Roatary Phase converter ??
   / Roatary Phase converter ?? #41
I suspect you are right about the table and coolant pump not being 3phase, which makes me wonder how those motors will react if I hook the machine up to a rotary converter. I am now thinking that there might be more wireing needed done to the switches on the machine. My son is a commercial electrician, I might have to pull him in to do the wireing.
If they are 110v single phase, it gets pretty easy. There will be a transformer in the electrical box that runs off of two legs from the three phase input. Just make sure you connect the two 'normal' legs to this transformer and not the 'wild' leg. You may end up with higher voltage than 110, but modern motors are safe at +\- 10 percent of rated voltage. Sometimes the transformers have multiple taps to account for this. Your son can help you here I'm sure.
   / Roatary Phase converter ?? #42
I'm running this 15' X 54" Cincinnati Hydrashift lathe (5hp) and 2 Scotchman Ironworkers (3&5hp) on a static converter that I built for $45.
3 Phase machines will use single phase for smaller electrical use items. For single phase they just use 2 legs or 1 leg and neutral for 120V.
My lathe uses 120V single for the relays that control the motor. When I first hooked it up I had the phantom leg in the wrong place and it would not work. All I had to do was shift the connections.
Right now I really need to make the trip to look the machine over and try and make the deal. I have seen the machine many times, but never looked at it as a potential buyer. He's asking $700 and it comes with a full set of r8 collets and hold down tools, but no vises or cutting tools. I know he cuts keyways in 4ft long shafts with it, but it sits mostly unused since he bought his newer mill. Its a manual machine with no dro's or any other fancy stuff. I guess first i need to buy the machine and then figure out how to power it.
   / Roatary Phase converter ?? #44
I believe you can get directions for hooking up a Phase-O-Matic static converter using what they call a pony motor. fancy name for additional 3 ph motor and the wiring in an interrupter switch. It is pretty simple to hook up I have built 2 this way with good success. Phase-O-Matic directions are I think available online.
   / Roatary Phase converter ?? #45
Well, sheeeeeiiiittt Why didn't you say that? He should know this cold. And if not, then smack him upside the head and ask what all that schoolin' was fer? :D
Obviously lots of ways to skin this cat as you have seen. It sounds mostly like you need to get a better read on what you need.
Something that hasn't been mentioned clearly here is that the difference between a rotary converter and a static one is the motor. Other than adjusting caps a bit, there is no difference. Just add a motor to a static and you have a rotary converter. ...If you do it correctly... tons of resources with a google search.
If I understand it correctly, a static converter just converts your machines 3phase motor to run off single phase and at 2/3 power, where as a rotary provides the third leg needed to run your machine motor off 3 phase. Using a static converter and adding a motor should be the same as a rotary. Which begs the question, why not just buy a static converter to build your rotary converter and run your equipment off the rotary. Static converters seem cheap enough. I have also read that running more than one motor at a time off your rotary would improve the balance of the 3phase. Some folks where even wiring in an extra, smaller hp motor, inline between the larger rotary motor and the equipment motor. They just turned the smaller motor on/off when its needed. Purpose being I think to provide cleaner power.
   / Roatary Phase converter ?? #47
I looked up the #2 machine with vertical attachment and I could not find how fast the spindle could turn. Videos only showed it turning slow, maybe 250 rpm. That would not be enough speed to run carbide endmills. I would prefer a Bridgeport type mill with a sliding, lockable column to ease drilling holes.
I dont know the speed either. I know it has a dial for speed control. I would guess the dial should tell the speeds. Something I hadnt thought about though. Glad you brought that up.
   / Roatary Phase converter ?? #49
If I understand it correctly, a static converter just converts your machines 3phase motor to run off single phase and at 2/3 power, where as a rotary provides the third leg needed to run your machine motor off 3 phase. Using a static converter and adding a motor should be the same as a rotary. Which begs the question, why not just buy a static converter to build your rotary converter and run your equipment off the rotary. Static converters seem cheap enough.<snip>
That's the basic concept.
Did you read phaseconverter ?
On Phase-Crafts ebay page (I won't link because I think I'm not supposed to link to ebay) he states that static converters are not supposed to be used with metal lathes and a whole bunch other stuff.
PLEASE NOTE: STATIC CONVERTERS ARE NOT SUITABLE FOR AIR COMPRESSORS, REFRIGERATION EQUIPMENT, AUTO LIFTS, IRON WORKERS, HYDRAULIC PUMPS, CNC MACHINERY, HEATERS, BATTERY CHARGERS, ELECTRONICALLY CONTROLLED EQUIPMENT, TWO SPEED MOTORS, OR HARD-STARTING DEVICES. PLEASE CONTACT ME BEFORE ORDERING IF YOU HAVE ANY QUESTIONS ABOUT THE SUITABILITY OF A STATIC CONVERTER FOR YOUR PARTICULAR APPLICATION. NOT RECOMMENDED FOR METAL LATHES. WE ALSO SELL ROTARY CONVERTERS WHICH WILL WORK WITH VIRTUALLY ANYTHING IF PROPERLY SIZED.
So you could probably start out with a static and upgrade to a rotary when you get more 3 phase equipment.
<snip> Some folks where even wiring in an extra, smaller hp motor, inline between the larger rotary motor and the equipment motor. They just turned the smaller motor on/off when its needed. Purpose being I think to provide cleaner power.
I think you are mixing up a "starter" or "pony" motor with something to clean up the power.
BUT really you should tap your son and tell him to get over and fix this up for his dad as a belated Father's Day present. Especially if you get into dealing with terms you are unfamiliar with.
120 volts at 15 amps hurts like H. 240 volts at 60 amps can probably kill.
   / Roatary Phase converter ?? #50
I have been using my converter on my lathe and Ironworkers for about 10 years with no problems! The ebay guy is mis-informed about these items.
I never run my machines wide open anyway which would cause problems.
Both my Ironworkers are hydraulic machines.
I had a Buffalo 3 ph Mechanical Ironworker which ran great also but I sold it because it was too scary! When you stepped on the peddle something was going to get cut or bent!
The 50 ton Ironworker is rated to punch a 1 1/8" hole in 3/4" steel!!! That probably won't work with the static converter.
Pretty sure I am not mixing up the starter/pony motor with using another motor to clean up the power. If I am reading right, a pony motor is just a motor used to get the bigger 3phase motor to turning before turning on the single phase power. The pony motor is just used as a starter instead of running a large starter capacitor. The article about running another motor in addition to the rotary is supposed to make the phases more in sync or something. The more motors you are running the cleaner the power. I other words, if you had 3 or 4, 3phase machines running off one RPC, turning on all the equipment, even though you only plan on using one piece, would make that one piece you are actually using have a purer 3phase power, Or something along those lines. Of course , I dont fully understand it. I have only had a couple of days of reading to learn about this stuff. Wait!, a couple of days of reading makes me a internet expert already. What was it you where needing to know??:laughing:
   / Roatary Phase converter ?? #52
My boss' RPC has the old shaft sticking out one end of the big motor. He just puts his tennis shoe on it and gives it a spin in the right direction and then turns it on.
   / Roatary Phase converter ?? #53
Single phase is the standard over here, usually 240v. Do you have 3ph in your homes in Norway? What voltage?
I have 3 phase in the cabin in Austria... also have a Siemens continuous flow on demand hot water heater...
   / Roatary Phase converter ?? #54
OK, yes you have it right. As I understand it if you have several motors on 1 RPC you start the RPC, start the biggest motor, then start other motors and somehow it improves the power.
Just don't let the smoke out.
Frome Phase-A-Matic's web page:
The first motor started, if not running heavily loaded, generates additional 3-phase power back into the circuit. You can then run additional motors, provided they are not running heavily loaded and not all started at the same time. A maximum of up to 3 times the HP rating of the Rotary Converter can run at the same time, if not heavily loaded, and not started simultaneously. For example, a 30 HP Rotary Converter potentially could run motors totaling up to 90 HP. Contact factory for verification of sizing.
   / Roatary Phase converter ?? #55
Just to add...
30 years ago I bought a NC Bridgeport Tape Mill and set it up in the garage.
For 30 years I have been using a 1 hp 3 phase electric motor with a rope start for my 3 phase power source.
About 20 years ago did the same for a 3 hp compressor with a 3 hp pony motor...
So far... zero problems and the Bridgeport has runs 8 to 10 hour days for several days at a time... don't use the big compressor much unless sandblasting.
   / Roatary Phase converter ?? #56
I'm fortunate for the fact that we've had 3 phase here on the farm since the mid 1950's.
I have no RPC info to contribute, but I must say I'm enjoying learning from this thread.
Terry
Terry
:thumbsup:
   / Roatary Phase converter ?? #58
know??:laughing:
Sounds like your getting it, muddstopper! You could literally spend several days researching this subject on Practical Machinist alone. Lots of ways to skin this animal. And if you let the 'magic smoke' out of a motor, you can start a thread on that and get many similar stories from others. I know I have few of my own but sometimes that's how you LEARN and never forget!
   / Roatary Phase converter ?? #59
I think you are getting it spot on so far.
I'll give a quick summary
Static: cheap an no moving parts. A 3 ph motor WILL run on just the two legs of single phase power. But since the legs are 180 degrees out of phase, it won't start and will sit in a locked rotor position unless something else influences it. With a static this is done with capacitors. But you can only operate at 2/3 power since you are only powering 2 legs instead of 2
A rotary is the same principal. It uses a 3phase motor being powered by your 2 hot legs. But that spinning rotor with coppor windings around it induces voltage in the 3rd leg to make 3 phase. Similar to the way an alternator or generator work. How the rotary is started can very. Others have mentioned the popular methods, a rope, a 110v pony motor, or capacitors( basically a static powering a donor motor).
With a rotary though, that 3rd created leg isn't quite the same as the two legs you are feeding power to. Thus some play with different size run capacitors to try to balance the voltages and phase separation better. This is where the more motors running the better the power. But with a rotary, you are still bound by the 2/3 power rule UNLESS you upsize the donor motor. It takes a 15hp donor to run a true 10hp phase convertor.
Actually buying a good quality rotary, it is more than just a donor motor. The 3rd (created) leg they put more windings in the donor to better balance the power from the start. And with a factory built rotary, there is no 2/3 rule. They just change the way they rate them. So if it says 10hp on the nameplate, that's what you can power. Cause they built it as a 15 hp motor, but labeled it for what it can power.
Vfd's are the best solution if you can afford them. They convert the single phase power to DC first. Then convert back to 3 equally balanced AC lines with darn near perfect voltages and phase separation. And they CAN be used on different motors, but NOT more than one at a time. I have a plug on the vfd. I can unplug one motor, plug another in and go. If the specs (hp, fla, rpm, etc) are different, you may have to spend 2 minutes changing a few parameters. But you have so much more control. Not just over the speed. But acxel and decell times, over current protection, over and under voltage protection etc.
Just remember though, with any of these convertors, you need to be sure your equipment cannbe wited to low voltage 3phase. If you have motors that only have high voltage windings, you are gonna be into alot more money for a transformer.
   / Roatary Phase converter ?? #60
mudstopper,
I have read the complete thread , a few things to add. If your small motors are single phase , then a VFD would
be a good thing. If more than one is 3 ph then a rotary would work well, or a static unit large enough to run the
mill and a 'slave' motor to give you instant start and instant reverse.
I have run my shop on a non solid state static with a 5 hp slave for 35 +years . The BS from the sales rep that the
motors won't stand up is wrong . The motors that I have used for slave are newer than anything on the machines,
the only failures were the slaves (2 in 35+years) one of which was caused by bearing failure ,the other didn't start
after a power outage. Most of these are old machines - a 1905 -30inch Leblonde lathe (10 hp), lucas #41 3 inch
horizontal boring mill (7.5 hp ) , 26 in lathe early 1900's - 7.5 hp , early 1900's -20 inch american 5 hp , a # 3 horiz
with 3 hp 1920's , 5 ft Cincinnati planer - 1.5-hp , 14 x 48 landis universal cylindrical grinder -5 hp plus small motors,
2 medium vertical mills , old cincinatti #2 horiz mill -1 hp , 14 in lodge & shipply lathe -1hp , and several hoists on bridge cranes . Also about to move in 2 surface grinders and an Index 1.5 vert mill.
Questions call me , # is on web site
george
Deere 310L (A53317)
Deere 310L (A53317)
Michelin CARGOXBIB High Floatation Tires (SET OF 4) (A56438)
Michelin CARGOXBIB...
Forklift (A56857)
Forklift (A56857)
2025 CFG Industrial QK18R Mini Excavator (A59228)
2025 CFG...
2017 Toyota Hybrid Camry Sedan (A59231)
2017 Toyota Hybrid...
2014 Ford Explorer AWD SUV (A59231)
2014 Ford Explorer...
