I keep seeing people running barely large enough generators right to the edge of tripping, instead of leaving some margin for motor starting and generator reliability . A consumer grade generator is not really built to operate continuous at "max rated" amperage.
Your generator and your electrical loads will last longer if the generator has power to spare instead of lugging the genny's guts out.
I also see people with little four, six or eight circuit transfer panels ??? It doesn't very much to install a interlock slider on a breaker panel. That way all the lights and receptacles will work on the generator. Just open the breakers to the electric stove and electric clothes dryer to prevent overloading the generator .
For the cost of the re-wiring and installation of a little 4,6 or 8 circuit transfer panel. When the FPE Stab-Loc panel had the main breaker failed. I just swapped in an entire 200 amp panel with a built in transfer switch. 18 circuits on the generator side so all lights, receptacles and well pump operates. Also installed the 100amp version in the daughter's house. There was a jackleg installed FPE Stab-Loc and a pony panel in the utility room there. The cut and past of the individual page did not format very well . Here is the link and look on page DE1-8 for the "All in One"
https://www.schneider-electric.ca/d...istribution/en/shared/catalogue/DE1.pdfNumber
Loadcentre Catalogue Number
https://www.schneider-electric.ca/documents/electrical-distribution/en/shared/catalogue/DE1.pdfTrim
Catalogue Number
Main Wire Size Al or Cu (AWG/MCM)
Standard QO
Tandem QO
3▼
QO403L100S
Included
12-1 Al or 14-1 Cu
12▼
24
QO312ML1
QOC16UC
4 - 2/0
20▼
40
QO320ML1
QOC24UC
4 - 2/0
24▼
48
QO324ML2
QOC30UC
4 - 250
30▼
60
QO330ML2
QOC30UC
4 - 250
42▼
60
QO342ML2
QOC42UC
4 - 300
Total Number of Circuits
Number of circuits available for (generator) critical loads
Loadcentre Catalogue Number
Main Wire Size Al or Cu (AWG/MCM)
Standard QO
Tandem QO
Standard QO
Tandem QO
4
8
CQO48M30DSGP
#14-8
4
8
CQO48M60DSGP
#8-2
18
36
QOGP3P3036
#14-8
18
36
QOGP3P6036
#8-2
40
80
18
36
QOGP3P604436200
#4-250
40
80
18
36
QOGP3P604436150
#4-250
40
80
18
36
QOGP3P604436125
#4-250
40
80
18
36
QOGP3P604436100
#4-250
QOョ Loadcentres and Circuit Breakers
QOョ Main Lugs Loadcentres - Type 1 Indoor
QOョ Main Lugs Loadcentres (1リ - 3W)
Mains Ampere Rating
30 70
100
125
200 225
QOョ Main Lugs Loadcentres (3リ - 4W)
Mains Ampere Rating
100 125 125
200 225
QOョ Generator Panel (1リ - 3W)
Mains Ampere Rating
Box Size (see page 16) 1
2
3
4
4
4
6
7
8
9
11
11
11
12
14
Box Size (see page 16)
5 7 8 10 10 12
Box Size (see page 16)
30 4 60 4 30 6 60 6
QOョ 疎ll-in-one SE Generator Panels
200 150 125 100
Service entrance approved.
● Will not accept QO-GFI or QO-EPD breakers.
✚ Maximum 20A QO-GFI breaker or AFI breaker.
▲ Maximum 70A branch breaker.
◆ Does not include a door. Order kit # QODK60-2.
▼ Shunt trip feature not available on any 3リ loadcentres.
12 12 12 12