70 amp service
/ 70 amp service #21
<font color="blue"> Utility companies...can run lighter gauge service laterals from the transformer to your meter than you are allowed to run from the meter into the service entrance.</font>
Now there's a scary thought! /forums/images/graemlins/shocked.gif
I was lucky with mine and the utility company asked me what I intended doing in the barn and (thinking on my feet for once in my life) I said, "I'll have compressors, welders, plasma cutters sandblasters and some other equipment running in there" so they ran a #2 drop in from the pole for me instead of the standard #4. It was the same kind of 'logic' that I employed when I went with the 200 amp service in the first place; If I get it now, it's there. /forums/images/graemlins/smile.gif If I don't and then need to upgrade later, it's going to be expensive. /forums/images/graemlins/frown.gif
/ 70 amp service #22
It wouldn't surprise me if there wasn't enough power to your home...
Contact the power company and discuss your options.
I would personally have 2 seperate 200 amp services, 1 for the house and 1 for the work shop, especially when your dealing with welding equipment.
$10 extra per month is nothing compared to the aggrevation of NOT having enough power.
/ 70 amp service
Took the collective advice of many responses and started with the village. Village electric says there is plenty of power at the pole across the dirt road from us, but the overhead lead to the house is undersized. But, since it's an overhead run instead of a buried line, the village will upgrade that at no charge, connecting it to the meter.
From the meter on is my responsibility. Called an electrician and after looking it over and listening to my (exaggerated) needs, he suggested bringing 200 amps into a new box, splitting it there with 100 amps going directly to the shop and another 100 amps feeding the existing box. That sounds pretty good to me!
Thanks again for all the sound advice! Pete
/ 70 amp service #24
Sounds like you got some good advice. Just make sure the electrician understands the things you'll be doing in the shop. I suspect that 100 amps is enough but like has been said before, cheaper to do it now than upgrade later /forums/images/graemlins/smile.gif
/ 70 amp service #25
Pete,
Just for the fun of it, ask your electrician how much more it would cost to bring 400 amps in and split it into two 200 amp services. I think you'll be surprised at how little the difference might be (though that's based on my experience with comparing 100 amp to 200 amp service). If you go with the 400 going to two 200 amp boxes, you'll never have to worry about whether or not you'll have enough for about anything you'll ever want to do.
I know it's easy for me to spend your money like this, but, trust me, it'll never be cheaper to do than it is right now. /forums/images/graemlins/smile.gif
/ 70 amp service #26
Gary, the trap on the 400 amp is that you'll enter the 'commercial' market product line. In general... 200 amp and less is considered ' residential' and is priced very competatively. Above that you pay a premium. There is no real standard or code that says so, its just the way the industry has evolved.
/ 70 amp service #27
I kind of wondered about that. I still hope Pete looks into it with his electrical contractor. I'm still curious to know what the cost differential is, even if it is on the salty side. /forums/images/graemlins/smile.gif
/ 70 amp service #28
When we built our house last year we had 400 amp service put in. We broke 200 amps off for the house and left 200 amps (and a dedicated disconnect box/switch) for a future building/barn. I was wondering, how far can you take the electricty after it has went through the transformer. I originally planned to put the building a 100' or so from the house. However, after living there for a year, there is a better spot (in terms of traffic flow, etc.) 150' away. Is there a limit and if so, how much?
/ 70 amp service #29
Ask your electrician about a pass through box. A pass through box has lugs on the bottom of the buss bars so you can connect your branch circuit conductors and then run to the barn. That way you can cut everything off in the house and have the full 200 amps in the barn if you ever need it. You can add a disconnect below the box so you can cut the barn power if you want.
/ 70 amp service #30
How far ?....Well that a fair question. Wire is sized to allow for a specific amperage at a specific voltage drop. The amount of heat generated and the wires ability to disipate that heat also play a factor.
To get electricity down a wire, you have a resistance to flow ( which is quite small in copper wire ). This resistance creates heat ( just like a toaster, but hopefully a lot less ) and costs volts ( pressure to push the electricity ). You don't want too high a voltage drop or your 220 volts just became 200 volts and the electrical equipment and motors aren't that happy.
To compensate for this drop, you can oversize the wire making the electron flow easier and reducing the drop.
Now for the good news...a 200 amp feeder shouldn't really care about that extra 50'. Go for an extra 250' and you'll need to start looking at the size of the wire to minimize the voltage drop.
You're probably looking at a 4/0 feeder size. That's about the size of your finger !!
/ 70 amp service #31
</font><font color="blue" class="small">( I was wondering, how far can you take the electricty after it has went through the transformer. )</font>
Another issue is to verify the transformer supplied is
sufficient for your service. I have seen undersized
transformers supplied to new installations with the
rationale of upgrading to a higher KW unit if and when
the demand exists. On the other hand the step-down
transformers are typically designed to handle double of
rated capacity on a fractional duty basis.
/ 70 amp service #32
</font><font color="blue" class="small">( Now for the good news...a 200 amp feeder shouldn't really care about that extra 50'. Go for an extra 250' and you'll need to start looking at the size of the wire to minimize the voltage drop.)</font>
The rule of thumb is to keep total voltage drop under 5%.
This includes everything from the transformer to the load
(service lateral, sub panel feeds, breaker-to-outlet).
If you consume too much of the voltage drop budget in the
lateral, you may have to deal with the issue multiple times
downstream.
/ 70 amp service #33
/forums/images/graemlins/tongue.gif Reading through the list of postings to your original query, I can see lots of good advice offered here. /forums/images/graemlins/smile.gif After looking through the lens of an infrared camera for almost thirteen years now, i can tell you that I have seen VERY FEW shop electrical feeds that were overloaded. Yes, there IS a lot of connected load in shops, but the reality is that they are rarely used altogether, so even a 100-AMP dedicated shop service goes quite a ways. /forums/images/graemlins/tongue.gif When we re-wired our 100-year old Iowa farmhouse this last year or so I knew we'd have a shop to feed eventually so I asked for a 200 AMP service. The power company installed a 15KW transformer which is what they consider a 200 AMP service and in actuality it is only 125 AMPS at nameplate rating (AMPs X Volts = Watts). The drop to the main is also way undersized from what I have popping out of the building; mine was 2/0, their cable is #1 AWG. Power companies depend on the OUTDOORS to cool their stuff, so they fudge quite a bit on everything, /forums/images/graemlins/frown.gif whereas our stuff which is all in conduit has to be sized by the book. /forums/images/graemlins/tongue.gif It isn't unusual for the power company to load transformers to 1.3 times nameplate, and that's continuous use. /forums/images/graemlins/tongue.gif We used a 200 AMP DISTRIBUTION PANEL which is just that, a distributor to sub panels. The distribution panel has a 200 AMP main, and four breakers below that which feed two 100 AMP subpanels, and two fifty AMP subpanels. BGOTT's idea of using a pass-through panel and connecting to the bottom is good because it avoids taking serious power off some teensy little push-on breaker connection. it does, however, mean that your feeders beyond that point would need to be 200 AMP rated, all the way to the second panel, whereas our setup with a genuine distribution panel made for that job allows for the distribution breakers to be right there for us to use. I'm a believer in the MAIN/DISTRIBUTION-to-SUBPANEL approach, but then I do my own stuff and that does make a difference in costs, no doubt about it. /forums/images/graemlins/tongue.gif
/ 70 amp service #34
</font><font color="blue" class="small">( The power company installed a 15KW transformer which is what they consider a 200 AMP service and in actuality it is only 125 AMPS at nameplate rating (AMPs X Volts = Watts).)</font>
15KW: 125A @ 120V or 62.5A @ 240V. An electric Kitchen range
weighs in worst case just under 50A/240V and an electric water
heater just under 30A/240V. So we have already exceeded the
stated rating of the transformer and I haven't even fired
up the welder.
From this it would be reasonable to assume there is
sufficient thermal mass in the transformer and cooling oil
to absorb large short-lived excess draws and enough
surface-to-air cooling to withstand longer, more modest
overloads.
Aside from the voltage drop associated with exceeding the
transformer design limit, somebody is paying to heat the
works up there on the pole. Be happy it is on the utility
company's side of the meter.
I'd suspect the rating of the transformer is that which may
be drawn at an acceptable efficiency (read: cost) to the
utility company.
/ 70 amp service #35
Short of going too far on electrical theory...transformers are most often ( always ) rated in VA or KVA which take the voltage and amperage into consideration. Three phase gets a little weird by factoring in the square root of 3 ( 1.73 ).
I have a 25KVA padmount along my driveway placed by the power company on an underground 7.8KV ( 7800 Volts ) feeder. It good to have some connections /forums/images/graemlins/cool.gif.
/ 70 amp service #36
Actually, the power company claims 125A PER LEG at nameplate rating on that 15KW transformer. /forums/images/graemlins/tongue.gif These transformers are really strange since I'm not used to seeing a single leg of 7800 volts going into a transformer and TWO coming out at 240 volts. /forums/images/graemlins/crazy.gif Out on the west coast we always had one primary for each secondary on both single AND three phase. We don't have an electric range, but we do have an electric water heater and air conditioning, plus an electric dryer. If we did have an electric range, I estimate that I could run the whole works and still be able to weld in our shop. The power company definitely does take some liberties with the service factor on these pole-mounted transformers, but they must get away with it as evidenced by the very infrequent outages. I have no doubt that if I had everything electric and on all at once that there would be a definite voltage drop on the overhead service drop since it is the observed bottleneck in our entire system. In that case I would simply get a hold of the crew foreman over at the power company, and have them upgrade the drop to 1/0 or even 2/0 wire. /forums/images/graemlins/tongue.gif In actual measurement, we have 12 AMPs to the A/C condenser with an additional 6 AMPs to the circulator fan; 22 AMPs to the electric dryer on high heat; the water heater pulls about 24 AMPs. The TV pulls about 3 AMPs and miscellaneous lighting and kitchen stuff that cycles on-off adds another 9 or 10 AMPs. The HOUSE itself can get by nicely on a 100 AMP service as it is, but with an electric range, it would be crowding things a little; doable, but it would take some management. With a 200AMP service we end up with a good margin for the shop, even if we did have an electric range. 400 AMP services are not unusual if the house has zone A/C like they use out out west and maybe double ovens. The last month we were in CA our household electricity cost $343.00....that was in August with lots of A/C running.
/ 70 amp service #37
</font><font color="blue" class="small">( The last month we were in CA our household electricity cost $343.00....that was in August with lots of A/C running. )</font>
Ouch! /forums/images/graemlins/shocked.gif
SnowRidge
/ 70 amp service #38
/forums/images/graemlins/tongue.gif And that was with power outages in a rotating-block sequence.....YUK! It was just ONE of fourteen good reasons that we put together to get OUT of California. /forums/images/graemlins/frown.gif The year 2001 was all about GENERATORS! /forums/images/graemlins/tongue.gif
/ 70 amp service #39
Wow. I run a 200 acre farm (35 head of cattle, electric deep well, electric stove/oven, electric water heater, 1 window air conditioner, welder, assortment of power tools & small grain augers, etc.) and the entire place has a 60 amp service. Bill is $35-40 most every month. Coop power in southern MN is pretty good. Do wish I had a 200 amp feed & could branch to the outbuildings a little better.
--->Paul
/ 70 amp service #40
I know it's done. It would just make me nervous doing it with my investment and my personal belongings. I don't know a whole bunch about electricity but I think if I knew more I'd be more nervous about it than I am already. I do know that the vast, vast majority of residential fires in the US every year are electrical in origin. Maybe that's a part of it. /forums/images/graemlins/crazy.gif
Here's hoping your luck continues. /forums/images/graemlins/smile.gif
CHEVY DUALLY TRUCK BED (A65643)
CHEVY DUALLY TRUCK...
Snap-On Southern Thunder Edition 24-drawer tool box (A63689)
Snap-On Southern...
New/Unused 7ft Double Chain Sling (A65583)
New/Unused 7ft...
2022 JOHN DEERE 333G SKID STEER (A65053)
2022 JOHN DEERE...
Giyi XKH39 Mini 4-in-1 Bucket (A64126)
Giyi XKH39 Mini...
John Deere Gator TX4x2 (A62177)
John Deere Gator...