Went to check one of the houses I watch yesterday. First thing I do when I get there is open the cover on the standby generator and check the display for the last run time. Display showed the wrong time and date, and a bunch of red lights were on.
Flipped the manual start switch and nothing but a click. Threw my multi meter on the battery 12.9 v, flipped the switch again, click and voltage drops to less than 5. So I pulled the battery out and threw it in my truck. Got it home and threw my tester on it and instead of 550CCA, it was only 55! Going to head to NAPA today for a replacement.
Since the oil and filters were more than 5 years old, I’ll pick up new filters, oil and spark plugs and change them out too.
Generator is a Cummins/Onan with an air cooled Briggs Intek Twin. Looked up filters on NAPA $41 for the stinking air filter and $23 for the oil filter! Holy crap. Checked elsewhere and nobody is stocking both, including TSC.
ETA: it is a Briggs Vanguard not Intek.
The negative battery clamp split in half today. I did get it tightened up, but I’ll have to get that replaced.
Flipped the manual start switch and nothing but a click. Threw my multi meter on the battery 12.9 v, flipped the switch again, click and voltage drops to less than 5. So I pulled the battery out and threw it in my truck. Got it home and threw my tester on it and instead of 550CCA, it was only 55! Going to head to NAPA today for a replacement.
Since the oil and filters were more than 5 years old, I’ll pick up new filters, oil and spark plugs and change them out too.
Generator is a Cummins/Onan with an air cooled Briggs Intek Twin. Looked up filters on NAPA $41 for the stinking air filter and $23 for the oil filter! Holy crap. Checked elsewhere and nobody is stocking both, including TSC.
ETA: it is a Briggs Vanguard not Intek.
The negative battery clamp split in half today. I did get it tightened up, but I’ll have to get that replaced.
Last edited: