I go twice the hp rating, so I'm running a 15hp rated VFD (Hitachi). The lathe in my avatar runs off of a 20 hp motor that is the size of a small block V8. I only fed my shop with 60 amps and the Spedestar drive (40 hp) starts it over a 10 second duration. I have programmed the digital readout on the drive to show the amp draw, and it only pulls 23 amps on start up and 19 amps idling. Most I've drawn is 28 amps on a deep cut. I have them on five different machines, all at twice the hp of the motor with zero issues so far. Note: there are some VFD's I've seen advertised specifically for single to three phase applications that are rated for the single phase motor hp.What sized VFD did you get to work with the 7.5HP motor? In my experience, it a gamble as to weather you need a 10 or 15HP drive.
According to spec, you should have a drive 1.5x's larger than the motor wanting to be driven. (or you need a motor with no more than 2/3 the power rating of the drive.
Most common stuff that us weekend warriors play with work out even. IE, 5HP motor with a 7.5HP drive, and 10HP motor with 15HP drive. But 7.5 hp motor really only needs a drive rated for 11.25hp. Kinda on the bubble as to weather a 10HP will work. If you try to pull too many amps through the drive, it just faults. No worries of burning things up, it just dont work. For an air compressor, intermittent use, if you got a 10hp drive to work that would be nice, not having to make the jump to a more expensive 15HP drive.
I got a 10hp 3 ph motor to run nicely on 240 single phase by using capacitors and a starting relay. I used 220 uf run capacitors and 900 uf start capacitors. It's putting out about 8 hp near as I can figure, but would probably do more If I had more load on it. Motor takes a long time to even get warm. It cost a little over $100. I got the run caps at Surplus center, the start caps on Ebay. I had the relay.
You basically made a static convertor. 8hp is a bit optimistic. How did you "figure" you are getting 8hp.
If you want.to get 10 HP, you need a 15 HP pony motor, use the caps to start it, and run the 10hp motor off that. That's a rotary and good for the full HP if you need it. Just cleaner and easier in the long run to go vfd's if you need the full power, and more adjustable too. Only downside is you can only run a single motor at a time
Just did a quick search and you're looking at about $1100.00 for a 20 hp VFD.
You basically made a static convertor. 8hp is a bit optimistic. How did you "figure" you are getting 8hp.
If you want.to get 10 HP, you need a 15 HP pony motor, use the caps to start it, and run the 10hp motor off that. That's a rotary and good for the full HP if you need it. Just cleaner and easier in the long run to go vfd's if you need the full power, and more adjustable too. Only downside is you can only run a single motor at a time
Static converters are only good for around 60% of the motor's capacity because you're not energizing 1/3 of the windings. You also end up with less torque than a single phase motor of the same size, and that's way less than the 3ph motor you're using when it's given good stiff power on all three legs.
I'd never run one on a high load application like an air compressor. I can't bring myself to run one on a 2hp mill.
Check the specs. on Ronk's website they tell a different story.. I've used several of them and seem to be very reliable and inexpensive.. I have also used a lot of VFD's and love them but price here is the issue..
I got my 75HP (that's not a typo!) VFD for $750 shipped. The smaller ones cost more than the bigger ones. You can set load limits in the controls on the higher end drives.
As most of the guys have said, you want to de-rate the drive by half, but going bigger is perfectly acceptable.
I did the motor swap to single phase on my T30 IR compressor before I realized the VFD's soft starting would actually pay for the conversion in energy not used, and then later yet I've discovered that the reactive current from the VFD's (I run 3 motors on them now) actually confuses my digital electric utility meter into thinking we're putting back more than I'm using. It runs our bill backwards when I'm in the shop a lot; which just means we don't pay as much to keep the wife at 72F in the summer time.
Some VFD's will have a leg-loss fault that you'll need to program to ignore. Every VFD on the market made for 3Ph will run on single off two legs. You can't get a VFD made for higher voltage to run off 220-240 though, they'll error out on low input voltage and it's not user fixable (I've tried). So as long as it's the correct input voltage and 2x the power of your load, you're set. You can get universal transformers to bump 240v up to 480 etc - and then run machines that are wired with controls that would be too much trouble to convert. A VFD will run on the input side of a big transformer.
Static converters are only good for around 60% of the motor's capacity because you're not energizing 1/3 of the windings. You also end up with less torque than a single phase motor of the same size, and that's way less than the 3ph motor you're using when it's given good stiff power on all three legs.
I'd never run one on a high load application like an air compressor. I can't bring myself to run one on a 2hp mill.
ECONO-PHASE Shifter - Static Phase Converters - Ronk Electrical This?
Says right on it for light to medium loading: i.e., NOT full power.
All three legs of my motor are getting power. The third leg is getting power through the run capacitors, which provide the required phase shift. I don't know if commercial static converters have run capacitors or just start capacitors. The motor reaches full speed in less than a second and runs with no audible hum.
How about a picture of that VFD?