Simple Electrical Question (hopefully)

   / Simple Electrical Question (hopefully) #11  
The answer is not really simple. Well, it could be but there are a lot of things to look at here. You did not mention if the cable has Aluminum or Copper conductors. Could make a difference here. You didn't say how many "several years ago" was. The conductors could be 60ー, 75ー or 90ー rated. Are they type UF, THWN, THHN, THWN-2, XHHW, XHHW-2? It makes a difference.

Let's say it's copper type THWN-2 and they were 90ー rated, such as in type NM-B cable.
First, NEC Article 110-14 says if the circuit is under 100A then the conductors need to be used at their 60ー rating, unless all terminations in the circuit carry a higher rating. #6 copper at 60ー is able to be used at no more than 55A. However, there is a way out here. According to NEC 240.6, 55A is not a standard fuse/breaker size so you are allowed to round up the the next standard size which is 60A. So if you had a 6-3 type NM-B cable run, you are good to go with a 60A breaker on a 45A load.

Now, let's say it is Aluminum conductors.
#6 at 60ー is only good for 40A according to NEC 310.16 and 110.14

So I need more info to accurately answer your question. Post what cable type was run and I'll try to help more.

Great Post to help a friend!!!
 
   / Simple Electrical Question (hopefully)
  • Thread Starter
#12  
Thanks a bunch, I'll be glad to use the tub to it's max features.
 

Tractor & Equipment Auctions

2005 Ford Explorer 4X4 SUV (A55758)
2005 Ford Explorer...
2020 Caterpillar D5K2 LGP Crawler Tractor Dozer (A55787)
2020 Caterpillar...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
TOYOTA 8FGU15 WAREHOUSE FORKLIFT (A52705)
TOYOTA 8FGU15...
2023 54' Hooklift Dumpster 20 Cubic Yard (A55788)
2023 54' Hooklift...
2018 MACK CHU613 DAYCAB (INOPERABLE) (A53843)
2018 MACK CHU613...
 
Top