Use a vibrator :p Long chutes are a drag
That’s concrete humor?

I actually have 40’ (4-10’ pieces) of U shaped 22 or 24 gauge sheet metal shrouds for some coiling doors.
 
/ Starting my bridge!! #43  
Interesting build. What type of vehicle are you planning on driving across your bridge?
 
/ Starting my bridge!! #45  
Without knowing the wall thickness of the tube.....off the cuff....I'd say the max for that structure is about 2500# presently. Based on the fact that you are spanning a little shy of 20' and deflecting ~1/4" with ~1200# of ATV's.

There is FAR more that goes into engineering calculations.....but for anything but the shortest of spans (where stress/shear become a factor).....L/360 deflection is usually a pretty good rule to follow. That is the length in inches divided by 360.

So say your span is ~18'....thats 216".......and 216/360 is 0.600" deflection MAX. And since you are nearly half that with teh ATV's.....safe to say thats about half the max load that structure will handle.

Then of course you have to have sufficient decking to handle the wheel load of 2.5' crossmember spacing.

Also throw in the fact that the entire weight of the truck or tractor are NOT right in the middle at the same time. A full sized pickup has a lengthy wheelbase. But then you also have to account for dynamic load/stresses of the vehicle moving.

I would forget the aircraft cable and truss it with some rebar similar to whats pictured above but on the BOTTOM so it stays in tension. That will add tremendous strength. But dont just weld the ends at a small point where the rebar comes back to the bridge. Flatten it back out so you get a good 4" or so of weld. Some 3/16 x 2" flat would work too.

Whatever modification you make, slowly work the weight of the load up and keep an eye on deflection. Dont go past 5/8" or so
 
/ Starting my bridge!! #47  
How about jetting a pole down mid-span of your bridge on each side to support the weight in the center, we used to jet poles down in water all the time and always found that creosote was far superior than any cca pole in water.
 
/ Starting my bridge!!
  • Thread Starter
#48  
Without knowing the wall thickness of the tube.....off the cuff....I'd say the max for that structure is about 2500# presently. Based on the fact that you are spanning a little shy of 20' and deflecting ~1/4" with ~1200# of ATV's.

There is FAR more that goes into engineering calculations.....but for anything but the shortest of spans (where stress/shear become a factor).....L/360 deflection is usually a pretty good rule to follow. That is the length in inches divided by 360.

So say your span is ~18'....thats 216".......and 216/360 is 0.600" deflection MAX. And since you are nearly half that with teh ATV's.....safe to say thats about half the max load that structure will handle.

Then of course you have to have sufficient decking to handle the wheel load of 2.5' crossmember spacing.

Also throw in the fact that the entire weight of the truck or tractor are NOT right in the middle at the same time. A full sized pickup has a lengthy wheelbase. But then you also have to account for dynamic load/stresses of the vehicle moving.

I would forget the aircraft cable and truss it with some rebar similar to whats pictured above but on the BOTTOM so it stays in tension. That will add tremendous strength. But dont just weld the ends at a small point where the rebar comes back to the bridge. Flatten it back out so you get a good 4" or so of weld. Some 3/16 x 2" flat would work too.

Whatever modification you make, slowly work the weight of the load up and keep an eye on deflection. Dont go past 5/8" or so
This is why we love this place!!

I have multiple 50’ lengths of 3/8 crane cable (not aircraft cable). 5k capacity turnbuckles aren’t hard to get…..that’s where my cable idea came from.

The rebar/flat stock idea work for me as well……overhead welding isn’t my strong suit so that’s why I was shying away from welding under the bridge.


The decking….I was gonna build a couple different test fixtures to see what will hold the tractor/pick-up.

I was thinking of just throwing some c-channel/tube steel down where the wheels ride and wood plank the rest……this idea has me nervous if someone didn’t drive on the steel.
 
/ Starting my bridge!!
  • Thread Starter
#50  
How about jetting a pole down mid-span of your bridge on each side to support the weight in the center, we used to jet poles down in water all the time and always found that creosote was far superior than any cca pole in water.

This is my last resort. I have another bridge with poles/cross bracing/etc in the center. I’m trying to see if it’s possible not to use them.
 

Marketplace Items

2020 INTERNATIONAL MV607 4X2 26FT NON CDL BOX TRUCK (A59906)
2020 INTERNATIONAL...
2019 Krause 8005-30 Excelerator - High Speed Vertical Tillage - 30 FT Working Width (A61307)
2019 Krause...
500 BBL FRAC TANK (A58214)
500 BBL FRAC TANK...
GENERAC MAGNUM PORTABLE LIGHT TOWER (A59823)
GENERAC MAGNUM...
2023 JOHN DEERE XUV 590M S4 UTV (A59823)
2023 JOHN DEERE...
Bell B45E (A60462)
Bell B45E (A60462)
 
Top