60 Amp. portable generator hookup to bldg.

/ 60 Amp. portable generator hookup to bldg. #1  

angustrees

Member
Joined
Mar 25, 2010
Messages
29
Location
E. Tennessee (relocated from IL/MI)
Tractor
1971 JD 4020 Diesel, Kubota 3400 & SVL75-2, RTV-X1140, Case 650M, CAT 311
I have a 15kw tractor powered WINCO generator delivered last spring & am just getting around to setting it up. The major problem seems to be finding a way of getting the generator 60 Amps to the Main panel. I only find 50 amp power inlet connectors -- female end to male in box. I prefer the safety of a 60 amp. female cord end and a 60 amp. connection in a box.

I need a weather proof exterior box (simply to contain a receptacle, to be mounted next to & wired directly into interlocked breakers in the main entrance breaker panel), that will accept female end of 12-15' power cord from generator. HVAC breakers shown will be moved to accommodate the 60 Amp. Gen breakers.

Pic shows MAIN box with safety cover. I have an interlock device to prevent cross or back feeding high line.

And I would also need the female cord END that would connect into that box. Any experience here?
 
/ 60 Amp. portable generator hookup to bldg. #2  
/ 60 Amp. portable generator hookup to bldg. #5  
Sounds like you need NEMA 18-60 connections.

I used NEMA 14-50s for my 15kw pto gen. It has a 240V 50A breaker.

You should be able to buy an RV hookup style box and put whatever outlet you need in it.
 
/ 60 Amp. portable generator hookup to bldg. #6  
Problem is a generator inlet box is a specialized male fitting. They dont make a standard 60 amp unit.
 
/ 60 Amp. portable generator hookup to bldg. #7  
18-60 is a standard NEMA plug. Just not seen very often.

 
/ 60 Amp. portable generator hookup to bldg. #8  
What you want to do is to simply use a 50 amp setup. Use the widely available California Special 50 amp flanged (male) inlet boxes available from Reliance or Generac or such, the matching plug on a 6/4 flex cord that is widely available for about $10/foot, and connect the flex cord to your generator. In the breaker panel, use a 50 amp breaker for your backfed breaker. This is exactly what I did for my setup. I was originally going to run a 25 kW generator (tractor could run a 40 easily) on a 100 amp circuit but the issues with cabling and connectors for more than 50 amps was a deal breaker. So I got a 12 kW unit and used the 50 amp gear.

If you want more than 50 amps, you will need to use a very expensive pin and sleeve inlet like what newbury linked to, that 100 amp pin and sleeve connector is about $600. You will also need 4/4 SO cable at $25 per foot for 60 amps. (FYI, the largest 4 conductor SO cable only generally comes in sizes up to 2 AWG good for 80 amps, larger than that and you are using mine cable or something else esoteric.) The 18-60 plugs and receptacles Hall00 linked to are not appropriate. First of all, they are regular plugs and receptacles and not inlets, you would be dealing with trying to plug a receptacle on the end of your flex cord into a plug mounted in a box, that is backwards. Secondly, those are 120/208 volt 3 phase ungrounded parts, you have 120/240 grounded, you would use a 14-60 plug and receptacle (which also exist) if you could use regular plugs and cords instead of needing an inlet.
 
/ 60 Amp. portable generator hookup to bldg. #9  
Talk to an electrician or go to an electric supplier and buy a fused disconnect and an outdoor 60A wall mount receptacle (aka weld plug).

1642585514875.jpeg
 
/ 60 Amp. portable generator hookup to bldg. #10  
I use these. I had to get them in 100 amp for my 25 KW Winco but they sure make hookup a snap.



1642590358922.png
 
/ 60 Amp. portable generator hookup to bldg. #11  
BTW, that is an Appleton 60 amp welding receptacle. Obviously you can get the plugs for it. It is weather tight.
 
 