Actually, I found this is the instruction manual from Lincoln.
"Using the following instructions, have a qualified electrician
connect this receptacle (NEMA 6-50R Type) to the power
lines at the fuse box. Three #10 or larger copper wires are
required if conduit is used. For long cable runs over
100'(31m), #8 or larger wire in conduit will be needed to prevent
excessive voltage drops. Fuse the two hot lines with 50
ampere super lag type fuses as shown in the following diagram.
The center contact in the receptacle is for the grounding
connection. A green wire in the input cable connects this
contact to the frame of the welder. This insures proper
grounding of the welder frame when the welder plug is inserted
into the receptacle. If a separate disconnect switch is
used, it should have two poles for the two hot lines and both
should be fused for 50 amperes."
"Using the following instructions, have a qualified electrician
connect this receptacle (NEMA 6-50R Type) to the power
lines at the fuse box. Three #10 or larger copper wires are
required if conduit is used. For long cable runs over
100'(31m), #8 or larger wire in conduit will be needed to prevent
excessive voltage drops. Fuse the two hot lines with 50
ampere super lag type fuses as shown in the following diagram.
The center contact in the receptacle is for the grounding
connection. A green wire in the input cable connects this
contact to the frame of the welder. This insures proper
grounding of the welder frame when the welder plug is inserted
into the receptacle. If a separate disconnect switch is
used, it should have two poles for the two hot lines and both
should be fused for 50 amperes."