I think I know answer, but appreciate input/ideas.
I'm running underground electric to a new barn from a garage. From panel to just inside barn is 130 ft. From panel to across barn other side is 200 ft.
Neighbor has lots of Square D boxes, etc. I can have. (His electrician Dad passed).
Barn will just have lights (maybe 6-7...so 420 watts max) 10 outlets (1500 watts max), so 25 amps max.
I thought I'd put a 50 amp breaker in garage box, run 8-2 uf wire out to a small panel box in barn. I don't need 240...but it's there and I can split it (2x120v).
I prefer copper...but I'm trying to save money. It would look and be better in conduit to other end...but shorter run means smaller gauge (200ft run=6-2 or maybe 4-2 wire?).
Thanks...ideas.