Breaker Size?

/ Breaker Size? #1  

kneedeep

Veteran Member
Joined
Apr 16, 2012
Messages
1,654
Location
AL Gulf Coast & MS Delta
Tractor
Mahindra 3510 & 8560
I have a Miller Thunderbolt AC/DC machine in a shed that has been wired with a 100 amp sub-panel. The feed from the main is about 160' to the Equipment shed with 2/0 Aluminum wire with a ground rod. Most of my welding is repair and medium size fabrication.
My question is, what size breaker would the welder require to operate?

TIA
 
/ Breaker Size? #2  
Probably a 50 amp two pole breaker would be fine. Three wire #6 copper plus ground to the 50 amp outlet.
 
/ Breaker Size? #3  
Receptacle that fits the plug on welders is generally 50 amps. Breaker should be 50 amps. Only 3 prongs on the plug, so 3 conductors, 2 rated at 50 amps, the 3rd conductor is the ground, could be as small as 10 gauge copper for that one. Least expensive cable to use would be #6 aluminum service entrance cable.
 
/ Breaker Size? #4  
Some locales specify four wires for all 240V circuits. I agree not needed for a welder.
 
/ Breaker Size? #5  
there will be a name plate on the welder. my thunderbolt lists 50 amps. dont need a neutral on welder. only 2 hots and aground
 
/ Breaker Size? #6  
Depending on how far from the panel, the duty cycle for the welder, and if you plan on upgrading to a welder with a higher duty cycle here are a couple charts to help. Below 100 amps use the 1st column and multiply using the derating factor for the duty cycle. Or don't de-rate and you are good for 50 amps non continuous use. 1509903101974.jpg1509903141970.jpg
 

Attachments

  • 1509903141970.jpg
    1509903141970.jpg
    76.9 KB · Views: 689
/ Breaker Size? #7  
Depending on how far from the panel, the duty cycle for the welder, and if you plan on upgrading to a welder with a higher duty cycle here are a couple charts to help. Below 100 amps use the 1st column and multiply using the derating factor for the duty cycle. Or don't de-rate and you are good for 50 amps non continuous use.View attachment 527482View attachment 527483
 
/ Breaker Size? #9  
Yes, I understand 4 wire is code in WA state.

I wonder if that's a recent change? When I built my house in 2000 the electrician put in a 50 amp 3 wire in the garage for my welder.
 
/ Breaker Size? #10  
Personally I avoid derating. I just stick with the standard NEMA guidelines. Wire Current Ampacities NEC Table 310-16 A bit more expensive for the extra copper, but no chance for confusion or problems down the road. I do tend towards overkill though. Makes upgrading easier.

I also go with NEMA L14-50 plugs. 50@ of 120v or 240v power. You need an extra wire for it, but you gain flexibility. Most generators in the 50@ range will use this plug so it makes it easy to go mobile if needed. It also becomes easier to make a sucide cable & back feed your house if needed as well. Although if you couldn't figure out from the cable name, that's not always the smartest move.


How pray tell so you obtain a ground , neutral and two live lines from a three prong plug and receptacle ? Anyone advocating the use of a double male suicide cord and without a fail safe transfer switch. Their opinions should be ignored .
 
/ Breaker Size? #11  
How pray tell so you obtain a ground , neutral and two live lines from a three prong plug and receptacle ? Anyone advocating the use of a double male suicide cord and without a fail safe transfer switch. Their opinions should be ignored .

NEMA 14-50 is a 4 pin plug (hot, hot, neutral, ground).

And I did say a sucide cord wasn't a great idea.
 
/ Breaker Size? #12  
I wonder if that's a recent change? When I built my house in 2000 the electrician put in a 50 amp 3 wire in the garage for my welder.
Don't know when the code changed but when a hot tub service panel was added (50amp) in 1998, it was 3 wire. This was before our time in the house. Our hot tub died earlier this year and when I spoke with the shop about putting a new one in, the guy said how old was your tub... I told him and he said I'd better check if you have 3 or 4 wire.
 
/ Breaker Size? #13  
The breaker is to protect the wires to the outlet and should be sized accordingly.

Doug in SW IA
 
/ Breaker Size? #15  
Short circuit protection or thermal protection? It depends . Do you agree that a 90 amp breaker is acceptable on a 38 amp motor with #8 R75 copper .

You will burn up that #8 wire, maybe cause a fire, long before the breaker will trip except for maybe a solid short circuit. There are motor rated breakers that will withstand the starting inrush w/o tripping unless the rotor locks up.

Ron
 
/ Breaker Size? #16  
Short circuit protection or thermal protection? It depends . Do you agree that a 90 amp breaker is acceptable on a 38 amp motor with #8 R75 copper .
Breakers & fuses protect wire from overheating & starting fires. They aren't there to protect devices plugged into ir connected to the wires. Sockets are considered part of the wiring in that aspect.
 
/ Breaker Size? #17  
You will burn up that #8 wire, maybe cause a fire, long before the breaker will trip except for maybe a solid short circuit. There are motor rated breakers that will withstand the starting inrush w/o tripping unless the rotor locks up.

Ron

You are not up to date on the electrical code . Perfectly legal and safe with 38GLA , #8 R75 wire and a 90 amp breaker . . Do you know the difference between thermal protection and short circuit protection ? Why would the wire burn up?
 
/ Breaker Size? #18  
For a random 50 amp wall receptacle use a 50 amp breaker and #8 R75.
From that 50 amp wall receptacle and 50 amp breaker it is legal to use #10 SOW Cab Tire cable rated for 30amps if the welders FLA is 24 amp.
 

Marketplace Items

2018 Ford Escape AWD SUV (A59231)
2018 Ford Escape...
2016 Hyundai Sonata Sedan (A59231)
2016 Hyundai...
Brent 420 Grain Cart (A61307)
Brent 420 Grain...
2019 PETERBILT 579 TANDEM AXLE SLEEPER (A59905)
2019 PETERBILT 579...
iDrive TDS-2010H ProJack M2 Electric Trailer Dolly (A59230)
iDrive TDS-2010H...
DEUTZ MARATHON 60KW GENERATOR (A58214)
DEUTZ MARATHON...
 
Top