don't know how many are aware, but there's an approved alternative to the transfer switch boxes (that run anywhere from $300 - $700) called "generalor interlock kits".

you will have to check with your local building inspector's office, but they're idiot proof fail safe - you are mechanically prevented from turning on the generator circuit if the main breaker is in the "ON" position. I actually liked the idea enough that I built my own (I was too cheap to pay for the custom one my panel box would have required. I did submit it to the electrical inspector for approval, mainly for insurance coverage purposes. I believe they start around $149 for the more common panel boxes - unfortunately mine was one of those - they'd had to modify an existing plate and wanted something like $200 for mine.

main reason I prefer the interlock kit idea over a transfer switch box, it allows me to simply feed the entire panel box w/240V and use the existing breakers - in an outage we're careful in terms of what we turn on, but this way, no matter what room we walk into, we've got lights if we need - no need to run an extension cord for the wife's hair dryer, etc. And no need for an electrician to install the transfer switch box, which just adds to the cost

basically i feed the panel box thru an electric dryer receptacle installed just below the panel box connected to a 60 amp dbl brkr, so when the interlock kit is moved to allow that breaker to thrown to the "on" postion, it feeds both 110v legs of the box


link to generator interlock kit: Generator InterLock Kit

Generatorinterlockkit.jpg



and my home made one - the red instruction plate i simply made myself in microsoft word, and used laminating plastic to place it on the top sliding plate. Figuring out the steps necessary in microsoft to get text inside a "frame" took me almost as long to fabricate the two plates (i'm maybe half notch above fred flintstone level in computers)

i used .090" 6061 alum with bellvue washers over nylon washers for the tension lock between the two plates - but's it's actually the main breaker that keeps the lock out plate from sliding down and releasing the gen breaker - as long as the main breaker is up in the "on" position, the lockout plate can't slide down - the tension washers are basically to keep the wgt of the sliding plate from putting any force on the main breaker

homemadegeneratorinterlockpix.jpg
 
/ generator to home panel connection #2  
Ive looked at those interlock kits and was considering one. Certinally a convient way to hook up a gen. Several of the panel manufacturers make a "Backfeed" kit that does the same thing, for a similar price.

I tried emailing the Company to confirm if they were CSA approved and usable in my area. They never got back to me:mad: Local Hydro, knows nothing about them.

Price is high, for what it is, but you need to remember that theres alot of costs in there for getting it approved.


Too late for you , but another option is the GenerLink.com - About GenerLink - The easy way to connect a home generator Some hydro companies actually sell them and will bill you for it monthly. Its a really easy install, just goes between your meter and its base. Installs in 5 mins.:eek: more expensive than your option but significantly cheaper than a traditional transfer switch when installation is considered
 
/ generator to home panel connection
  • Thread Starter
#3  
just noticed you're in NS - can i ask where?
we almost moved there - had a contract on a motel in Yarmouth and seller backed out

i've still got a camp in Maxwellton (inland from Meteghan)
 
/ generator to home panel connection #4  
60 amp breaker feeding a 30 amp dryer outlet...???:confused:
 
/ generator to home panel connection
  • Thread Starter
#5  
60 amp breaker feeding a 30 amp dryer outlet...???:confused:

??? uhh, no, a 60 amp receptacle feeding to a 60 amp breaker - nothing feeds to that receptacle from the panel, nor can it, when the main breaker is in the "ON" position as the main breaker can't be moved to "ON" unless the gen breaker has been moved to "OFF" position

generator has a 50 amp breaker controling the circuit as it feeds the receptacle which is backfeeding into the panel box

and before you ask, i used that dryer receptacle and that dbl breaker as those were already here, installed, and were freed up when i converted to natural gas clothes dryer
 
/ generator to home panel connection #6  
AT&T, Verizon, Quest and all of the other telcos have without exaggeration well over a million of these in use in virtually every community across the country for all their equipment (anything fed by fiber optics) that needs generator backup when ever there is a commercial power failure.

Their bigger equipment at cell sites and other larger installations have auto-transfer switches where there are generators on site, but for almost all of the 30-100 amp locations, they all have manual transfer switches.
 
/ generator to home panel connection #8  
Mace :D Sooo right.. Nothing takes the place of a "REAL" transfer switch
 
/ generator to home panel connection #10  
A few hundred dollars extra for an approved gen panel is far less expensive than hospital costs from electrocution or home replacement costs from insurance claim.

Buy once, cry once.
 
/ generator to home panel connection #11  
If you do a search, you'll see that this whole issue has been discussed in depth before, complete with passionate arguments for different opinions.
 
/ generator to home panel connection
  • Thread Starter
#12  
didn't realize this was such a polarizing item
 
/ generator to home panel connection #13  
didn't realize this was such a polarizing item

Anything safety related seems to incite heated discussion.

I considered fabbing up my own interlock like you did. but ended up installing a more traditional partial transfer switch. If I ever have a new service box installed, I think I'll go with one with the built in interlock, since it allows one to power every circuit during an outage.
 
/ generator to home panel connection #14  
The kits from Interlockkit are listed, not by UL, but still listed by a NRTL.
They are acceptable here in Ohio.
 

Attachments

  • Interlock.jpg
    Interlock.jpg
    28.2 KB · Views: 349
/ generator to home panel connection #16  
while i respect your experience, and agree with the assessment that a portion of the population is "stuck on stupid", i'm not sure what you feel would make someone "stuck on stupid" any less inclined to removing the panel cover on a panel box employing a transfer switch to "tweak" or "adjust" it - and effecting a dangerous scenario

Being the owner of a double pole, double throw transfer switch wired between my meter and entrance panel, I can't imagine how anyone "stuck on stupid" (I love that!) could configure the device to backfeed into the grid without electrocuting himself (or to be fair, herself) or committing an act of criminal negligence. The DP/DT transfer switch is about as close to idiot-proof as anything can be. I can't imagine a mechanical failure of the switch that would allow a backfeed, unlike the device featured in this thread . The price I paid for the switch and professional installation of it is an investment in peace of mind and one more payment towards a clear conscience.
 
/ generator to home panel connection #17  
as a side note, they still haven't replaced the underground cable leading up to my house meter - apparently, their words, a mole or something has broken the insulation on one leg or wire and moist soil grounds it out when it rains but it hasn't been permanent outage or occurred often enough so they've left without replacing it

That scenario speaks volumes about the attitude of your local utility and more importantly, your (lack of) understanding of the dangers posed by allowing that condition to exist on your property.
 
/ generator to home panel connection #18  
You are right this is a very passionate subject.. There are those of us that like to do things the tryed and true way then there are those who don't.. The "easy" way out and does work, is to buy a "UL" listed device to do what you are doing Larry.. You can make your own,,also and it looks nice,,good job,, But in the UL one you "copied" there were captive screws that were flat on the backside... #1- so that they would not come close to anything behind the panel cover #2 - and so that no nut's or washers will fall down into your live panel... I wonder if it were to cause a problem and you were to contact your insurance company for damages if they would cover it,,hmmm I think not,,,even if you still had the letter from your local inspector after the fire.. I wonder if he could be held liable .. #3- you are still also running your 50a breaker from your gen. into a 30a dryer outlet "and I wonder if it is 3 wire or 4 wire"???
 
/ generator to home panel connection
  • Thread Starter
#19  
That scenario speaks volumes about the attitude of your local utility and more importantly, your (lack of) understanding of the dangers posed by allowing that condition to exist on your property.

i think it sez exactly the opposite - i've called & written the SCC about it as i am aware - i've worried about how much current is running thru the ground and will it fry my bird dogs if they step on the wrong wet spot in the yard (have no kids, here or in the neighborhood as everyone around me is same as i am, 60s and yard is fenced) - but unknown what else i can do short of sending a couple ninjas to take a utility company manager hostage till they fix it?? I suspect the odds are low as the ground will absorb a lot of current, but still i mentioned it as i think the odds of it hurting my bird dogs is greater than my allowing anyone inside my panel box to do anything stupid.

As to your point on not imagining what someone stuck on stupid could do to defeat a transfer switch - i can imagine quite a bit if that transfer box is mounted next to the panel box and not outside - if i'm wrong on that, correct me as i'm not an electrical engineer but have seen my share of idiots - i used to be in real estate and had a tenant burn a house down in the 80s when he, to save on electrical bill, installed his own flourescent light fixture in the kitchen ceiling fixture, using masking tape in lieu of electrical wire nut - fire department identified cause of fire


hr3 "...But in the UL one you "copied" there were captive screws that were flat on the backside... #1- so that they would not come close to anything behind the panel cover #2 - and so that no nut's or washers will fall down into your live panel..."

and what i used were barrel nuts (McMaster-Carr) - the back side of the panel cover was abraded where the head of the barrel's head would contact, and JB Weld applied under the head before installing - that nut isn't going anywhere without a propane torch to soften that JB Weld - next time can i suggest you not assume, in advance, you know what someone "didn't do"

and as to "....#3- you are still also running your 50a breaker from your gen. into a 30a dryer outlet "and I wonder if it is 3 wire or 4 wire"???"

i have no idea where you read that i'm running a 30A dryer receptacle. A) i am using a pre-existing circuit, both the receptacle and breaker that were here, installed and feeding an electric clothes dryer when i moved in (i converted to natural gas right after we moved it, so that freed up that circuit and receptacle) - house was inspected by electrician, as part of purchase b) panel was inspected by county electrical inspector - i don't think it would have survived those two inspections if that were a 30a dryer receptacle. I'm not an electrician but i don't think i've ever even seen a 30a dryer receptacle - every clothes dryer circuit i've seen was 60A, same as electric hot water heater - i could be wrong, that a 30A dryer circuit exists but it would seem to be an awfully slow drying cycle. but i am dying of curiousity - where did you see mention of a 30a receptacle? Running a 50a circuit thru a 60amp receptacle would seem to be on the safe side and having accumulated 577 hours on this generator, with no meltdowns, i feel kinda safe in assuming it is -


PS -
genreceptacle.jpg
 
Last edited:
 