Breaker Size?
/ Breaker Size? #1
kneedeep
AL Gulf Coast & MS Delta
Mahindra 3510 & 8560
I have a Miller Thunderbolt AC/DC machine in a shed that has been wired with a 100 amp sub-panel. The feed from the main is about 160' to the Equipment shed with 2/0 Aluminum wire with a ground rod. Most of my welding is repair and medium size fabrication.
My question is, what size breaker would the welder require to operate?
TIA
/ Breaker Size? #2
Probably a 50 amp two pole breaker would be fine. Three wire #6 copper plus ground to the 50 amp outlet.
/ Breaker Size? #3
Receptacle that fits the plug on welders is generally 50 amps. Breaker should be 50 amps. Only 3 prongs on the plug, so 3 conductors, 2 rated at 50 amps, the 3rd conductor is the ground, could be as small as 10 gauge copper for that one. Least expensive cable to use would be #6 aluminum service entrance cable.
/ Breaker Size? #4
Some locales specify four wires for all 240V circuits. I agree not needed for a welder.
/ Breaker Size? #5
there will be a name plate on the welder. my thunderbolt lists 50 amps. dont need a neutral on welder. only 2 hots and aground
/ Breaker Size? #6
Depending on how far from the panel, the duty cycle for the welder, and if you plan on upgrading to a welder with a higher duty cycle here are a couple charts to help. Below 100 amps use the 1st column and multiply using the derating factor for the duty cycle. Or don't de-rate and you are good for 50 amps non continuous use. 1509903101974.jpg1509903141970.jpg
/ Breaker Size? #7
Depending on how far from the panel, the duty cycle for the welder, and if you plan on upgrading to a welder with a higher duty cycle here are a couple charts to help. Below 100 amps use the 1st column and multiply using the derating factor for the duty cycle. Or don't de-rate and you are good for 50 amps non continuous use.View attachment 527482View attachment 527483
/ Breaker Size? #9
Yes, I understand 4 wire is code in WA state.
I wonder if that's a recent change? When I built my house in 2000 the electrician put in a 50 amp 3 wire in the garage for my welder.
/ Breaker Size? #10
Personally I avoid derating. I just stick with the standard NEMA guidelines. Wire Current Ampacities NEC Table 310-16 A bit more expensive for the extra copper, but no chance for confusion or problems down the road. I do tend towards overkill though. Makes upgrading easier.
I also go with NEMA L14-50 plugs. 50@ of 120v or 240v power. You need an extra wire for it, but you gain flexibility. Most generators in the 50@ range will use this plug so it makes it easy to go mobile if needed. It also becomes easier to make a sucide cable & back feed your house if needed as well. Although if you couldn't figure out from the cable name, that's not always the smartest move.
How pray tell so you obtain a ground , neutral and two live lines from a three prong plug and receptacle ? Anyone advocating the use of a double male suicide cord and without a fail safe transfer switch. Their opinions should be ignored .
2008 Ford Ranger Ext. Cab Pickup Truck (A59230)
2008 Ford Ranger...
2003 Ford E-450 Super Duty Passenger Bus (A59230)
2003 Ford E-450...
HYSTER S60FT STRAIGHT MAST FOKLIFT (A59823)
HYSTER S60FT...
2019 Chevrolet AWD Equinox SUV (A59231)
2019 Chevrolet AWD...
UNUSED FUTURE FT-RP72 - 72" HYD ROCK CRUSHER (A52706)
UNUSED FUTURE...
2015 GENIE GTH-1056 TELESCOPIC FORKLIFT (A52709)
2015 GENIE...