generator to home panel connection

/ generator to home panel connection #61  
And people need to realize that these aren't all new homes that have never had a generator, So making new codes is OK. But its not like we tear the house down each year and build it to the present codes.
i think most understand that the codes are there for a reason.But also that it doesn't mean we have to redo things to meet the present day codes.
 
/ generator to home panel connection #62  
Bedlem,, I think most of them are talking about installing something "new" on an old,,,or new home.. It dosn't matter if it is a new or old home when something electrical is installed it must meet current codes.. not the codes when the house was built...Just looked in the oldest code book i have,,,1987,,dad has the older ones,,he's 94 and still trying to find them,,lol
230-83 Transfer Equipment... Transfer equipment shall operate such that all ungrounded conductors of one source of supply are disconnected before and ungrounded conductors of the second source are connected

Brin.. the link looked good I think you will find a "UL" tag on that.. I see what you ment about the 2 switches you throw now...the link you gave though shows only 50amps allowed on the gen set side,, seems low..??
 
/ generator to home panel connection #63  
What I meant is the only 100% way not to backfeed is if your not hooked up to the grid, anything can break! I used to do machine repair and we always disconnected power then locked the box first. Maybe overkill, but safe!
That said wow a lot of upset folks here, guess I can understand why -- but Im glad no codes where I live! Thanks to everyone I learned a lot here on this post!
 
/ generator to home panel connection #65  
Crazy, isn't it?

There is a 0% chance of having a rational conversation about generators here.

Zero.


Then I suppose my plan to shinny up the pole and attach jumper cables is off the table? :D
 
/ generator to home panel connection #67  
They wouldn't have to be long because you would definitely install a meter right after the jumper cables:D and then underground wire from there in.LOL
 
/ generator to home panel connection #68  
Ooo man now you bring up the safety of climbing poles without the proper safefty equipment...:eek:
 
/ generator to home panel connection
  • Thread Starter
#69  
Then I suppose my plan to shinny up the pole and attach jumper cables is off the table? :D

and on that note, i just pulled my dog out of this fight:D
 
/ generator to home panel connection #70  
I understand the issues linemen have with this backfeeding. You shall understand the issues we consumers have when the power goes out. We are not all stupid consumers.

Did not say all are stupid, all it takes is one. Yes, I will admit I fully expect to find a backfeed when I check out a homeowner with a honda generator running his house during an extended outage, have found too many during my years. Most of the chicken houses in the area have back up, never found one that would backfeed. I think most of the problem is the areas that do not deal with extended outages as a way of life and have to plan for them but then I do understand there are stupid people all over. Guess I am a bit touchy right now, found out this afternoon we have a young man that got burnt last night. Tomorrow, Sunday, he will lose his left leg above the knee and part of his left bisep. Do not know what happened yet, just know a fine young man has had his life forever changed.
 
/ generator to home panel connection #71  
I know what you're feeling, ninefinger, I've been in the same situation as you find yourself in now. My thoughts are with you and especially the young man.
 
/ generator to home panel connection #72  
Then I suppose my plan to shinny up the pole and attach jumper cables is off the table? :D

Hey, while you're up there you may as well bootleg cable off of your neighbors line. Backup power ~and~ free cable.... Sweet!:D
 
/ generator to home panel connection #75  
I thought the original device described was clever (the mechanical interlock plate). It seems a bit disingenuous to to suggest someone might disable the interlock by removing it-- they can do that for any device installed including automatic transfer switches. If it doesn't seem to be working right, so just jump some wires from "A" to "B"...

What seems to be missing is that cheap and dirty solutions are far more common than the mechanical interlock plates. At least around here, it seems fairly common to use a simple suicide cord (male-male) to connect a genset through the dryer outlet, and to have to "remember" to cut off the main breaker:eek:.

For a while the local power company was offering something like the GenerLink. This seemed like a good idea, except that the monthly rental was 14.95 (plus taxes)!

I prefer automatic transfer with critical functions like computers running on UPSs. Being the NY Metro area with crumbling infrastructure, the power here isn't very good... short outages (less than 30S) about 6-12x/yr, longer outages (hours to a day) about 1-3x/yr and very long outages (1-18 days) every 2-4 years.
 
/ generator to home panel connection #76  
image.jpg Don't see the issue if Eaton/Cutler Hammer sell them on their website saying they are UL listed and ROBUST
 
/ generator to home panel connection #78  
Mace - thank you for a 10 minute chuckle. I will without any hesitation steal your "Stuck on Stupid" as a useful descriptor of those unable to change their brain gears.

As well, after reading through this thread, you've convinced me of one thing - I'm hiring an electrician to do a proper install of a proper switching system. Better safe then lawsuit.

hahahahahahah'stuckonstupid'hahahahhaahahahhh
 
/ generator to home panel connection #79  
didn't realize this was such a polarizing item

There are those who will trade safety for the Almighty Dollar.
I haven't read the entire 8 page post yet but...........you are back feeding using a clothes dryer receptacle? Are you using a male plug with exposed live prongs on the generator side?
 
/ generator to home panel connection #80  
i've worried about how much current is running thru the ground

I'm not an electrician but i don't think i've ever even seen a 30a dryer receptacle - every clothes dryer circuit i've seen was 60A, same as electric hot water heater

i am dying of curiosity - where did you see mention of a 30a receptacle? Running a 50a circuit thru a 60amp receptacle would seem to be on the safe side and having accumulated 577 hours on this generator, with no meltdowns, i feel kinda safe in assuming it is -


PS -
genreceptacle.jpg

There is no current flowing through ground if wired correctly. Just what exactly are are you doing?

You are not an electrician, yup I could tell that a while back

Pure BS on the currents. An electric clothes dryer is a 120/240V 30 amp four wire plug. An electric stove is a 50 amp 120/240 four wire plug.

Just because it "works" doesn't make it right.
 

Marketplace Items

159116 (A60430)
159116 (A60430)
Preliminary Listing / Full Catalog Coming Soon! (A62177)
Preliminary...
Skid steer Asphalt attachment (A61567)
Skid steer Asphalt...
2025 Kivel Quick Hitch Skid Steer Attachment (A61567)
2025 Kivel Quick...
2012 Chevrolet Impala Sedan (A61569)
2012 Chevrolet...
(2) UNUSED 27X10.50-15 TIRES W/6 LUG RIMS (A62130)
(2) UNUSED...
 
Top