Hayden,
Progress looks great and I can sympathize with your aching back.:)
I have two of those power vents, but in my hot solar shed it's not enough, even with the hydrogen collecting caps. Your basement will be ten times better though. Is there separation between the controllers and the batteries?
Access is my only concern. We find ourselves checking specific gravity, adding water etc. lol ... What about when you have to change the batteries out 10 years from now and you are old like me?
Also, do you have a spill tray planned for the batteries inside the box?
 
/ Solar Electric Project
  • Thread Starter
#62  
3RRL said:
Hayden,
Progress looks great and I can sympathize with your aching back.:)
I have two of those power vents, but in my hot solar shed it's not enough, even with the hydrogen collecting caps. Your basement will be ten times better though. Is there separation between the controllers and the batteries?
Access is my only concern. We find ourselves checking specific gravity, adding water etc. lol ... What about when you have to change the batteries out 10 years from now and you are old like me?
Also, do you have a spill tray planned for the batteries inside the box?

Hi Rob,

Glad to hear you are checking the battery vitals - it's real important to maximizing their life.

My battery box and power panel are right next to each other, but there is clearance to open the battery box and gain access without the panel and electronics getting in the way. I think in some of the pictures you can catch a glimse of the relative position of the two. I loaded all the batteries with the power panel in place, so that's the ultimate test. If anything, the battery box cramps access to the panels a bit, but once it's all wired up everything can be controlled by the system panel which will be in the kitchen.

The basement has worked real well with my old system to maintain comfortable battery temps. They get down to maybe 50 in the winter, but warm up when charged. In the summer is stays below 80. I don't think I could ask for better than that.

Your batteries in that hot shed does worry me. Would it be possible to insulate the building, or at least the roof to moderate the summer heat?

Replacement 10 years from now? Hopefully I'll still be good and fit. Between the tractor, hand truck, and engine hoist, I got all 12 batteries from the yard, into the basement, and loaded into the battery box 100% by myself. We'll see how good a repeat performance I can do in 15 years. 15 years, that's how long these batteries are going to last;) .

I don't have a spill tray. I probably should, but I don't. Fortunately the outer case of each battery is itself a secondary containment vessel. The actual cells are another container inside, with two of them bolted together to give the 4V that each battery produces. There's RTV sealer around where the lugs come through the top cover, but otherwise the cover would just lift off. So, my rationalization is that I'm depending on the battery's secondary containment vessel for spill containment. Are you buying it?

I'll probably post some more pictures later tonight with an update.
 
/ Solar Electric Project #63  
Hahaha, I know you probably don't spill a drop, but I always use the old Murphy's Law thing ... if it can happen it WILL happen. Hence my battery trays. Especially during filling and checking the SG, there's always some spillage on my end.
I've been thinking of adding another turbine to create additional venting and perhaps a little more cooling during the Summer, but might take the step to fully insulate? I don't know.

The reason I asked about separation between controllers and batteries was because of the potential for an electrical discharge of some kind. As you saw, my solar contractor made me seal the battery side 100% away from the controllers.
Your project is of extreme interest to me and I'm sure I will learn more about my system from reading your thread.
Thanks,
 
/ Solar Electric Project
  • Thread Starter
#64  
Rob, I think separation/sealing of the batteries from the electronics is all about explosion protection and corrosion protection. These are the only two issues I'm aware of. Explosion protection is the biggest issue since the batteries off-gas hydrogen while charging. Venting of battery compartments, either convection or powered, is designed to prevent hydrogen buildup.

I remember when I was in college there was a guy working on his car out behind my apartment. There was a huge bag and he went screaming into his house. Somehow he created a spark and there was enough hydrogen to explode the battery and launch sulfuric acid all over the place, including on him. He was OK, but it sure taught me (and I hope him) a lesson.

The inverters and charges have a number of relays in them which are ignition sources for hydrogen, so you want to be sure the gas doesn't get around the electronics.

One thing I did on my last system, and will do on this new one, is to carefully plug the battery cable conduit that runs between the battery box and the power panel to prevent hydrogen from venting through that path. I've also placed the conduit entrance a couple of inches below where the vent will be, which will help too.

One other thought on power venting - I don't think the in-line power vents that are sold for venting battery boxes will move enough air to impact the temp in your shed. I'm guessing that's what you have? Mine just arrived yesterday and it only moves 5-8 CFM. In comparison, a bathroom vent fan moves 30-40 CFM. If you want to cool the shed you will probably need a much bigger fan than the power vents. But if you put something in, be sure it is brushless and that any switches are outside the battery room (no sparks allowed).

The other issues I've heard of is corrosion from the battery gas. I think the other gas emitted is hydrogen sulfide, but I'm not sure. I gather it's corrosive.
 
/ Solar Electric Project #65  
1st I want to thank you for posting so much information on a great project, as a long time lurker on the board and only a recent member I enjoy reading about such wonderful projects. I hope to do something similar at my place in the very near future, assuming the state actually gets the rebate program back.

But I do have one question that I'm suprised that no one else has asked. What about fire danger? I can't see where a wooden battery box will meet NEC or NFPA code for containing a fire. Do you have some kind of plans to put an extinguisher system in the box? I've seen some marine engine compartment extinguisher systems that would help.

Thanks,
 
/ Solar Electric Project
  • Thread Starter
#66  
Lil_FarmerJim said:
1st I want to thank you for posting so much information on a great project, as a long time lurker on the board and only a recent member I enjoy reading about such wonderful projects. I hope to do something similar at my place in the very near future, assuming the state actually gets the rebate program back.

But I do have one question that I'm suprised that no one else has asked. What about fire danger? I can't see where a wooden battery box will meet NEC or NFPA code for containing a fire. Do you have some kind of plans to put an extinguisher system in the box? I've seen some marine engine compartment extinguisher systems that would help.

Thanks,

I'm glad you are enjoying the post - I'm having fun doing it :D

That's a great question, and I think it's an example of one of the many areas where these types of systems are still really immature. I'll have to go check what NEC and NFPA have to say about large battery banks. For better or for worse, these plywood boxes are largely the norm in the industry for off grid residential systems.

It's an interesting tradeoff between wood and metal; Wood's insulating properties makes it much safer when handling or working on the batteries, but it's flamable. Metal poses much more danger with battery handling and maintenance, but would help contain a fire.

I haven't looked into them yet, but I like the idea of an automatic fire supression system. I was thinking about one over the generator, but one over the power system is a great idea.

I have to say that the home-built battery box was my last resort. It's ugly and makes the whole system seem less polished and professional. In looking for alternatives I found:

1) Open rack systems. These are designed primarily for the telco industry and other large UPS installations where you have large rooms filled with batteries. I visited one (computing data center) in Sacramento in the last year and it was quite impressive. This might be what 3RRL used in his battery house where he has the advantage of a whole room (though a small one) dedicated to batteries. In this case, the room is the battery box.

2) Small metal enclosures. These were mostly designed for small, remote communications and signalling installations. They are for much smaller batteries.

3) Mid size enclosures. These are targetted at the small scale RE system like mine, but are still too small or too expensive. I've got one of these for my current system and have been very happy with it. It's a fiberglass/foam box with a lid that encloses the batteries, has a vent hole for easy vent hookup, and is insulated. When I bought it there were different sizes available including one for the 8 L16 batteries in that system. Unfortunately, I couldn't find something similar for the Surrette batteries. I did find a large metal enclosure, but it was way too expensive - something like $5000 if I remember - so much that I dismissed it outright.

The best alternative I could find would have been 3 metal Jobsite tool boxes, but it would have taken up much more space, and the dimensions were problematic given my height restriction in the basement.

If anyone comes across any good boxes, I'd welcome the info for the next system.
 
/ Solar Electric Project
  • Thread Starter
#67  
It's been raining like crazy here, but the other day it broke for long enough to get the remaining batteries around to the basement outside entrance. I ended up take three at a time which lightened the load enough to keep from sinking. It also enabled me to drive over a drier, but more sloped section of the yard without fear of tipping over. Finally, they are all in as you can see in the first picture.

The next shot shows the first interconnect cable. I was playing around with how to best route them to be neat, but keep clear of the fill caps. The routing you see is what I settled on.

Next shows them all interconnected. 12 batteries wired in series with 4V each gives the required 48v. You can also see that I've replaced the fill caps with hydrogen recovery vent caps. These help reduce water loss subsequent filling.

Other than running the main cables up to the wiring panel and breakers, then only thing left is to install the power vent. I'll be sure to do that before hooking up the panels or other charge device.
 

Attachments

  • PCH_2008-07-21-0319.JPG
    PCH_2008-07-21-0319.JPG
    81.1 KB · Views: 128
  • PCH_2008-07-22-0322.JPG
    PCH_2008-07-22-0322.JPG
    59 KB · Views: 117
  • PCH_2008-07-22-0323.JPG
    PCH_2008-07-22-0323.JPG
    82.6 KB · Views: 159
/ Solar Electric Project
  • Thread Starter
#68  
Now on to wiring the panel. The first thing they recommend is to run all the low voltage communications and battery temp sensor wires. There are shielded chases in the back of the wiring panels that aid in keeping the wires isolated from the AC and high voltage DC. However, to get up to the charge controllers they have to venture out into the wiring space. In these pictures you can see the blue wires running into the two charge controllers, then the same blue wires connecting into the inverter. They are standard Cat5 cables, though the electrical protocol isn't ethernet. The silver covers in the lower back of the wiring boxed are the chases.

I also realized that I should not have the battery sensor wire running in the main battery cable conduit, so I ran a second small flex conduit from the panel to the battery box. You can see it in the last picture.
 

Attachments

  • PCH_2008-07-20-0317.JPG
    PCH_2008-07-20-0317.JPG
    58.1 KB · Views: 130
  • PCH_2008-07-20-0318.JPG
    PCH_2008-07-20-0318.JPG
    50.1 KB · Views: 121
  • PCH_2008-07-21-0321.JPG
    PCH_2008-07-21-0321.JPG
    59.3 KB · Views: 142
  • PCH_2008-07-23-0332.JPG
    PCH_2008-07-23-0332.JPG
    64.2 KB · Views: 120
/ Solar Electric Project
  • Thread Starter
#69  
Next step was to hook up the AC. The panel comes with breakers for the generator, inverter, and bypass, and it's all prewired for connecting to the inverter so hookup is a breeze - sort of.

From the factory the panel is wired to have the inverter on the left and the charge controllers on the right. In my config I'm reversing it so I can get the panel closer to the batteries and keep the cable run to 5' rather than 10'.

The first thing I needed to do was move the 200A DC breaker for the inverter from the right to the left of the box. You can see it's original position in the first picture.

In the second picture you can see it's been moved to the left closer to the battery box and directly over the conduit entrance. Then I hooked up all the AC lines to the inverter. The idea was to keep all the AC lines grouped in the upper right and along the right side. You can see this in the picture.

The last picture shows the AC connections to the inverter. You can also see the inverter DC cables which also come pre-wired in the panel. Hook up was a bit touchy, again because everything is focused on being set up reverse to what I did.
 

Attachments

  • PCH_2008-07-21-0321.JPG
    PCH_2008-07-21-0321.JPG
    59.3 KB · Views: 113
  • PCH_2008-07-21-0320.JPG
    PCH_2008-07-21-0320.JPG
    69.5 KB · Views: 121
  • PCH_2008-07-20-0316.JPG
    PCH_2008-07-20-0316.JPG
    49.7 KB · Views: 115
/ Solar Electric Project
  • Thread Starter
#70  
And now for the DC wiring.

When I went to hook up the charge controllers, I had a bit of a surprise. Even though the controllers are designed to mount directly to the side of the wiring panel, and even though there are matching knockouts for running wires, you still need to fabricate and install external conduit between the panel and controllers :( . The wiring box of the controllers is split into two sections; the DC connections and the control/communications connections, and they are separated by a shield. The knockouts let you access only one of the two sections of the wiring box, and you have to run conduit for the other part. Given my left-side attachment, this meant my coms cables had a natural passage, but I needed to fabricate conduit for the DC cables. What a pain. This of course resulted in two trips to town for parts at about 3 hrs per trip :mad: .

Finally, the results are visible in the first picture. I pre-cut and labeled the wires and fished them all through before assembling the conduit ends. I don't know if you've ever tried to thread #6 THHN copper wire through 1" conduit with 90 deg elbows on each end, but it's not a happening thing. Now try 4 wires plus a #10 ground:eek: . Threading it ahead of time is the way to go.

The next pictures show each of the controllers all wired up. It's a pretty tight fit, but it works.
 

Attachments

  • PCH_2008-07-23-0330.JPG
    PCH_2008-07-23-0330.JPG
    54.9 KB · Views: 111
  • PCH_2008-07-23-0326.JPG
    PCH_2008-07-23-0326.JPG
    60.3 KB · Views: 125
  • PCH_2008-07-23-0327.JPG
    PCH_2008-07-23-0327.JPG
    68.1 KB · Views: 135
/ Solar Electric Project
  • Thread Starter
#71  
OK, getting towards the home stretch. Next is to terminate all those wires coming out of the charge controllers. There are 2 60A DC breakers for each controller, for a total of 4 breakers. One disconnects the solar array from the controller, and the other disconnects the controller from the battery.

The first picture shows the 4 breakers and all the wires hooked up.

Then, the batteries. It too a lot of wiggling and pushing to the the cables through the conduit and into place (they are 4/0 THHN with end lugs). In the second picture you can see the negative cable bolted to the negative bus bar. It's the cable on the left. The one on the right goes to the inverter. The bus bar slightly above is the ground bar - not to be confused with the negative bar (visible) or the AC neutral bar (not visible). All are different and isolated in this wiring box. In the main breaker panel, and only in the main breaker panel, the ground and neutral are bonded together. This is all per NEC.

In the last picture you can see the Positive battery cable mounted to the bus plate. The other 4/0 cable in the forground is the inverter + cable.
 

Attachments

  • PCH_2008-07-23-0329.JPG
    PCH_2008-07-23-0329.JPG
    67.7 KB · Views: 123
  • PCH_2008-07-23-0328.JPG
    PCH_2008-07-23-0328.JPG
    56 KB · Views: 129
  • PCH_2008-07-23-0325.JPG
    PCH_2008-07-23-0325.JPG
    69.6 KB · Views: 148
/ Solar Electric Project
  • Thread Starter
#72  
Let there be light!

After checking voltages and checking for shorts, I ducked behind the battery box and touched the final battery cable to the battery. No sparks:D . Next, I flipped the main breaker for the inverter and presto - on it came. After taking it out of standby, I was able to measure 120V on both sides of the 240V circuit, and 240V across it. All good :) .

But, when I threw the breaker to apply the house load, the inverter buzzed and shut down.:( . A little probing revield the one leg of the AC was shorted somewhere. I was luck to find it quickly - on of the cable clamps had pinched too tight and gone through the insulation on the red wire. This is exactly why everything has a safety ground!!! After rerouting the cable, we were in business. With careful throwing of breakers, I can run the house off the old or new inverter.

These last pictures show things getting buttoned up. The next major step is to get the solar arrays assembled and attached, but I'll be taking a break from this for a couple of weeks. The array mounts are still a couple of weeks away from delivery anyway, so there is not much more to do in the mean time. Then I need to get the generator set up, but I'll be waiting on the shop for that. Hopefully, with 3200W of solar, I won't need the generator for a while.....
 

Attachments

  • PCH_2008-07-23-0333.JPG
    PCH_2008-07-23-0333.JPG
    43 KB · Views: 118
  • PCH_2008-07-23-0334.JPG
    PCH_2008-07-23-0334.JPG
    48.4 KB · Views: 120
  • PCH_2008-07-23-0335.JPG
    PCH_2008-07-23-0335.JPG
    56.4 KB · Views: 142
/ Solar Electric Project #73  
Very cool Hayden. Did you look at Outback equipment? If you did why did you choose Xantrex? I'm looking at system components, may try some of the new cheaper companies, (yeah yeah I know) lol. Do you have the 208 page AEE solar catalog? I have it on PDF, if you would like it.
 
/ Solar Electric Project
  • Thread Starter
#74  
Bill Barrett said:
Very cool Hayden. Did you look at Outback equipment? If you did why did you choose Xantrex? I'm looking at system components, may try some of the new cheaper companies, (yeah yeah I know) lol. Do you have the 208 page AEE solar catalog? I have it on PDF, if you would like it.

Yes, I looked at Outback. If Xantrex hadn't come out with the XW series, I probably would have stayed with my current system and just jacked up the batteries and panels. I don't like to Outback stuff for a couple of reasons. First, is that you need two inverters to get a split phase system, plus a balancing transformer. Second, it's a kludgie system. Too many odds and ends that sort of go together, but not completely. Third, their computer interface is incomplete. You can't program the system or even trigger an equalize. Last, it takes up more space.

The XW stuff really goes together nicely as an integrated system. I came across a couple of rough edges, but I still think it's the best there is out there.

Oh, one other thing. The Outback MX chargers have a fan that has a reputation of failing, and it's a pain to replace. The XW has no fan. I like that.

I'll let you know if I feel differently after using it for a few months or a year, but so far I like it. I won't really be on line for another month or so, and 100% ( gen is missing piece) probably won't happen until the fall.
 
/ Solar Electric Project #75  
Nice clean installation! Looks very good!

One question, I heard somewhere that the inverters make a fair amount of noise, a hum maybe? Might have been in reference to a grid tie system if that makes any difference. When your system is complete and running off the pv panels will it make any sound or will it be totally quiet?
 
/ Solar Electric Project
  • Thread Starter
#76  
Bill Barrett - I think I came across too harsh on Outback. It's a widely used product with lots of satisfied customers. The whole renewable energy industry is young, and periodically experiences big steps forward in product design and technology. For years, Trace (now Xantrex) was the only game in town. It was a quality product, but had it's limitations and quirks. That's what I've been running.

After Xantrex bought Trace, the product kind of stalled, and Outback emerged as the new leader. Much of that was due to their MX charge controller which does Maximum Power Point Tracking for solar arrays, a technique developed by Blue Sky to operate the panels at the Voltage/Current point that produces max power and do DC/DC conversion to match the battery voltage. Past controllers just forced the panel voltage to match the batteries causing the panels to operate 10-15% less efficiently. They are solid products, but have their own set of quirks.

From what I've seen so far, the Xantrex XW system has really taken the concept of a "system" to the next level. I've got my fingers crossed that it continues to be solid. Typically you don't encounter all the quirks until you've used a product for a while, and although I've read all the material, I've only scratched the surface in actual use.
 
/ Solar Electric Project
  • Thread Starter
#77  
charlz said:
Nice clean installation! Looks very good!

One question, I heard somewhere that the inverters make a fair amount of noise, a hum maybe? Might have been in reference to a grid tie system if that makes any difference. When your system is complete and running off the pv panels will it make any sound or will it be totally quiet?

Yes, they make a variety of noises, and that's one reason I'm moving my power panel to the basement. My current one is in a shallow closet in our entry vestibule. The closet has louvered bi-fold doors which cover things up, but don't provide any sound protection.

First, there's the 60hz hum. It's around us everywhere and you don't really notice until it goes away. On a light load the inverter sounds like a florescent shop light, but with a heavy load it's more like a fridge. All-in-all not too bad.

Worse, though, is when the cooling fan kicks in. For me, that only happens when the generator is running and the thing is putting out 85A charging the batteries, but man what a howl. When it's cranking we have to close the doors to the vestibule it's so loud and annoying. The fan has never come on due to the AC load on the inverter, but I think it would if it were working real hard for a while.

We are really looking forward to getting it out of the living space, and hopefully having a quieter system. The XW charge controllers don't have fans, so they will be reasonably quiet. I'm still not sure about the inverter. Before I bought it I pulled the panels off one (as best I could) to see if I could spot fans, and I couldn't. I also can't find any reference to fans in any of the manuals. I'll know for sure once I get it running at full power, but that won't be until I've got the generator installed and can do a long battery charge cycle.

I don't know for sure about grid tie systems, but I'm doing one later this summer/fall. However, I'd expect them to be consistently noisy when the sun is out because they always operate at the full power produced by the panels. I'm glad you brought this up - now I'll pay attention to it on this next system when we locate the inverter.
 
/ Solar Electric Project #78  
hayden said:
Bill Barrett - I think I came across too harsh on Outback. It's a widely used product with lots of satisfied customers. The whole renewable energy industry is young, and periodically experiences big steps forward in product design and technology. For years, Trace (now Xantrex) was the only game in town. It was a quality product, but had it's limitations and quirks. That's what I've been running.

After Xantrex bought Trace, the product kind of stalled, and Outback emerged as the new leader. Much of that was due to their MX charge controller which does Maximum Power Point Tracking for solar arrays, a technique developed by Blue Sky to operate the panels at the Voltage/Current point that produces max power and do DC/DC conversion to match the battery voltage. Past controllers just forced the panel voltage to match the batteries causing the panels to operate 10-15% less efficiently. They are solid products, but have their own set of quirks.

From what I've seen so far, the Xantrex XW system has really taken the concept of a "system" to the next level. I've got my fingers crossed that it continues to be solid. Typically you don't encounter all the quirks until you've used a product for a while, and although I've read all the material, I've only scratched the surface in actual use.

Thanks for the feed back, this is the kind of info I'm looking for!
 
/ Solar Electric Project #79  
Loved reading all the posts. I have an off grid, small system in New Mexico at a vacation place. I put 3 195w panels on the top of a storage room, components inside, golf cart batteries in a vented box. I use the xantrex prosine 2k inverter with no problems, and love the outback MX60 charger. It is amazing how it can come up with useable charging voltage from any hint of light. By the way, you can synch 2 of the prosines together in a second to get 240v.

I used to have a 12v gel cell forklift battery set, but lost a couple of cells........I guess that's why they were cheap and well used. Went to regular golf cart batteries with no regrets. The cost of the batteries was a fraction of the cost of one gel cell. I know, they won't last as long, but they work great, and most useage is during the day, shallow discharge at night. Swamp cooler in the day, especially in the summer. Gas fridge really helps. Have to ration power when using microwave, but otherwise have t.v., internet, water pump,power for compressor, fans, etc. lights are 12v on a separate panel and battery for some sort of backup. It's the only choice other than generator, and it works great! Remember, no Air Conditioning or Refrigerator, Electric dryer, etc. at this level!
 
/ Solar Electric Project #80  
Hayden I have a Mx charge controller and a FX inverter and its in our mud room and the only noise I notice is the fan no AM or FM or TV noise.

tommu
 

Marketplace Items

2018 International 4300 TMA (A60352)
2018 International...
2014 FORREST RIVER SALEM TRAVEL TRAILER (A60736)
2014 FORREST RIVER...
2019 Big Tex 14TL (A60462)
2019 Big Tex 14TL...
2024 Linx UT357712T (A60463)
2024 Linx...
2023 Deere 317G (A60462)
2023 Deere 317G...
500 BBL FRAC TANK (A58214)
500 BBL FRAC TANK...
 
Top