Is this the t-stat you have https://customer.honeywell.com/resources/techlit/TechLitDocuments/68-0000s/68-0280.pdf
If so, look at installer setup # 0680 and 0690. Not sure if thats what you need, but it appears thats what tells the furnace when to start/stop based on t-stat temp. Weather you want it to control the temp aggressively (try as hard as it can to keep it right on the setpoint without going too far over/under desired temp......frequent cycling).....or a looser setting allowing a little more over/under
No, its actually this one - https://customer.honeywell.com/en-U....3.1.4.16&rank=1&v1=Sort.1.Product.Rank&asc=1
Two things. One is the stat may be in a spot where there is airflow directly from a register. That can cause short cycling. The other is that you have a larger air handler, which is good for efficiency, but has a potential problem. Assuming it is not a variable speed unit, it should have the ability to select one of 3 fan speeds. I would change (or ask the installer to change) the fan speed to the lowest setting. Assuming that the installer used a TXV valve, it will compensate for the lower air flow rate. Normally a larger air handler has a fan with a higher flow rate. Given the size and the fact that the unit is higher efficiency, I would slow the fan to reduce the effect you are seeing.
Paul
Its possible the T-stat may be "some" register air. There is a register on a perpendicular wall but not underneath the the T-stat.
It is not a variable speed unit. I kept my old oil furnace as back up and the whole system uses that indoor fan blower. It does have a speed setting and a few years ago it was adjusted. But now the sticker is gone that showed which wires need to be where for that fan speed. And what exactly will a slower fan speed do? There is a TXV valve on the coil because that or the first new coil was not working properly, hence the new coil install the second time they came out.
/ Any HVAC techs in the house? #23
Are you able to access the installer settings/options or did your installer lock you out of that?
I am guessing there should be some setting in the installer pages, but cannot find any info for that online?
/ Any HVAC techs in the house? #24
Brothers 1949 home or 2400 square feet had no central air or heat... just an old wall furnace and bedroom window box... several days at a time it can be over 100 and in the 90's for longer periods of time.
I went undersize due to only having 30 amps available... the entire 14 years until he sold he was the envy of his neighbors... we did spend extra installing the best ducts and making sure all was properly sealed... enen commercial metal ducts with add insulation in areas that would not be later accessible.. variable blower, 3 stage gas heat and oversize returns..
Very happy with that job and put the extra money into doing a first class install... he also planted a nice summer shade tree and we insulated and replaced all the windows...
His friend that sold us the unit said he could not put in a undersized unit... simply could not... now he will reference us on sales calls saying he has one customer that went undersized without issue.
/ Any HVAC techs in the house? #25
I sold my business a while back so I'm no expert, but With your system having old equipment mated to newer equipment could be the issue. The old blower may be moving too much air across the newer A coil. The air flow may need to be adjusted at the old furnace / air handler. It's best to have a load calculation instead of guessing the size of the unit. Your unit shouldn't be short cycling . you are using energy ,and not removing humidity from your home. Short cycling isn't good for you or your unit. JMO..
LD1- I can access the installer options. That is how I changed it from 5 cycles an hour to 3 . Last night when the load wasn't as great it seemed to cycle 3 times an hour.
Ok - some updates . Today is in the 90's and the unit is running longer periods of time BUT its only staying off for 5-6 minutes before coming back on.
I know I have insufficient return air. A second return was added a few years back right beside the blower motor. This helped quiet the air return upstairs as it was annoyingly loud. Now some techs are saying its bad for me to be drawing in so much basement air (basement is unfinished) which is affecting the efficiency of the unit. Some techs say the more air the better. Right now the basement return is partially blocked as the latest tech feels it would benefit the unit to draw in more upstairs living space air instead of alot of cooler basement air mixing in. It would allow the TXV to open up more and produce cooler air. Only thing now is the upstairs air return is slightly louder because its drawing harder.
Now what sparked my second call back to the company was, after the new replacement coil was installed we started the system and let it run. The house temp was about 77 degrees. We had a 22* temp split at the unit and 56.5* air coming out of my closest vent. I was very pleased. Now my Temp splits are 15-16* and I'm getting 59* air out of that same vent. I thought I had a problem because the numbers were falling.
They tell me when the unit has to work harder hence the 77* air in the house my temp splits will be greater. Once the house air stabilizes or the heat load is less, it is harder to get the big temp splits. IS this true? Kinda makes sense to me.
/ Any HVAC techs in the house? #27
A slower fan speed will result in a slower rate of change in air temp when the AC comes on. This will normally result in a longer run time. With a TXV valve the coil temp is maintained independent of load on the coil. Older orifice systems will have a range of delta temps as they deliver near full capacity when they run. TXV will automatically compensate.
paul
/ Any HVAC techs in the house? #28
you should not be taking return air from any space, other than living space. I would never pull return air from a non living space just to get more return air... this isn't helping you 1 bit ! Your basement return is killing your efficiency .... This company should have fixed your return air problem B-4 installing a unit...
Didn't you say in another thread that you trusted this company ?
/ Any HVAC techs in the house? #29
I disagree about basement air.
The basement is the coolest place in my house. Hotter return air makes the unit work harder.
My basement isnt finished, but is occupied. Kits toy room, laundry, etc. ITs not uncommon for it to be 60 in the basement and 80 upstairs (prior to ac). When I really dont need any cooling.....rather I need blending of the air to make the whole house average out at 70.
I have a basement return, its open to pull all that cool air it desires and blow it upstairs.
As to the temp swings, the hotter the return air, the greater the swing....but that dont equate to efficiency.
And when you said "once the house stabilizes the heat loss will be less".....
Not sure what you mean by that. IF its 95 outside, heat loss will be less at 77 than it will at 72.
The greater the difference in temp between the house and outside....the greater the heat transfer. So the hotter the house is, the less BTU's get transferred to the outside, The farther the spread, the greater the transfer rate. So keeping the house cooler, equates to faster heat loss with the same outside temps.
2022 THOMPSON PUMP 6X6S1 PORTABLE PUMP (A59823)
2022 THOMPSON PUMP...
2020 DRAGON ESP...
2025 JMR Single Cylinder Grapple Bucket Mini Skid Steer Attachment (A59228)
2025 JMR Single...
2025 BrushFox XHD-78HF 78in Hydraulic Rotary Brush Cutter Skid Steer Attachment (A59228)
2025 BrushFox...
Sterling AT (A61307)
2013 Ford E-150 Passenger Van (A59230)
2013 Ford E-150...