Question for electricians

/ Question for electricians
  • Thread Starter
#101  
Not sure how yours is setup. Mine has 2 separate meters and 2 separate CT’S set to read both phases. Mine reads Volts, Amps and frequency

View attachment 3795486
The setup is:
-Power box is plugged in 50 amp generator outlet
-Cable from power box plugged in wall outlet connected to 50 amp
circuit breaker in the panel.
-There is manual interlock kit installed so generator serves whole house
 
/ Question for electricians #103  
There's no owner manual
Do you have a clamp on ac meter?
I’m guessing it’s only equipped with 1 current donut, and is probably only valid amp and power readings for balanced loads.

If you want to see what it’s measuring, and you do have a clamp on, turn off all breakers except a 240 volt load like an active electric range, and see if the current measurement agrees . Then do the same test using only a 120v circuit on L1, finally another test using only a 120v L2 circuit.
This will let you see what your new unit is actually measuring.
 
/ Question for electricians
  • Thread Starter
#104  
Do you have a clamp on ac meter?
I’m guessing it’s only equipped with 1 current donut, and is probably only valid amp and power readings for balanced loads.

If you want to see what it’s measuring, and you do have a clamp on, turn off all breakers except a 240 volt load like an active electric range, and see if the current measurement agrees . Then do the same test using only a 120v circuit on L1, finally another test using only a 120v L2 circuit.
This will let you see what your new unit is actually measuring.
Thank you! I'll try that
 
 

Marketplace Items

UNUSED KJ 20' BI-PARTING GALVANIZED GATE (A62131)
UNUSED KJ 20'...
207274 (A52708)
207274 (A52708)
6069 (A61165)
6069 (A61165)
2002 INTERNATIONAL 4700 4X2 LANDSCAPING TRUCK (A59908)
2002 INTERNATIONAL...
2024 Kubota SVL97-2, PIN: KBCZ064CJN1J72104 (A61166)
2024 Kubota...
2019 FORD F-150 STX CREW CAB TRUCK (A59823)
2019 FORD F-150...
 
Top