GaryBDavis
Below is a write up of my generator hookup. If there is something I've missed, please let me know. Constructive feedback is welcomed!
Important Notice
An incorrect generator hookup could possibly energize the power company's transmission line creating an illegal and dangerous situation. Any generator hookup should be approved by the local power company and installed in accordance with local and national codes. All work should be performed under the supervision of a licensed electrician. This write up makes available conceptual plans and information that can be helpful in selecting equipment for various applications. These plans do not necessarily represent the most current technology, applicable laws or safety standards. They are not engineered plans and do not replace the need for competent design assistance in developing a safe, legal and well-functioning apparatus. Gary B. Davis does not warranty these plans.
When I built my new house, I planned for a generator hookup that could be connected at the meter loop. I initially wanted to install a transfer switch, but one capable of handling 320 Amps cost several hundred dollars. Instead I settled on mechanical interlock kits and feedback breakers installed on the main feed-through panels.
Electrical Service
My electrical service is 320 Amp single phase. I have two 200 Amp feed-through breaker panels installed at the meter loop. One panel serves the house and the other serves the shop. Each feed-through panel has a 200 Amp main breaker, a few slots for standard type breakers, and secondary lugs that feed the service through to the house and shop. At the house and shop, there are 200 Amp/40 position main lug panels. Main lug panels are panels with no main breaker as they are protected by the main breakers in the feed-through panels mounted at the meter loop.
Mechanical Interlock and Feedback Breakers
The concept behind a mechanical interlock kit and feedback breaker is this: the power from the generator is fed back into the breaker panel from a standard breaker. Instead of connecting the feedback breaker to a load, it is connected to the generator. Current is passed backward through the breaker where it energizes the panel. However, the main breaker must be turned off to prevent power from the power company energizing the panel at the same time as the generator. This is where the mechanical interlock comes into play. A mechanical interlock is a simple sliding plate that prevents the main breaker and the feedback breaker from being turned on at the same time. Only one or the other can be on at any given time. In the particular setup, the feedback breaker must be installed in the top-right position.
A feedback breaker should never be used without a mechanical interlock that prevents both the main breaker and feedback breaker from being turned on at the same time. Interlock kits are not available from all manufacturers for all models. I used SquareD QO series panels. I recommend using an interlock kit that is made by the same manufacturer as the breaker panel and is listed as a compatible item.
Generator Inlet
The two-pole, 50Amp feedback breakers in the main panels feeding the house and shop are connected to a generator inlet installed at the meter loop. This inlet is made by Midwest and contains a 50 AMP 125/250V 3-Pole 4-Wire Grounding Non-NEMA locking connector. This connector is angled and the cover can be closed with the power cable plugged in. It is rated for NEMA 3R while "in use". This means its rain tight and outdoor rated even while the power cable is plugged in.
Generator
The power source is a Miller Trailblazer 302 portable welder with a built in generator rated for 10,000 Watts. Ithas a 50Amp 125/250V NEMA 14-50 outlet. This is the same 50 Amp outlet you see at RV campgrounds.
Grounding
The generator inlet has a dedicated ground wire leading to the ground rod installed at the meter loop. There are also dedicated ground wires from the meter base and each main panel leading to the same ground rod. The house and shop each have their own ground rods as there is no common grounding between the meter loop, house and shop. When the generator is providing power, it has the same grounding scheme as when service is coming from the power company.
Applying The Load
The 10,000 Watt generator won't provide enough power to run everything in the house. So, you have to pick and choose which items you turn on. However, since the generator connects at the main panel, you can pick any combination of items to run just as long as you don't overload the generator.
Pilot Lamp
One drawback of turning off the main breaker is that you don't have a way to tell when power has been restored. Since I live in a rural area, I cannot see any of the neighbor's house lights to indicate power is back on. To solve that issue, there is a pilot lamp installed in one of the main panels. It is fused directly off the meter base feed and operates independently of the main breaker. When the power company is providing power, the lamp is on. It is a very low Wattage bulb and draws very little electricity.
Portable Power Pedestal
Sometimes I take the generator to off-site locations to provide temporary power. In these situations, I use a portable power pedestal. This allows me to place the generator a bit further away from the application to keep the noise down, etc. The pedestal consists of a 50 AMP 125/250V 3-Pole 4-Wire Grounding Non-NEMA locking inlet, two-pole 40 Amp 24 hour timer, breaker panel with four 20 Amp GFI breakers and standard NEMA 5-15 outlets. All items are rated for NEMA 3R while "in use". This makes the pedestal operational during rain, snow, sleet, etc. The 50 Amp inlet is a different style from the meter loop, but when used in conjunction with a matching connector mated with a rubber cover, it is NEMA 3R while "in use". There are two types of standard 5-15 outlets one quad box with a wet location cover and four corded outlets with rain tight rubber covers.
The reason for having a main timer is so that the pedestal can be used for temporary seasonal light displays. For example you could run a Christmas light display where the timer turns the power on at 5:00PM and off at midnight. The pedestal can be plugged into any 50 Amp RV outlet as well as a generator.
Important Notice
Electrical Service
Generator Inlet
Generator
Grounding
Applying The Load
Pilot Lamp