tankless heater is way too large to be an efficient maintainer of the relatively small but constant load that is this recirc loop. Think of it as starting a semi truck to drive 100 feet, then shutting it down, over and over all day long.

If you can adjust the hysteresis in the system to be very wide, then you might minimize the problems with this. But then your shower comfort goes way down, as the water temperature drifts and you need to constantly re-adjust the knobs. I also wonder where you're going to sense temperature in the recirc loop, to drive the firing circuit in the tankless system.

I'll admit I've never owned one of these, but on the surface, it really appears to me that a small water heater downstream of the tankless must be a much better solution. Simpler to plumb, as well.
 
   / Propane tankless water heater #27  
Recirculation systems used to be considered pretty high end stuff for residential homes.
 
   / Propane tankless water heater #28  
The only type I've ever seen deployed is this second type, and I predict problems, namely because the power output of the tankless heater is way too large to be an efficient maintainer of the relatively small but constant load that is this recirc loop. Think of it as starting a semi truck to drive 100 feet, then shutting it down, over and over all day long.

If you can adjust the hysteresis in the system to be very wide, then you might minimize the problems with this. But then your shower comfort goes way down, as the water temperature drifts and you need to constantly re-adjust the knobs. I also wonder where you're going to sense temperature in the recirc loop, to drive the firing circuit in the tankless system.

I'll admit I've never owned one of these, but on the surface, it really appears to me that a small water heater downstream of the tankless must be a much better solution. Simpler to plumb, as well.
I mean this system is no different than turning the hot water tap on and sitting there for 50 seconds until the hot water gets to that tap, washing your hands and then shutting it off. I do that 20 times a day already, how is this different? Sometimes I turn on the hot water tap to wash my hands and I shut it off before I even get hot water because I am sick of waiting.


Your tank only takes care of the issue at that one tap and nowhere else.
 
   / Propane tankless water heater #29  
I mean this system is no different than turning the hot water tap on and sitting there for 50 seconds until the hot water gets to that tap, washing your hands and then shutting it off. I do that 20 times a day already, how is this different? Sometimes I turn on the hot water tap to wash my hands and I shut it off before I even get hot water because I am sick of waiting.
Good point, on the runtime. But how are you sensing the temperature in the loop? Are you teeing it back into the inlet side of the tankless system, and just counting on the pressure differential created by the recirc pump to minimize mixing? I still see this as creating more short-cycling, than normal usage.

Your tank only takes care of the issue at that one tap and nowhere else.
Not if tank is installed before first tee, or separate tanks for the branch to each floor, etc. Still resolves issue of differential time, waiting for tankless to heat up, as compared to former tanked system.
 
Last edited:
   / Propane tankless water heater #30  
Good point, on the runtime. But how are you sensing the temperature in the loop? Are you teeing it back into the inlet side of the tankless system, and installing a check valve upstream of that in cold supply to minimize mixing?


Not if tank is installed before first tee, or separate tanks for the branch to each floor, etc. Still resolves issue of differential time, waiting for tankless to heat up, as compared to former tanked system.
There is a valve in the pump that senses temperature in the line. The pump turns on at 85 deg and turns off at 105 degrees. The excess water is pumped back into cold supply line.

Yes, that is what I was thinking, if the tank/tanks were centralized this would help that.

I have to figure out some solution because waiting 50-60 seconds is unacceptable in my opinion. Lots of wasted water and time.
 
   / Propane tankless water heater #31  
I feel like there has to be something not setup right causing this.
Even the sink that is literally 4 feet from the heater takes 40 seconds to get hot. So I am hoping we can figure out the issue and make it hit the taps in less time.
 
   / Propane tankless water heater #32  
There is a valve in the pump that senses temperature in the line. The pump turns on at 85 deg and turns off at 105 degrees. The excess water is pumped back into cold supply line.

Yes, that is what I was thinking, if the tank/tanks were centralized this would help that.

I have to figure out some solution because waiting 50-60 seconds is unacceptable in my opinion. Lots of wasted water and time.
Okay, I could see this working, with a thermostat having a side differential on the pump itself. I was imagining a pump running all the time, and the tighter-differential thermostat in the heater itself working against this.

So then you have to be selective in where you install the pump, I guess? You'd probably want it closer to your point of use, if the thermostat is in the pump.

I feel like there has to be something not setup right causing this.
Even the sink that is literally 4 feet from the heater takes 40 seconds to get hot. So I am hoping we can figure out the issue and make it hit the taps in less time.
I've heard others (see post about my neighbor) reporting similar times, even for appliances close to the heater.
 
   / Propane tankless water heater #33  
Anyway to the OP take this is consideration. Our house is not very big and this time to tap is an issue. If you live in a big house or in a colder climate it could get much worse. I have since installing mine done more digging and lots of people have it much worse than we do. These things were not designed for large American style houses. They were designed for small apartments or flats where the pipes are more centrally located with much shorter runs.
At this point I have a bit of buyers remorse. I hope I can figure out a solution.
 
   / Propane tankless water heater #34  
Okay, I could see this working, with a thermostat having a side differential on the pump itself. I was imagining a pump running all the time, and the tighter-differential thermostat in the heater itself working against this.

So then you have to be selective in where you install the pump, I guess? You'd probably want it closer to your point of use, if the thermostat is in the pump.


I've heard others (see post about my neighbor) reporting similar times, even for appliances close to the heater.
Yessir! Installed at furthest faucet.
 

Attachments

  • Screenshot 2024-12-03 at 11.18.21 AM.png
    Screenshot 2024-12-03 at 11.18.21 AM.png
    1.2 MB · Views: 77
   / Propane tankless water heater #35  
Yessir! Installed at furthest faucet.
I have the same pump installed on our water tank, with a polymer bypass sensor at a remote tap. The pump is on a timer, and runs a few times a hour. It keeps the water warm at the remote tap for things like handwashing.

This version works well for tankless water heaters, and often the outlet is switched hopefully with a flip flop timer. That way you turn on the pump, listen for it to stop and use the hot water.

Because tankless hot water can vary a bit on temperature as demand shifts, I like shower valves that are temperature sensing, either mechanical or electronic, to keep the shower temperature (more) stable.

And yes, I do agree with that I think tankless work better in overseas situations where the homes are smaller, plumbing often added after the home was built, resulting in shorter hot water runs, often only a few feet. But, in many areas with harder water, the expectation is that there will be 3rd party maintenance, with plumbers stopping by (semi) annually as a service check to flush the exchangers, recirculate cleaning agents, and put the water heater back on line. It is a trade off for not having water softeners, and supported by less of a DIY culture (or by law) in many areas, at least in my opinion.

All the best,

Peter
 
   / Propane tankless water heater #36  
Yessir! Installed at furthest faucet.
I like that setup. I had been considering running one on my own, but was looking at doing a return line from the hot supply side back to the water heater, all in sweated copper. This makes much more sense.

But searching, most of what I'm finding is 3/4" NPT and capable of up to 10 bars pressure. Total overkill. Where'd you find that little guy?

Something that can be wall-mounted in the back of the cabinet under the sink, with 3/8" compression hose fittings to tees at the supplies like you have shown, appears to be ideal for this.

My coffee bar and pantry sink are about 60 feet from our kitchen and water heater, so it's a reasonably long loop (120' round trip) that I'll be heating. Pipe insulation is in my near future.
 
   / Propane tankless water heater #37  
I like that setup. I had been considering running one on my own, but was looking at doing a return line from the hot supply side back to the water heater, all in sweated copper. This makes much more sense.

But searching, most of what I'm finding is 3/4" NPT and capable of up to 10 bars pressure. Total overkill. Where'd you find that little guy?

Something that can be wall-mounted in the back of the cabinet under the sink, with 3/8" compression hose fittings to tees at the supplies like you have shown, appears to be ideal for this.

My coffee bar and pantry sink are about 60 feet from our kitchen and water heater, so it's a reasonably long loop (120' round trip) that I'll be heating. Pipe insulation is in my near future.

Yes, I will be adding insulation to all of my hot water pipes as well.
 
   / Propane tankless water heater #38  
I like that setup. I had been considering running one on my own, but was looking at doing a return line from the hot supply side back to the water heater, all in sweated copper. This makes much more sense.

But searching, most of what I'm finding is 3/4" NPT and capable of up to 10 bars pressure. Total overkill. Where'd you find that little guy?

Something that can be wall-mounted in the back of the cabinet under the sink, with 3/8" compression hose fittings to tees at the supplies like you have shown, appears to be ideal for this.

My coffee bar and pantry sink are about 60 feet from our kitchen and water heater, so it's a reasonably long loop (120' round trip) that I'll be heating. Pipe insulation is in my near future.
To get tankless water heaters to kick on, there is a minimum flow that varies amongst the units.

That said try searching for Grundfos. They are the primary manufacturer of these pumps, both residential and commercial, and related pumps.

All the best,

Peter
 
   / Propane tankless water heater #39  
Did a bit of hunting on these pumps. Lots of no-name crap out there, but the major brands all seem to include a timer I wouldn’t want or need. Any recommendations for a pump with thermostat only, and no timer? I’d rather manage timing by my home automation system, than have another independent timer to keep on schedule though every power outage.
 
   / Propane tankless water heater
  • Thread Starter
#40  
Anyway to the OP take this is consideration. Our house is not very big and this time to tap is an issue. If you live in a big house or in a colder climate it could get much worse. I have since installing mine done more digging and lots of people have it much worse than we do. These things were not designed for large American style houses. They were designed for small apartments or flats where the pipes are more centrally located with much shorter runs.
At this point I have a bit of buyers remorse. I hope I can figure out a solution.
I live in a big house and already wait for hot water. So waiting for a tankless heater won't bug me. I already looked into a recirc. system and nixed the idea. Too much energy wasted.
Eric
 

Tractor & Equipment Auctions

Honda EM3500S Portable Gasoline Generator (A59228)
Honda EM3500S...
Commercial truck Frame with Axle (A59230)
Commercial truck...
2014 Cadillac ATS Sedan (A59231)
2014 Cadillac ATS...
2013 Godwin Dri-Prime CD103M Towable Trash Pump (A59228)
2013 Godwin...
1969 VOLKSWAGEN BUG (A59905)
1969 VOLKSWAGEN...
2015 CATERPILLAR 308E2 CR EXCAVATOR (A60429)
2015 CATERPILLAR...
 
Top