Breaker Size?

/ Breaker Size? #1  

kneedeep

Veteran Member
Joined
Apr 16, 2012
Messages
1,655
Location
AL Gulf Coast & MS Delta
Tractor
Mahindra 3510 & 8560
I have a Miller Thunderbolt AC/DC machine in a shed that has been wired with a 100 amp sub-panel. The feed from the main is about 160' to the Equipment shed with 2/0 Aluminum wire with a ground rod. Most of my welding is repair and medium size fabrication.
My question is, what size breaker would the welder require to operate?

TIA
 
/ Breaker Size? #2  
Probably a 50 amp two pole breaker would be fine. Three wire #6 copper plus ground to the 50 amp outlet.
 
/ Breaker Size? #3  
Receptacle that fits the plug on welders is generally 50 amps. Breaker should be 50 amps. Only 3 prongs on the plug, so 3 conductors, 2 rated at 50 amps, the 3rd conductor is the ground, could be as small as 10 gauge copper for that one. Least expensive cable to use would be #6 aluminum service entrance cable.
 
/ Breaker Size? #4  
Some locales specify four wires for all 240V circuits. I agree not needed for a welder.
 
/ Breaker Size? #5  
there will be a name plate on the welder. my thunderbolt lists 50 amps. dont need a neutral on welder. only 2 hots and aground
 
/ Breaker Size? #6  
Depending on how far from the panel, the duty cycle for the welder, and if you plan on upgrading to a welder with a higher duty cycle here are a couple charts to help. Below 100 amps use the 1st column and multiply using the derating factor for the duty cycle. Or don't de-rate and you are good for 50 amps non continuous use. 1509903101974.jpg1509903141970.jpg
 

Attachments

  • 1509903141970.jpg
    1509903141970.jpg
    76.9 KB · Views: 695
/ Breaker Size? #7  
Depending on how far from the panel, the duty cycle for the welder, and if you plan on upgrading to a welder with a higher duty cycle here are a couple charts to help. Below 100 amps use the 1st column and multiply using the derating factor for the duty cycle. Or don't de-rate and you are good for 50 amps non continuous use.View attachment 527482View attachment 527483
 
/ Breaker Size? #9  
Yes, I understand 4 wire is code in WA state.

I wonder if that's a recent change? When I built my house in 2000 the electrician put in a 50 amp 3 wire in the garage for my welder.
 
/ Breaker Size? #10  
Personally I avoid derating. I just stick with the standard NEMA guidelines. Wire Current Ampacities NEC Table 310-16 A bit more expensive for the extra copper, but no chance for confusion or problems down the road. I do tend towards overkill though. Makes upgrading easier.

I also go with NEMA L14-50 plugs. 50@ of 120v or 240v power. You need an extra wire for it, but you gain flexibility. Most generators in the 50@ range will use this plug so it makes it easy to go mobile if needed. It also becomes easier to make a sucide cable & back feed your house if needed as well. Although if you couldn't figure out from the cable name, that's not always the smartest move.


How pray tell so you obtain a ground , neutral and two live lines from a three prong plug and receptacle ? Anyone advocating the use of a double male suicide cord and without a fail safe transfer switch. Their opinions should be ignored .
 
/ Breaker Size? #11  
How pray tell so you obtain a ground , neutral and two live lines from a three prong plug and receptacle ? Anyone advocating the use of a double male suicide cord and without a fail safe transfer switch. Their opinions should be ignored .

NEMA 14-50 is a 4 pin plug (hot, hot, neutral, ground).

And I did say a sucide cord wasn't a great idea.
 
/ Breaker Size? #12  
I wonder if that's a recent change? When I built my house in 2000 the electrician put in a 50 amp 3 wire in the garage for my welder.
Don't know when the code changed but when a hot tub service panel was added (50amp) in 1998, it was 3 wire. This was before our time in the house. Our hot tub died earlier this year and when I spoke with the shop about putting a new one in, the guy said how old was your tub... I told him and he said I'd better check if you have 3 or 4 wire.
 
/ Breaker Size? #13  
The breaker is to protect the wires to the outlet and should be sized accordingly.

Doug in SW IA
 
/ Breaker Size? #15  
Short circuit protection or thermal protection? It depends . Do you agree that a 90 amp breaker is acceptable on a 38 amp motor with #8 R75 copper .

You will burn up that #8 wire, maybe cause a fire, long before the breaker will trip except for maybe a solid short circuit. There are motor rated breakers that will withstand the starting inrush w/o tripping unless the rotor locks up.

Ron
 
/ Breaker Size? #16  
Short circuit protection or thermal protection? It depends . Do you agree that a 90 amp breaker is acceptable on a 38 amp motor with #8 R75 copper .
Breakers & fuses protect wire from overheating & starting fires. They aren't there to protect devices plugged into ir connected to the wires. Sockets are considered part of the wiring in that aspect.
 
/ Breaker Size? #17  
You will burn up that #8 wire, maybe cause a fire, long before the breaker will trip except for maybe a solid short circuit. There are motor rated breakers that will withstand the starting inrush w/o tripping unless the rotor locks up.

Ron

You are not up to date on the electrical code . Perfectly legal and safe with 38GLA , #8 R75 wire and a 90 amp breaker . . Do you know the difference between thermal protection and short circuit protection ? Why would the wire burn up?
 
/ Breaker Size? #18  
For a random 50 amp wall receptacle use a 50 amp breaker and #8 R75.
From that 50 amp wall receptacle and 50 amp breaker it is legal to use #10 SOW Cab Tire cable rated for 30amps if the welders FLA is 24 amp.
 

Marketplace Items

2011 CIRCLE M  35 GOOSENECK (A60736)
2011 CIRCLE M 35...
(12) SKLP SK-LJB-12 Polyethylene Roadbed Protection Pads (A60463)
(12) SKLP...
3pt 26' Field Cultivator (A60462)
3pt 26' Field...
SKIDDED PLAIN/WASTE WATER TANK (A60736)
SKIDDED...
Roto Grind 760 (A60462)
Roto Grind 760...
2019 Sellick S80 (A60462)
2019 Sellick S80...
 
Top