HVAC disconnect question

/ HVAC disconnect question #21  
Here we go, over thinking again. The old adage KISS applies here!
 
/ HVAC disconnect question #22  
Well, ive been doing commercial and industrial electrical for 35 years. All our motors have a fused disconnect. And all motor control panels have multiple fuse protection devices along with heaters . Breakers are always rated 125% over motor loads. Offer limited protection .


but i digress from OP. The states i work in require that we follow nameplate on device. For instance my AC unit has a nameplate that states minimum fuse size. I HAVE to use fuse. If label says minimum OCPD (over current protective device) then you can use a breaker. All this is superseded by whatever manufacturer requires. Most A/C Manufacturers install paperwork i used to read REQUIRED a fused disconnect, so it was never an issue.
 
Last edited:
/ HVAC disconnect question #23  
Well, ive been doing commercial and industrial electrical for 35 years. All our motors have a fused disconnect. And all motor control panels have multiple fuse protection devices along with heaters . Breakers are always rated 125% over motor loads. Offer limited protection .


but i digress from OP. The states i work in require that we follow nameplate on device. For instance my AC unit has a nameplate that states minimum fuse size. I HAVE to use fuse. If label says minimum OCPD (over current protective device) then you can use a breaker. All this is superseded by whatever manufacturer requires. Most A/C Manufacturers install paperwork i used to read REQUIRED a fused disconnect, so it was never an issue.
I have had a number of corrections (from inspectors) due to the manufacturers label saying minimum fuse size, and then being required to install a fused disconnect to pass inspection.
If it states minimum OCPD (overcurrent protection device), then a breaker in the panel can be the protective device and non-fused cheap disconnect can be installed next to the HVAC unit.
 

Marketplace Items

2025 SAWYER 85BP20 20FT T/A ENCLOSED BUMPER PULL TRAILER (A59910)
2025 SAWYER 85BP20...
Miva MS36C Skid Steer (A62183)
Miva MS36C Skid...
High-End Mini Golf Cart (A62183)
High-End Mini Golf...
LILLISTON 2R ROLLING CULTIVATOR (A63290)
LILLISTON 2R...
2011 Honda Civic Coupe (A61574)
2011 Honda Civic...
2006 Ditch Witch H313 Trencher Attachment (A62183)
2006 Ditch Witch...
 
Top