...people had run out of propane in the first week...
I've lived within 30 miles of the same place for 51 years, and we have never seen an outage longer than 4 days. I'm no saying it couldn't happen, but for any event to have so much impact in a region so used to dealing with everything from hurricanes to blizzards, I'm guessing a generator might not be my biggest problem.

Heck, the eye of Hurricane Sandy passed straight over my house, the place looked like a complete war zone, and we
still had power restored in something like 2-3 days.
Besides, what's the alternaive solution? Install 2000 gallons of propane capacity, on the off chance we might have the longest-ever-recorded outage sometime between now and when I die? Doesn't feel like a very good gamble, compared to just making reasonable effort to ensure my current 500 gallon tank never dips too low.
There are also load shedding things that will just disable circuits if grid power fails, rather than waiting for the generator to fail at it.
Yes, this is the old way of doing it, and what I had in mind when people talked about shedding loads. But I don't think I would want that here, there simply is no major load I'd be willing to do without for the entire duration of an outage.
If propane consumption and delivery
really become a problem, I can always manually shut off some loads, such as my heated and cooled shop or the swimming pool. But avoiding having to regularly shut down and then recover a pool left to stagnate and turn green, or deal with damage to equipment and chemicals in the shop, are a few of the primary reasons I want an automatic standby generator in the first place.
... not going to be able to run AC.
Not run AC in July?!? My wife has rented hotels during outages, for lesser reasons!

(I'm not kidding.)
@WinterDeere, I think that you are underestimating the no load consumption. From experience, propane/gas generators can consume almost the same amount of fuel at 0 (no load) and at 1/4 power loads as they do at 1/2 power.
I remember you or someone else saying this previously, so I asked two installers about it this week, and they both disagreed. One guy actually named the no-load consumption at 0.5 gallons per hour on their 26 kW air cooled, which almost perfectly agrees with the 0.49 gal/hour no-load intercept Generac's data yields for their 28 kW Next Gen model.
A simple linear fit on the Generac data gives usage at 0.49 gal/hour + 0.124 gal/hour/kW. But even if we take the absolute worst case of the thing burning it's listed "1/2 load" consumption of 2.23 gal/hour, that's still 78 hours = 3.3 days for your proposed 35% drawdown on the tank from 50% to 15%. And I can't imagine any generator is actually going to burn it's rate listed for 13 - 14 kW load, when seeing an average load of only 2.5 - 5.5 kW... can you?
And here, where the natural gas consumption of a 30 or 40kW unit at 1/4 load is about half of the full load.
Yes, that's pretty close to correct, according to the Generac data. But I think you're drawing the wrong conclusion from that, because:
1. You're talking about natural gas, but the drop-off rate in LP is greater than Nat.Gas. Generac lists their half-load consumption in Nat.Gas at 61% of their full-load consumption, but only 56% in LP.
2. Linear extrapolation of Generac's own data yields a quarter load consumption of 42% of full load for Nat.Gas, but only 34% in LP.
3. My average load is not anywhere near quarter load or half load of the proposed models. It is only 10% most of the year, peaking at 20% in July and August.
Just trying to help make sure that the rest of the family is fine if you aren't on deck to tend to things.
As much as I'm arguing, I appreciate that. I think we'll need to do some test runs to shake things out, and see where we actually stand. I do know that I'll be making an effort to check tank level ahead of any planned travel, and to just put an order in anytime I find it nearing or under 50% full.
I seem to remember my supplier having an up-charge for any delivery under 100 gallons, which is really only 20% of tank capacity. Believing they usually target filling to 80%, that allows me to call them for a fill any time the tank is under 60%, without having to hear from them about any "shorted delivery" hassle. But when push comes to shove, I also don't mind just paying whatever surcharge they'd apply, if that's what it takes to make sure we stay up and running.