Electrical Service Question

/ Electrical Service Question #1  

Believer

Silver Member
Joined
Aug 17, 2008
Messages
164
I have a 200 amp disconnect at the meter on the utility pole. I have a 100 amp main lug panel on a house that's 200 feet away. Is the run from the disconnect to the main lug considered a service entrance or a feeder? If I understand correctly, a service entrance can be direct bury but a feeder must be in conduit. Is that correct? Thanks.
 
/ Electrical Service Question #2  
Here anything after the meter belongs to you. The power company doesn't look at it or even care, you can run it across the grass. For residential you can do the work yourself and no inspection is required. If you hire an electrician then he/ she needs to do it to code. You will not be given the choice when it comes to the wire going to the meter, your power company will tell you what size conduit is needed.

Personally I wouldn't run the wire between the meter and my service panel underground not in conduit. The extra cost really isn't that much. If you damage the wire while backfilling the trench , even if it's not enough to cause an issue right off down the road you could have problems that'll cost you much more to dig it back up to repair it.
 
/ Electrical Service Question #3  
I have a 200 amp disconnect at the meter on the utility pole. I have a 100 amp main lug panel on a house that's 200 feet away. Is the run from the disconnect to the main lug considered a service entrance or a feeder? If I understand correctly, a service entrance can be direct bury but a feeder must be in conduit. Is that correct? Thanks.

Technically any breaker panel other than the main disconnect is considered a sub-panel. A service entrance is referring to the drop from the transformer into the meter base. A feeder is ANY wire run between the service equipment and the final branch circuit overprotection device (for example if an air cond unit has a fused disconnect, the wire leading from the breaker panel to the disconnect is referred to a feeder). Now if that same a/c unit has an un-fused disconnect, then the wire leading to the disconnect is considered a branch circuit. All pretty confusing aint it. These differences allow for different wire size and ratings allowed. They don't effect what needs conduit and what doesn't.

Terminology aside, there is no rule as to what needs to be in conduit and what doesn't need to be. I personally never install without conduit (I'm an electrical contractor), as the minor extra cost saves me the headache of damaging direct bury wires. Any nick that penetrates into aluminum direct bury wires WILL cause the wires to degenerate.

The house panel should have its own main breaker. Depending on whether you have any local codes saying otherwise, there are varying depth requirements for tranches. If its under a driveway it will be different than if its under the backyard, etc. Conduit burial depths are generally not as deep as direct burial (except under driveways). For instance a 100 amp service run direct buried requires 24" depth, but only 18" if in conduit. I personally use URD rated direct bury wires AND place then in conduit. The urd have heavier insulation and this gives added protection.
 
/ Electrical Service Question #4  
I have a 200 amp disconnect at the meter on the utility pole. I have a 100 amp main lug panel on a house that's 200 feet away. Is the run from the disconnect to the main lug considered a service entrance or a feeder? If I understand correctly, a service entrance can be direct bury but a feeder must be in conduit. Is that correct? Thanks.

Do it with underground trench lay wire, expensive wire, plus put it in a plastic 3/4 conduit with a extra separate ground. The cost of 200' of plastic conduit is very little and the extra ground is the current standard in michigan and probably most states. Do it right and pay very little more.---Fuseboxer
 
/ Electrical Service Question #5  
Do it with underground trench lay wire, expensive wire, plus put it in a plastic 3/4 conduit with a extra separate ground. The cost of 200' of plastic conduit is very little and the extra ground is the current standard in michigan and probably most states. Do it right and pay very little more.---Fuseboxer

I've been following this thread with interest, since I may do a similar thing myself. Why the extra ground, and what does that consist of - just a separate insulated strand of solid copper wire?
 
/ Electrical Service Question #6  
Do it with underground trench lay wire, expensive wire, plus put it in a plastic 3/4 conduit with a extra separate ground. The cost of 200' of plastic conduit is very little and the extra ground is the current standard in michigan and probably most states. Do it right and pay very little more.---Fuseboxer


Most states are still on 2008 code and that requires 4 wires (2 hot 1 neutral 1 ground) to the sub panel with the neutral not bonded to the panel. and grounds driven at both places.

whats is the plastic conduit for if you are using direct burial ("expensive wire" your term)

I'm with grsthegreat on conduit install pull the wire (4 of them) put an extra conduit in too I use 1" most of the time for the extra conduit the power run sized for the wires used rounded up 1 or 2 sizes for easier pulling.

tom
 
/ Electrical Service Question #7  
Why the extra ground, and what does that consist of - just a separate insulated strand of solid copper wire?[/QUOTE]

Check with your electrical supply house in your state or possibly a good Home Depot/Lowes electrical department manager. The second[U] separate ground [/U]is code in Michigan and was explained to me years ago. I do it but do not remember all the reasons why. ---Fuseboxer
 
/ Electrical Service Question #8  
Most states are still on 2008 code and that requires 4 wires (2 hot 1 neutral 1 ground) to the sub panel with the neutral not bonded to the panel. and grounds driven at both places.

whats is the plastic conduit for if you are using direct burial ("expensive wire" your term)

I'm with grsthegreat on conduit install pull the wire (4 of them) put an extra conduit in too I use 1" most of the time for the extra conduit the power run sized for the wires used rounded up 1 or 2 sizes for easier pulling.

tom

You are 100% correct. I use direct burial in 1" conduit, overkill.
 
/ Electrical Service Question #9  
First off I'm not sure how many amps the OP is wanting to run to the shop. If its 100 amps, you'll need 1-1/4" conduit and 2/2/4 alum wire with a #6 alum ground wire. ( I personally usually upsize the wires i run to a 1/1/2 urd....very little difference in overall cost, but helps with voltage drop)

All sub-panels (shop) require a separate ground run to it from the main panel, and a separate ground rod driven at the shop panel. The reason for this is cause dry earth may provide too high of resistance for a ground short circuit to reach the main breaker and trip it. so the wire provides a low resistance path back to the source.

If the shop only needs a 50 amp service you can use 1" conduit and 6/6/8 URD but still need a #6 ground wire.. Personally 2/2/4 URD isn't very expensive, so id run it even if you only want 50 amp service. Good for future increase and for less voltage drop (although 200' shouldn't be an issue with voltage drop).
 
/ Electrical Service Question #10  
I have a 200 amp disconnect at the meter on the utility pole. I have a 100 amp main lug panel on a house that's 200 feet away. Is the run from the disconnect to the main lug considered a service entrance or a feeder? If I understand correctly, a service entrance can be direct bury but a feeder must be in conduit. Is that correct? Thanks.

OK guys lets back up a bit.. The OP says he has a 200 amp disc. going to a 100amp panel hmm...:confused: better to start with that problem before anything else..:confused2:
 
/ Electrical Service Question #11  
OK guys lets back up a bit.. The OP says he has a 200 amp disc. going to a 100amp panel hmm...:confused: better to start with that problem before anything else..:confused2:

That parts a little confusing. Ive seen 200 amp disconnects with multiple breakers (say 100 amp) to feed other buildings. Im not sure how a 200 amp disconnect can feed a 100 amp lug. unless he means a 200 amp lug?

its soo easy to get off course on these chat rooms.
 
/ Electrical Service Question #12  
OK guys lets back up a bit.. The OP says he has a 200 amp disc. going to a 100amp panel hmm...:confused: better to start with that problem before anything else..:confused2:

If the wiring going to the 100 amp panel is sized for 200 amps would there still be a problem?

I'm curious because I may end up with this scenario depending on placement of future buildings.
 
Last edited:
/ Electrical Service Question #13  
If the wiring going to the 100 amp panel is sized for 200 amps would there still be a problem?

I'm curious because I may end up with this scenario depending on placement of future buildings.


You can over wire the panel but it has to have protection = main breaker in the sub panel to limit the current in the panel to 100a.
This also means the correct lugs on the main breaker to take the 200a wire some times they won't.
You cant trim the wires to fit the lugs because you are reducing the capicity of the wire and wire has a ring effect = more current travels on the outside of the wire than the center and when people trim wires guess what ones get trimmed first. there are transition crimp lugs that cam be used to change size at sub panel.

larger wire sizes are done for long runs to minimize voltage drops.

tom
 
/ Electrical Service Question
  • Thread Starter
#14  
Oops. I left out an important part when I originally started the thread. Let me try again.

At the utility pole. Meter wires to a 200 amp disconnect. I will be wiring from the 200 amp disconnect to a 200 amp main lug on the utility pole, so just a couple feet of wire. In that main lug, I'll have circuit protection for the feeder to the house.

From that main lug on the utility pole, I need to go underground 200 feed to the 100 amp main lug on the house. I wasn't planning to have a main breaker at the house (old house we use as a cabin really). I don't really need 100 amps, probably 50 would be fine, but the 100 main lug was really all I could find at Home Depot that had enough circuits. I'm trying to figure out what specification of wiere, CU or AL, and whether I should direct bury or run in conduit.

At a later date, I will run another feed from the main lug on the utility pole out to the barn.
 
/ Electrical Service Question #15  
Oops. I left out an important part when I originally started the thread. Let me try again.

At the utility pole. Meter wires to a 200 amp disconnect. I will be wiring from the 200 amp disconnect to a 200 amp main lug on the utility pole, so just a couple feet of wire. In that main lug, I'll have circuit protection for the feeder to the house.

From that main lug on the utility pole, I need to go underground 200 feed to the 100 amp main lug on the house. I wasn't planning to have a main breaker at the house (old house we use as a cabin really). I don't really need 100 amps, probably 50 would be fine, but the 100 main lug was really all I could find at Home Depot that had enough circuits. I'm trying to figure out what specification of wiere, CU or AL, and whether I should direct bury or run in conduit.

At a later date, I will run another feed from the main lug on the utility pole out to the barn.

Have you bought your meter socket yet or does the utility company supply it? The reason I ask is there is a panel called a meter main. It contains the meter socket and main breaker in the same enclosure. It also has spaces for a few more additional breakers just like a breaker panel would.
 
/ Electrical Service Question #16  
You can over wire the panel but it has to have protection = main breaker in the sub panel to limit the current in the panel to 100a.
This also means the correct lugs on the main breaker to take the 200a wire some times they won't.
You cant trim the wires to fit the lugs because you are reducing the capicity of the wire and wire has a ring effect = more current travels on the outside of the wire than the center and when people trim wires guess what ones get trimmed first. there are transition crimp lugs that cam be used to change size at sub panel.

larger wire sizes are done for long runs to minimize voltage drops.

tom

Thanks for answering my over wire question. The larger wires would be terminated in a properly sized disconnect for a future building before reaching the 100 amp panel so no need for wire trimming.
 
/ Electrical Service Question #17  
If the wiring going to the 100 amp panel is sized for 200 amps would there still be a problem?

I'm curious because I may end up with this scenario depending on placement of future buildings.

If the breaker in your disconnect that is after the meter is 200 amp and panel that it is feeding is rated for 100 amps then yes you have a problem.. The wire size as you have been told has nothing to do with it,, It is common to use bigger sized wire to overcome voltage drop..

There is a very simple solution to your problem if all you need is 100 amps in your house...
 
/ Electrical Service Question #18  
If the main breaker on the meter pole is 200 amps, then you HAVE to supply wire off of it that can carry 200 amps (ie: 4/0 alum or 2/0 copper). If however you can downsize the breaker at the meter pole to 100 amps, then you can size the wire to the house accordingly (#1 or #2 alum.) Mind you if you plan on running 200 amps to a future house than you will need to run the heavier wire now. You cant simply install a 100 amp panel in the house and say its protected to only 100 amps if its being fed from a 200 amp breaker. It doesnt work that way. You size the wire according to the breaker that supplies the load.

That being said, you HAVE TO have a main breaker panel at the house. you cannot use a main lug panel (legally) unless its within the same building that houses the main breaker panel (ie: a subpanel). iF YOU PLAN ON REBUILDING AT A LATER DATE AND INSTALLING A 200 AMp service, than install a 200 amp main breaker panel at this time, and you can re-use it on the new house. If the job isnt being inspected....then i guess you can do what you want with regards to the panel, but your insurance wont cover you if theres a fire.
 
/ Electrical Service Question #19  
Oops. I left out an important part when I originally started the thread. Let me try again.

At the utility pole. Meter wires to a 200 amp disconnect. I will be wiring from the 200 amp disconnect to a 200 amp main lug on the utility pole, so just a couple feet of wire. In that main lug, I'll have circuit protection for the feeder to the house.

From that main lug on the utility pole, I need to go underground 200 feed to the 100 amp main lug on the house. I wasn't planning to have a main breaker at the house (old house we use as a cabin really). I don't really need 100 amps, probably 50 would be fine, but the 100 main lug was really all I could find at Home Depot that had enough circuits. I'm trying to figure out what specification of wiere, CU or AL, and whether I should direct bury or run in conduit.

At a later date, I will run another feed from the main lug on the utility pole out to the barn.
Whatever you decide, do yourself and anyone who comes along behind you a BIG favor and bury your service in conduit.:thumbsup:
 
/ Electrical Service Question
  • Thread Starter
#20  
OK, I need a main breaker in the subpanel at the house. Someone mentioned I had a problem on the utility pole. On the utility pole, I have the meter and 200 amp disconnect. I will wire from the 200 amp disconnect to a 200 amp main lug using a wire with the correct ampacity--no problem here is there? In the main lug I will install circuit protection for the feeder to the house. What type of wire should I use from the main lug on the utility pole to the house? Thanks.
 
 