Electrical through concrete foundation

/ Electrical through concrete foundation
  • Thread Starter
#21  
Turns out that for my footing (only 12" below grade) I must use rigid conduit rather than PVC. That stuff is pretty expensive and it seems to me it's just going to rust out eventually, but there it is.

Anyway, I'm told I need to run three #3 TNNH wires and a #8 TNNH for ground to have 100AMP service and 220.

Cliff
 
/ Electrical through concrete foundation #22  
you probably only have to use rigid where it comes through the floor. Ask more questions to be certain as to what the local regulations are . In this part of CT, I would have needed to use rigid (steel) sweeps and risers on the poles if there was a possibility that it could be struck by a car. Since my pole is in a lawn area, this requirement was waived. Possibly Inspector 507 can give us some guidance as to what code requires. He is our resident expert when it comes to electrical code requirements. /forums/images/graemlins/smile.gif
 
/ Electrical through concrete foundation #23  
</font><font color="blue" class="small">( Here in north Texas, in every house I've seen, electric service comes out of the ground outside the building, up through conduit to a breaker box. This breaker box is then connected through the wall to the service panel inside the building (or garage) where the individual circuit breakers are installed.)</font>

That's all about meter reading. The meter needs to be where the reader can see it. So they always put the meter base on an outside wall with conduit to the breaker panel inside.
 
/ Electrical through concrete foundation #24  
Cliff,
PVC going to your service needs to be 18" below grade but Rigid Metallic Conduit only needs to be 6" below grade.
If they are asking for RMC, then ask if you can use Schedule 80 PVC. It is approved for areas that may be subject to physical damage.
If you decide to use the rigid only where it comes through the floor, extend it all the way up to the new box so it can be bonded/grounded. If you only have the rigid in the middle of the PVC run, that could be a problem.
 

Marketplace Items

48in Forks and Frame Skid Steer Attachment (A56857)
48in Forks and...
2018 FREIGHTLINER M2 FORESTRY UTILITY BUCKET TRUCK (A59823)
2018 FREIGHTLINER...
2017 Ford Transit Connect Cargo Van (A59230)
2017 Ford Transit...
2021 Chevrolet Silverado 1500 4x4 Crew Cab Pickup Truck (A59230)
2021 Chevrolet...
2014 Chevrolet Impala Limited Sedan (A59231)
2014 Chevrolet...
2004 Ford F-150 Ext. Cab Pickup Truck (A59230)
2004 Ford F-150...
 
Top