In a nutshell, it improves the power factor of inductive loads (motors), to .95. So it should be able to make any non EnergyStar rated appliance operate more efficiently. I got a 350w motor that runs 24/7 (primary circulation pump for my salt water tanks), not to mention a butt load of other motors, all in non EnergyStar rated appliances that are more than 3 years old, so I might just have to give this device a try. At $300, it would pay for itself in 5 month it it saved me 15% a month.
It's basically a big capacitor that install by your breaker panel via a 20A breaker, much like how a whole house surge protector would (which this unit also provides).
I am still extremely skeptical. As an EE, I can tell you that power factor is important especially for power companies so they typically put in massive capacitor banks in attempt to get the power factor as close to 1.0 as possible. This means that the power they generate which is measured in KVA equals what they sell which is measured in KW. Since they bill you at the KW level, not KVA, I don't entirely understand how this product would save you money.
That being said, for the price, it is probably worth trying. However, with the amount of power you pull, you may want to consider upgrading to one of the larger commercial units. One benefit you would see is that when the generator is running, you would get more power out of it for what you pay in propane.
I to am an EE with 35 years experience in industrial and power. It is true that correcting power factor in a residential setting WILL save money. Most likely up to one dollar per year. This is due to the fact that high reactance (KVA) will result in higher current for the power used (KW). This means that the current is higher and some additional heating losses (I^2R) will occur in wiring. That said, it will only take a hundred or more years to recoup your investment.
On a genset, improving power factor may help, since poor power factor (inductive loads) may push up the current beyond what is needed, and the generator does not have a large reserve for excess current in the form of heavier wiring and excess iron in the stator. You may effectively get less than rated capacity out of the genny if your power factor is poor and you are running it near the full rating. So power factor caps on the generator may be of some small help.
paul
Makes sense. If such a device was truly able to get you a 15-20% savings, everybody would have one already.
Would the caps aid with the start up current draw of large loads? I think this 15kw gen-set will be border line as far as being able to start the compressor in my 5 ton A/C unit.
I think this 15kw gen-set will be border line as far as being able to start the compressor in my 5 ton A/C unit.
Might get the "hard start kit" for your compressor. That has a cap which makes it pull less power on startup.Makes sense. If such a device was truly able to get you a 15-20% savings, everybody would have one already.
Would the caps aid with the start up current draw of large loads? I think this 15kw gen-set will be border line as far as being able to start the compressor in my 5 ton A/C unit.
Might get the "hard start kit" for your compressor. That has a cap which makes it pull less power on startup.
Aaron Z
Is that more inrush to the motor or more inrush from the breaker panel?Actually a hard start kit will increase the initial inrush. It allows for a greater starting torque. Without a hard start kit, the compressor will start more slowly, allowing a longer time at high inrush current. The quicker current spike may assist with getting it started faster and possibly help with the genset.
![]()
Putting a current clamp on gives me a 18A reading per leg, so that's 36A @ 240V I believe, or 8640W. This would be with the unit already running. Not sure how I would capture start up current. Perhaps the label above would offer a clue?
I noticed that as well when trying to find that spec. Their 15kw portable is advertised as having 22.5kw surge, so I would imagine a whole house of same continuous rating by the same manufacturer would be similar.Do you know why portable gens list surge capacity and the stationary whole house gens do not?
Come to think about, that makes sense since one leg is the supply and the other return on a 240V circuit. Much like I would get the same reading on both the hot and neutral on a 120V circuit.The old electrician who taught me how to use a volt/amp meter advised to use the reading obtained from one leg of the electrical supply line to determine running amps. If he was right, your running amps is 18 not 36. A 36 amp running device would really make a power bill jump each month.
Come to think about, that makes sense since one leg is the supply and the other return on a 240V circuit. Much like I would get the same reading on both the hot and neutral on a 120V circuit.