Cut underground electrical line question

/ Cut underground electrical line question #1  

gmason

Platinum Member
Joined
Nov 15, 2000
Messages
585
Location
NC
Tractor
NH TC35D4
About 8 years ago I cut the in ground power line(120v 20A) to my septic tank high water alarm with a tiller. Needless to say it was a mess. I spliced it the best i could do back then, I had to add about a 4ft piece of in ground rated electrical line. I soldered the wires and use shrink tubing and some die-electric paste. Still recently, the alarm failed and I tested the voltage on the wires coming into the box and found that the voltage getting to the box was only in the 10v range.

I dug up the line where the splices were made and found that the voltage at the splice was a little better at 24v max, still nowhere near 120v.

Now when I cut the line to test the voltage i found that there was some moisture inside the wire insulation and the copper had the green corrosion on the surface. I dug up another 2ft back on the line and cut it there too and got 35v max and the copper was still green.

I've got about 75ft left to the get to the house and just wondering if there are any ideas of what I should do. I'm very much just considering trenching a whole new line, a little deeper this time.

Can anyone tell me what might have happened, my guess is that the water found it's way up the line and found a place to short out the wire, but without digging the whole thing up, I don't know how I'd find it. I know coming out of the house it's 120v.

thanks
gary
 
/ Cut underground electrical line question #2  
gmason said:
About 8 years ago I cut the in ground power line(120v 20A) to my septic tank high water alarm with a tiller. Needless to say it was a mess. I spliced it the best i could do back then, I had to add about a 4ft piece of in ground rated electrical line. I soldered the wires and use shrink tubing and some die-electric paste. Still recently, the alarm failed and I tested the voltage on the wires coming into the box and found that the voltage getting to the box was only in the 10v range.

I dug up the line where the splices were made and found that the voltage at the splice was a little better at 24v max, still nowhere near 120v.

Now when I cut the line to test the voltage i found that there was some moisture inside the wire insulation and the copper had the green corrosion on the surface. I dug up another 2ft back on the line and cut it there too and got 35v max and the copper was still green.

I've got about 75ft left to the get to the house and just wondering if there are any ideas of what I should do. I'm very much just considering trenching a whole new line, a little deeper this time.

Can anyone tell me what might have happened, my guess is that the water found it's way up the line and found a place to short out the wire, but without digging the whole thing up, I don't know how I'd find it. I know coming out of the house it's 120v.

thanks
gary

I can't recall if it is voltage that drops or amperage that drops when corssion comes in. Example- A battery cable that is corroded inside that goes from battery to starter. Battery could be 100% new and charged and sometimes there is enough resistance and breakdown of the copper that the current will not get to the starter- acts like battery is low or starter is bad. It's happened to me. I thought the cable was clean and then I looked under the insulation....OPPPS. Put a brand new one on.... thing turned over like it was a stuck pig.

Just for kicks, check it at the panel......

My suggestion, replace ALL of the line with new stuff rated for being burried. If you damanged it w/ a tiller (don't know what kind), but that seems really shallow. Even a 3pt tiller might get 8-11" down. I suggest trenching at least 18"-24" if you plan to to be gardening above the line.... if not deeper.
 
/ Cut underground electrical line question #3  
Well a cable trace probe could probably locate the bad spot within a few feet, but with that much past damage and the water intrusion you have noted, it is probably just better to lay in a new line. I mean you could dig and sweat and fix the problem on the old line(and seal every place you test) only to have the water weep a few more feet along and short it out again in a few weeks or a year. A new cable will be more work and cost, but you will only have to do it once... And running it deeper is a very good idea:)
 
/ Cut underground electrical line question #4  
The wire has either corroded open or shorted. Sounds like it could be open. You should be certain to use UF rated wire for direct burial. As stated earlier, you really should replace the entire run. Per code, direct burial cable needs to be at least 24" deep, so dig down. If you do need to do any buried splices, which I would recommend against, use the splice kits that are made for submersed wells. It is a crimp connector that uses a heat shrink rubber sleeve that is filled with a heat melt glue. When you heat the sleeve, it melts the glue and makes a solid water proof joint.

paul
 
/ Cut underground electrical line question #5  
The way I read it the line has been there for a long time 10 12 yrs. Far better and easier to just lay a new line.
 
/ Cut underground electrical line question #6  
Jimbrown said:
The way I read it the line has been there for a long time 10 12 yrs. Far better and easier to just lay a new line.
Yeah, I wouldn't be surprized if the corrosion extends through practically the whole line. The corrosion will drop both the voltage and current through the line. By the way, did you use acid core solder on the wires? That's a big no-no, and maybe part of the problem. You should only use rosin core solder on wire. Save the acid for copper tubing.

Mike
 
/ Cut underground electrical line question #7  
I would replace the whole run also. It doesn't take much moisture in a wire to destroy the whole thing. The wire acts just like a candle wick drawing moisture along it's length.
 
/ Cut underground electrical line question
  • Thread Starter
#8  
techman said:
The wire has either corroded open or shorted. Sounds like it could be open. You should be certain to use UF rated wire for direct burial. As stated earlier, you really should replace the entire run. Per code, direct burial cable needs to be at least 24" deep, so dig down. If you do need to do any buried splices, which I would recommend against, use the splice kits that are made for submersed wells. It is a crimp connector that uses a heat shrink rubber sleeve that is filled with a heat melt glue. When you heat the sleeve, it melts the glue and makes a solid water proof joint.

paul

Paul,thanks for the info, do you have a web link to these splice kits or what they are called? I've used that black dielectric glue/sealer with some great results. stays wet for a while, but does a great job of sealing up the exposed copper. any comments on that stuff?
gary
 
/ Cut underground electrical line question #9  
gmason said:
Paul,thanks for the info, do you have a web link to these splice kits or what they are called? I've used that black dielectric glue/sealer with some great results. stays wet for a while, but does a great job of sealing up the exposed copper. any comments on that stuff?
gary

I've seen them at Home Depot in the plumbing area.

You can also look here:

well splice kit - - SHOP.COM

paul
 
/ Cut underground electrical line question #11  
Next time consider running conduit and THWN rated wire for underground circuts. THWN is rated for wet locations, and by runnning conduit you can always pull new wire if the need arises.
 
/ Cut underground electrical line question #12  
I would say that you are lucky that it burned open on you. That moisture is either carrying your voltage to ground through the hot leg and spinning your electrical meter, or has opened the neutral. In my earlier career I worked in the electrical distribution area of the electric utility. Most underground wires were aluminium. If water got to the aluminum it would turn to boxite and not conduct electricity. When we would dig up the fault the ground would be hot and steaming. The advice to put the wire in conduit is valid, and don't put any spices underground of you can avoid it.
 
/ Cut underground electrical line question
  • Thread Starter
#13  
to fix a couple of points here... the builder put the line in the ground and not me originally. I would have put it much deeper yes.

I haven't trenched for a new line as yet, so all of your advice has been very helpful

thanks
gary
 
/ Cut underground electrical line question #14  
gmason said:
to fix a couple of points here... the builder put the line in the ground and not me originally. I would have put it much deeper yes.

I haven't trenched for a new line as yet, so all of your advice has been very helpful

thanks
gary
I am a electric lineman and have been for 30 years.I have worked on faults in underground wire many times.IMHO I would lay new wire in conduit verses trying to repair the old wire as it will proable fault again.I layed some new wire from my barn out to a new light pole,you would be amazed how well a 1 bottom plow works for plowing a trench.coobie.
 
/ Cut underground electrical line question #15  
I am with Coobie on this one. If you are going through all that effort, just do it right...and put new wire in conduit! And it's also a good idea to leave a run of extra cable cord inside the conduit with your wire. Then, in the future, you have the option and ability to be able to pull another wire out to the alarm if you ever have a need to for whatever reason.

When I bought my house, the wire to my well was buried using the direct burial method without conduit. I had to replace it for the same reasons as you. I ran new cable inside of conduit. All it takes is a nick somewhere along the cable run when it is directly buried to mess up the cable. Water will wick inside causing corrosion and after several years it will have to be replaced.

I imagine the earthworms will finally come back home!
 
Last edited:
/ Cut underground electrical line question #16  
Is this a pump tank alarm or a ATU alarm. Can you find a name plate on the alarm panel. You need to start by testing the float switch first. Make sure that is still working. There should be a J box inside the pump tank. Give us more info.
 

Marketplace Items

FERGUSON PEANUT RE SHAKER, 3PT (A62130)
FERGUSON PEANUT RE...
(1) New 7ft Chain Sling (A61166)
(1) New 7ft Chain...
2023 BLAZER GN14 GOOSENECK TRAILER (A62130)
2023 BLAZER GN14...
UNUSED WOLVERINE QC1-26-20G UNIVERSAL HITCH (A62131)
UNUSED WOLVERINE...
UNUSED REMOTE CONTROLLED DUMPER TRUCK (A62130)
UNUSED REMOTE...
2006 TRAIL KING ADVANTAGE PLUS RGN/DETACH TRAILER (A58375)
2006 TRAIL KING...
 
Top