Underground wire size question
/ Underground wire size question #1
bfisherman11
IL and WI
LS G3033H
I have a small building i want to run about 20-30amps in 110V to. My run is 180 feet from my electrical panel to the building.
I have searched "electrical" and gone back 8 pages to no avail.
I won't be welding etc. All i want are about 6 light fixtures (LED) and a couple outlets for a drill or hand saw.
I don't have any 220v needs....
Would say #10/2 with a ground work? I was having trouble looking at charts and understanding on line. I am not an electrician.
Thank you!
Bill
/ Underground wire size question #2
You are well covered for 20 amps with a 10/2 at that distance. I would probably run 10/3 and have 2 110v circuits. Even though new code no longer blesses sharing the neutral.
/ Underground wire size question #3
10-3 with ground to a sub panel in your building.
/ Underground wire size question #4
10 /2 would be fine for what you want are you going to put a small panel in shed if so you may want to run 220 amp and run 10/3 so you get 2 hot 1neutral and 1 ground not much more money !!!
/ Underground wire size question #5
This option might also allow you to upgrade to 220 if you needed to at some later date for a at this time unknown need. Without having to rerun new wire.
/ Underground wire size question #6
Can you expand on that? Not an electrician, just curious what has changed. Thanks.
/ Underground wire size question #7
New code in my area says each circuit has to have its own neutral and ground. So, if you run a 10/3 to a small panel you can put a couple breakers in, you would splitting the hots and sharing the ground and neutral for each circuit. To stay within code, you would run two 10/2 WG so each circuit has 3 wires. It sounds like we are making this into more than what you actually need (it's what we do here), if so stay with the 10/2 plan and then run #12 wires out of a junction box to your lights and plugs.
/ Underground wire size question #8
If you are going through all the trouble to dig the line, ditch10/2 or 10/3 and put in conduit- 1 1/4". Then pull the needed size wire. With the length you are running you will need to upsize (per code recommended) one size. So #10 for 20a and #8 for 30a. All the sizes assume copper wire. To google the answers check out/Google
NEC T3705.1 (note code has maximum amps for 14,12and10awg)
NEC 210.19 fpn no. 4
/ Underground wire size question #9
If you are doing this as cheap (and as easy) as possible, you can run direct burial romex and run into conduit where you enter the panel and at the building. Just be aware you are potentially creating a termite super highway.
/ Underground wire size question #10
As an absolute minimum in a conduit from panel to shed .10/3 from a pair of 20amp breakers in the main service. A set of 20amp T-slot receptacles for power tools on one circuit. All the lights and a couple of receptacles for low draw loads such as a radio on the other circuit.
This way if you trip the breaker to the power tools the lights won't go out. Also the lights won't brighten and dim as much when ever a power tool is started.
Far better to go with what other posters have stated with a 1-1/4" conduit, pull #8 wires, two live lines a neutral and a ground. 30 amp breaker in supply panel. 30 amp panel in shed, floating neutral bar with a pair of 20 amp breakers. Ground rod at shed, do not under estimate lightening. Sooner or later you will install an electric heater for winter, an AC for summer , a beer fridge and a microwave.
If over loaded, the 20amp breaker in the shed should trip instead of the 30amp breaker in the house.
/ Underground wire size question #11
The way I would do this, as an electrician, is run a 1-1/4" conduit, pull 3-8AWG wires plus a ground. In the shed, I would put in a small sub-panel. This would give you 30A-220V, just in case you wanted anything extra like heaters, or a beer fridge etc. From the panel run the circuits as needed for lights and plugs. The #8AWG is to take care of voltage drop on a run that is close to 200ft.
The reasoning behind this would be, so I could upgrade anytime at a later date. The 1-1/4 conduit would allow upgrade to 100A-220V. This spring, I have to do exactly this to feed my shop. My run is a little shorter though.
/ Underground wire size question #12
To further drive the point home- Home Depot has 1 1/2" pvc conduit listed for $0.62/ft or about $112 for the run-they don't list 1 1/4" on the website.
To have 4 8 ga wires (1000' of wire) is $274. 4 wires gets you 2+ circuits and or 240v.
Total $384 plus conduit ends.
The direct bury 10/2 romex is $175 The non outdoor rated (that's all HD had listed) 8/2 was $375 plus conduit ends. Direct bury is more!
So for about the same price as direct bury romex that only gets you one or two circuits and no 240v option you can have multiple circuits (double the power/amps of the romex) and 240v. Plus the conduit is big enough to upgrade the wires for anything you would want to do in the future. You have to dig the trench anyway- might as well use the conduit.
/ Underground wire size question #13
Since this subject came up, I need help also. We are building new house and shop and want to run single phase 300 amp service from meter 425 feet underground. Want 200 for the house and 100 for shop. What size wire do we need? Thanks
I was planning a subpanel. I like what You all advised and think I will do the pic conduit and #8. Good ideas.
Thanks,
Bill
/ Underground wire size question #15
Where's the meter/transformer? In other words is the 425' after the meter? That's a long run you may not need if your PUP will "help".
/ Underground wire size question #16
The meter is very near the transformer, and all the service is underground so yes the 425' is after the meter. To make matters worse our 8 acres is in a HOA. The developer had all the infrastructure done upfront,city water, phone. No NG,only buried propane tanks are allowed.
/ Underground wire size question #17
instead of running solid pvc pipe (white or gray) at local hardware stores. see about black poly hose (comes in a large roll say 3 to 4 feet in diameter) it might be easier to pull the wire through it. along with putting the hose into the trench. let the hose snake back and forth some in bottom of trench (weave back and forth) so any settling / movement of ground through frost heaves will not put extra strain on hose and electrical in it. if you un-wind the hose and leave it set outside for a day in the hot sun. generally the curves in pipe will go away making it easier to drop the black poly hose into the trench.
get the electrical to depth or deeper, if memory serves 2 feet depth or 2.5 feet depth for my area (central IL), but you may need to be a little deeper for frost zone were you live.
you say you do not want 220, but really it be easier atleast for me a diy bozo. to run a 220 30amp breaker at panel in home. and then run wires out to shed, and install a 30amp breaker panel there. and then split off to individual 15amp and 20amp circuits (lights, and outlets)
call around, local hardware stores were 1/3 to nearly double the cost of a local electrical supply wholesaler in my area for the wire i needed. for running 60amps out to shed i think length was around 120 to 150 feet.
i bought each wire separately, and then took some electrical tape and taped all wires together about every 4 feet (2 hots, 1 netural, 1 ground) and coiled them into a single bundle, and then pulled all 4 wires together and i think i had my mom just seating there with gloves on covering the wire with dish soap as it feed into the end of the pipe, while i pulled. i did use shop vac to suck some kite string through initially with a rag tied onto end, then pulled larger rope through. then pulled a larger cable through, then finally pulled all the 4 wires together. it went smoothly but a bit messy.
when pulling wire do not wrap wire around hands and/or make sharp kinks in it. i ended up using my shoulder (wire going over it) and pulling. and also half U shape around belt area of my body. to get a grip on it. to help pull it through.
to note it, i did go with copper, when looking at aluminum wire, and diameter. i knew my wimpy body was not going to be able to pull the aluminum through any pipe. that and my luck i would of ended up with corrosion on the ends were they connected to the breaker panels. copper cost a little more but worth it.
wire needs to come out of the house above ground. and then a pipe entering the ground. then once at shed, electrical needs to come out of ground in a pipe, and then enter shed from the outside above ground.
air compressor, fridge, freezer, various tools more so drills and hand saws, table saw, window a/c conditioner, fan/s, battery tender/charger, and more so car jumper/charger. upgrade the amps if possible it costs a bit more. but worth it.
if you are out of your league. dealing with 220 and dealing with all the electrical. you might work with a local contractor. and see about putting in trench yourself and pulling in the wire, and leave the hookup to local contractor. and then go from there.
rent a trenching machine. it is worth it! or a small mini ex (mini excavator) for the trench digging, if going through a rock driveway, and/or some trees are nearby, you might need a backhoe/ excavator to get through the rock and/or tree roots. the chain saw like trenching machines can get hung up on rock and roots. they can handle some size, but....
if renting a machine to put trenches in. get some more black poly pipe. 3/4" to 1" inside diameter. and run water out to shed. electrical and water lines if memory serves need to be 4 feet or further apart (horizontally), and i want to say water needs to be 1 to 1.5 feet deeper (vertically) than the electrical. when both are being ran parallel to each other. do not run them in same trench!
if you want internet or say cable tv or satilite tv out there, or an old land line phone. i want to say you can run the cable 8" or 12" above the eletrical, by code (do not quote me on that) been to many years.
/ Underground wire size question #18
I'd set a 400a meter main near the transformer (assuming meter isn't set yet) and run 2 sets of wires from there.
Your friend has shared a link to a Home Depot product they think you would be interested in seeing.
400 Amp 30-Space 42-Circuit Surface Mount Underground Fed Meter Load Center Combination
Siemens 4 Amp 3-Space 42-Circuit Surface Mount Underground Fed Meter Load Center Combination-MC342B14SDS - The Home Depot
Trying to run wire big enough for 300a 425' involves a truck, wench and a spool of wire about the size of a Mini Cooper car. Copper is a bit easier but more expensive. Aluminum is a bit cheaper but requires bigger wire. Which one.
/ Underground wire size question #19
Meter main is set. It's 425' to the building envelope and the buildings will be at the very edge of the envelope closest to the meter. Is it possible to run two separate lines,say a 100 amp line and a 200 amp line?
/ Underground wire size question #20
Yes it would be best IMO. So what's at the meter? A panel or just a meter and main breaker? What type of wire- copper or aluminum?
MF GC2300 fel replaced
NEW ATS Mini Ride on Skid Steer (A62679)
NEW ATS Mini Ride...
2017 ISUZU NPR 18 FT  BOX TRUCK (A59905)
2017 ISUZU NPR 18...
(1) HD 24ft Free Standing Corral Panel with 7ft Gate (A65579)
(1) HD 24ft Free...
621B PAN 300Hrs on Engine 3406 Offsite Danville VA Everything Works (A62613)
621B PAN 300Hrs on...
2026 MACK GRANITE GR64F DUMP TRUCK (A63276)
2026 MACK GRANITE...