Calculating gpm

/ Calculating gpm #1  

Chillimau

Silver Member
Joined
Mar 23, 2001
Messages
210
Location
Prairie View, OK
Tractor
Yanmar 147, 1987 Model Made for USA (not a grey)
I need to install a 1200' to 1300' water line. I have calculated that I could get about 100gpm out of a 3" line with about 65 to 70 psi line pressure. Does this sound right? The meter is a 2" meter so it should get close on the flow. I can't remember what the feet per second was but seems like around 5 or 6. From what I have read it should be below 10 fps.

99% of the time this size of line would be overkill. Just thinking about a little fire protection from a pasture fire. A 3/4" frost proof hydrant will flow about 30 to 35 gpm according to the spec sheet. If we had three or four of these scattered around the house and barn, along with a lawn sprinkler system, maybe we could protect the buildings until help arrived?

On another note, I don't think I would need to worry about water hammer in the service line, the fps would probably be 1 to 2 or less, most of the time. Still would need to protect individual lines in the buildings with hammer arrestors. (statement is somewhat redundant because the hammer shock wave would travel backwards into the service line.)

Anyway, I'm not an engineer, but I'm trying to approach it from that perspective. I haven't found anything on fire protection but, 100 gpm is probably still not enough but probably all I could afford. Maybe just wasting my time thinking about it. I am going to run 2" at a min. I haven't priced the difference yet. That may decide for me.

Thanks

Gary
 
/ Calculating gpm #2  
The price difference is considerable between 2" sch 40 and 3" sch 40. The velocity of the water in the 3" and frictional loses will obviously be minimized. I would go with the 3" for all the trouble of trenching and for 1300' of line, wow, thats gonna definitely call for 3". You could always drop to 2" after the first 1000' since frictional loss will be minimal in 2" for 200' to 300' at maximum gpm. I ran 2" for about 800' and definitely notice the drop after about 40 gpm to my irrigation. Rat...
 
/ Calculating gpm #3  
Gary,

Get yourself a copy of "Handyman in Your Pocket" by Richard Young and Thomas Glover. It has the Hazen/Williams pipe tables and equations for head loss and velocity calculations. Its real handy for a lot of stuff, costs about $7. Or you can click here Head Loss calculator More fun but you don't learn much from it. /w3tcompact/icons/wink.gif

If you run your numbers it don't look to good at 100GPM/w3tcompact/icons/frown.gif
Al
 
/ Calculating gpm #4  
What kind of irrigation are you guys doing? And what kind of water bills do you have?/w3tcompact/icons/shocked.gif The water main that we (and about 8 or 10 other homes are on is only a 2" for a half mile. And we have a 3/4" meter and lines from the meter to the house, 3 outside hydrants, and the barn. We're on the very end of that water main and have a little over 80 psi pressure. Of course, we sure couldn't get the gpm you guys are talking about.

Bird
 
/ Calculating gpm
  • Thread Starter
#5  
Bird,

I'm not irrigating. Only planning on irrigating if there is a fire!The fellow before me had planned on running a dairy, so I guess he was going need a lot of water for cleaning and more cleaning. I'm seriously thinking about the aerobic septic system you have and using that for pasture irrigation. Not really enough water from the septic system but we are using about 4,000 gal/month right now, so it should help out.

I'm on rural water and my meter is on one of the main lines, (5" or 6" maybe?) and the meter is only about 1500' from a water tower. Prior fellow had installed a 2" compound meter, so might as well use it. I think it was about a $700 meter!

Twinkle toes,

I looked at that Hazen-Williams formula and didn't quite understand what it was telling me, 39.84 head feet? I have a Machinery Handbook, will dig it out and figure what the psi drop is. Just looking at the chart, which doesn't really fit my sizes, doesn't look too good.

AH I think I just found it. Looks like about a 17 psi drop, if I'm reading right. Not too bad, still have 45-50 psi at the faucet.

Is 100 gpm enough to fight a pasture fire around the house and barn ?

Gotta go back later,...
 
/ Calculating gpm #6  
100 gpm is enough to run 2-3 decent nozzles at the same time.

waver.gif
<font color=green>stan</font color=green>
 
/ Calculating gpm #7  
Chillimau, I agree; if you have that size meter, might as well use it, but your rural water system is obviously a lot different than ours. We have a base water rate of $18 a month even if you don't use any water, and if a person wants a 1" meter instead of the 3/4", there is not only a higher cost for installation, but the base rate is $45 a month. And I don't think our system even has anyone with a 2" meter.

Bird
 
/ Calculating gpm #8  
Hey just wanted to throw in that on a aerobic septic for a typical home 300gpd system under normal loads only discharges the equilvent of a 1/10 an inch of rain. They are expensive systems and here in Tx require annual inspections and maintence. Meaning more $$$

Just reread your post, I just got a permit to install a 4500gpd sytem for a trailor park Iam building. If your putting 4000gpd down the hole what happens is they require more spray area. In my case something like 160,000sq ft. or around 3acres. So here anyway you still only get the equilvent of a tenth of an inch of rain.. I had thoughts of planting a tree farm type operation in the area and use the spray to help irrigate but I came to, too many obstacles for that.
 
/ Calculating gpm #9  
<font color=blue>aerobic septic for a typical home 300gpd</font color=blue>

Mine is rated at 500 gallons per day.

<font color=blue>They are expensive systems</font color=blue>

Mine cost $4,000 (a small septic system two years earlier cost $3,800)

<font color=blue>in Tx require annual inspections and maintence</font color=blue>

Requires a maintenance contract with a licensed installer who inspects it 4 times a year.

<font color=blue>Meaning more $$$</font color=blue>

I pay $200 a year for the maintenance contract. I know a guy who'll do it for $125, but I've stayed with someone I know and trust.

Bird
 
/ Calculating gpm #10  
The code requires a calculation on the amount of capacity(sp) It all depends, do you have water saving fixtures etc. I used 300 for an avg. by no means is that the rule of thumb. If I remember right you have a double wide so that makes sense. They are more expesive no matter how you cut it. We installed conventional systems for years again a average $2500 installed. Two 500 gallon tanks 300' field line. dont get me wrong I like the new aerobic systems but they have pros and cons. No eletricity no workie, same with bad pump compressor etc. The old style if you lost power, hurricane whatever you could still flush your commode with a bucket of water.

The price you pay for your service contract sounds right, It is supposed to be going up because of supply and demand. To service these things you have to go to the manufactors class, so usaully you service what you install. I attended some classes and there is a shortage of licensed installers. Hear that anyone wanting to go into business..

I just bought a fourplex that I would like to convert to an aerobic system, when money allows.

BTW Bird what brand do you have? I attended the clearstream class, nice setup.
 
/ Calculating gpm #11  
<font color=blue>Only planning on irrigating if there is a fire!</font color=blue>

There was a thread about three months ago - covering the requirements for water storage and volume/pressure requirements.

See <font color=blue>Clear Your Defensible Space</font color=blue>.
 
/ Calculating gpm
  • Thread Starter
#12  
Thanks Stan and DocHeb, that will probably cause some more questions :) .

Sounds like a 3" line would work good.

Bird, I haven't used any water from the meter and the base bill was $8.00/month but went down a few months ago, I think it is around $6.00/month now. Again that is with no usage right now.

John4NH, I'm running about 4,000 gallons a month at my current house, thanks for the "rainfall amounts" 1/10" a day isn't much considering the lawn ought to have about a inch a week.

I failed the perc test, so I can go with a lagoon, eta (evapotransabsorbtion) (sp) or aerobic. What do you all think about a lagoon or ETA? Definately cheaper.
 
/ Calculating gpm #13  
Humm you got me on lagon and eta?

4000 a month oh, thats not so bad I was thinking day..
 
/ Calculating gpm #14  
John, my system (and my brother's) is a Hydro-Action Model G-500. Their web site is http://www.hydro-action.com. Of course the new system is a little different from the ones they had 4 to 5 years ago.

Bird
 
/ Calculating gpm #15  
Sounds like you have a lot better water rates than we're paying. I just looked at my records and find we've averaged about 4900 gallons a month (low of 2400; high of 8200) and the bill has averaged $41.70 a month.

I don't know anything about the lagoon, but what we had to install for my parents (before I learned about the aerobic systems) was what they called an "evapotranspiration" system. It was just for a little 14 x 52 mobile home; two 400 gallon tanks, and two 20' x 40' evapotranspiration beds. They dug those two beds 2' deep, laid a loop of 8" perforated pipe and filled them with sandy loam (they said they used to use sand, but had learned that sandy loam worked better). There's a gate valve so you can direct the flow to whichever bed you want. They told me when the ground looked wet to switch to the other one. We never had a problem and I didn't wait and let either one show moisture; I just turned the valve on the first of each month to alternate using them.

Bird<P ID="edit"><FONT SIZE=-1>Edited by Bird on 10/24/01 11:05 AM (server time).</FONT></P>
 
/ Calculating gpm #16  
I've heard - but haven't investigated - that Bastrop county now requires that any new systems be aerobic. Is that quarterly inspection a state or county requirement? I can't believe that there's too much to maintaining that system that a fella couldn't learn himself. I really don't want to have to pay maintenance fees for something I should be able to do myself.
mike
 
/ Calculating gpm #17  
Mike

What you heard sounds right to me. The tnrcc is dictating to the county a min. requirement of what they want, then the county can add if they desire. This is all from the hip, I dont have my notes with me. As a homeowner you can install your own system, but you cannot hire anyone to do any part of it except the eletrical. As far as the inspections go it is my understanding you can attend a yearly class and qualify yourself to do them. Its a little grey for me in this area but I will check and let you know definitely.
 
/ Calculating gpm #18  
Mike, the requirement for a service contract (the system installation includes the first two year's warranty and service) is a state law. However, when I first inquired about them, a couple of dealer/installers told me there was no one to enforce that law, so you could ignore it if you wanted to. However, in Navarro County we have a county sanitarian who does enforce it. If you get a permit for installation, there is a form that he requires be filed in the courthouse with the deed to the property, and on that form, the property owner is agreeing to maintain a service contract. And then he keeps a file of the contracts and if a copy of the new one isn't forwarded when the old one expires, he sends you a letter asking where it is. And the service company has a form they fill out each time they inspect the system and they send me, and the county sanitarian, a copy each time.

But otherwise, you're right. I could do all the maintenance myself in about 20 minutes every 3 months./w3tcompact/icons/frown.gif It's just a visual inspection, clean the air filter on the air pump, wash the filter in the treatment tank, and check the chlorine in the final tank.

Bird
 
/ Calculating gpm #20  
self-maintenance and annual qualifications sound good to me - with my luck the class will cost twice as much as a contract - maybe a whole new career field for me in retirement?? gotta find a wrinkle in this somewhere to change my sh!@#tty outlook on the subject/w3tcompact/icons/crazy.gif/w3tcompact/icons/wink.gif

On the water thingy --- for all you engineers out there --- if a fella (me) wanted to put in a solar powered well pump (pumps slow) and pump it into a tower/tank -- the questions I have are ... how high/large would the tank have to be to provide a good psi at the house fed through a 3/4" or 1" pipe less than 300 feet away? and that's after filtering etc at the well house. the idea being that I'd still have water pressure even w/o electricity. and what is a good psi for a standard 3/2 house?
mike
 

Marketplace Items

2006 JLG 600S TELESCOPIC BOOM LIFT (A62129)
2006 JLG 600S...
2011 HEIL TRAILER INTERNATIONAL CRUDE TRAILER (A60736)
2011 HEIL TRAILER...
2018 Bobcat T650 (A60462)
2018 Bobcat T650...
Giyi RB66 Quick Attach 66" Rock Bucket (A60463)
Giyi RB66 Quick...
2007 JLG 600S SKYPOWER TELESCOPIC BOOM LIFT (A62129)
2007 JLG 600S...
KJ K0720 7'x20' Metal Gate (Deep) (A60463)
KJ K0720 7'x20'...
 
Top