The neighbor down the road called me this past Tuesday and asked if I might help him with an electrical problem that he was having.

Seems over the summer months he had used an older dehumidifier in the basement to keep things dry. The latter part of the summer the dehumidifier quit working as did half of the receptacles in the basement area.

Since I'm aware that most receptacles are connected daisy chain style the last receptacle in the basement that was still working would most likely be the place to start troubleshooting.

I removed the Bakelite cover plate after killing the power to find a melted area on a foam draft gasket about the size of a quarter. The wood paneling was also charred in an area about the size of a dime and the wires suppling power to the next receptacle were burnt completely off the receptacle. The receptacle itself fell apart in my hands as I was removing it from the single gang box. :eek:

Most likely this damage was a result of a loose connection and aggravated by the amp draw of the old dehumidifier. My recommendation was that the dehumidifier no longer be used, that he count his blessings, and that he say a prayer that evening thanking the man above that the home and possibly his life were spared from a fire.

I thought this might be a good story to share since it ended well. Most of the time we only hear about the unfortunate accidents that happen from day to day.
 
/ Electrical problem might have ended badly #2  
Did he move from plug to plug? Or did the line just short out all at once?

-Mike Z.
 
/ Electrical problem might have ended badly #3  
my neighbor wired up some extra recepticals. Pulled them off an existing junction box in the celing. Finnally got some real load on them (new compter and a space heater) and then all of a sudden POP! and that burnt electrical smell..... hmmmmm

im called in to help trouble shoot.

what i find? the connection in the junction box was bad. bad nutral twisting job inside the wire nut. my only guess is that over time the current draw = thermal expansion/contraction of the wires worked loose shorting to a hot.

compleately melted the the wire nut and about an inch of wire insulation. did NOT trip a breaker.
 
/ Electrical problem might have ended badly
  • Thread Starter
#4  
Mike once the damage occurred it killed a total of 4 receptacles in the basement. He had the dehumidifier plugged into the receptacle at the very end of the circuit. When it died he had enough sense not to plug it into another outlet.
 
/ Electrical problem might have ended badly #5  
L U C K Y.

Darn lucky. He should go buy a lottery ticket.

-Mike Z.
 
/ Electrical problem might have ended badly
  • Thread Starter
#6  
Hope some of that luck transfers to me, as I picked up a lotto ticket for myself. ;)
 
/ Electrical problem might have ended badly #7  
Loose connection = not gas tight and corrosion forms at the contact point.

Corrosion = resistance.

Resistance and current flow = heat.

Heat = accelerated rate of corrosion.

More corrosion = more resistance = even more heat.

We now have a positive feedback loop which soon accelerates to the point of combustion, and the circuit burns open. In most cases, the cycle ends with nothing more than a few burned up electrical bits. Unfortunately, sometimes there is a serious fire with all its consequences. Which you get is the luck of the draw.

In my experience this tends to happen most often on fully loaded circuits in damp evironments.
 
/ Electrical problem might have ended badly #8  
I had a similar experience with an outlet on our porch a few years ago. We kept smelling what seemed like a whiff of a dead mouse for a few weeks out there. There is just a dirt crawl space under it, so I figured that's all it was. After a while, I got sick of it and started sniffing around the walls and floor. I got to an outlet that stunk like that burnt bakelite. Funny, a few feet away smelled like dead mouse but right up to it was that disticnt smell of trouble. I pulled the cover and found the receptacle all but gone with only a few pieces of metal in there. Fortunately, the receptacle was inside a metal box. It looked like it contained the fire that was in there. :eek:

When something like that happens you do tend to count your blessings and give thanks that it was no worse. It also makes you double check your work in the future. ;)
 
/ Electrical problem might have ended badly #9  
MossRoad said:
... Fortunately, the receptacle was inside a metal box. It looked like it contained the fire that was in there....

Sorry to go off topic for a second, I am planning on re-wiring my 100+ year old dairy barn next year. Actually in a few months... I plan on using metal casings for the wires and metal boxes for the receptacles and switches.

Why don't houses use metal?

-Mike Z.
 
/ Electrical problem might have ended badly #10  
Plastic is cheaper and it doesn't conduct electricity? You can use metal in a house if you want to.
 
/ Electrical problem might have ended badly #11  
A breaker should have tripped or fuse blown before "wires suppling power to the next receptacle were burnt completely off". I'd strongly suggest your neighbor have his electrical system inspected by an electrician. It sounds like a higher capacity breaker or fuse has been installed on that line. No circuit containing outlets should have a breaker greater than 20 amps. Someone may have had a 30 or higher breaker in a drawer and put it in, trying to save the cost of buying a proper replacement. I don't think he's out of the woods yet.


PineRidge said:
The neighbor down the road called me this past Tuesday and asked if I might help him with an electrical problem that he was having.

Seems over the summer months he had used an older dehumidifier in the basement to keep things dry. The latter part of the summer the dehumidifier quit working as did half of the receptacles in the basement area.

Since I'm aware that most receptacles are connected daisy chain style the last receptacle in the basement that was still working would most likely be the place to start troubleshooting.

I removed the Bakelite cover plate after killing the power to find a melted area on a foam draft gasket about the size of a quarter. The wood paneling was also charred in an area about the size of a dime and the wires suppling power to the next receptacle were burnt completely off the receptacle. The receptacle itself fell apart in my hands as I was removing it from the single gang box. :eek:

Most likely this damage was a result of a loose connection and aggravated by the amp draw of the old dehumidifier. My recommendation was that the dehumidifier no longer be used, that he count his blessings, and that he say a prayer that evening thanking the man above that the home and possibly his life were spared from a fire.

I thought this might be a good story to share since it ended well. Most of the time we only hear about the unfortunate accidents that happen from day to day.
 
/ Electrical problem might have ended badly
  • Thread Starter
#12  
Mike it's #14 wire w/a 15 amp breaker at the panel. All the receptacles are also rated at 15 amps as well.

Don't think a breaker will trip unless an over-current condition exists. Loose connections can cause enough heat to start a fire without an over-current situation to the best of my knowledge.
 
/ Electrical problem might have ended badly #13  
PineRidge said:
Mike it's #14 wire w/a 15 amp breaker at the panel. All the receptacles are also rated at 15 amps as well.

Don't think a breaker will trip unless an over-current condition exists. Loose connections can cause enough heat to start a fire without an over-current situation to the best of my knowledge.
Absolutely. Think of the elements in a old style electric heater or a toaster oven. They glow red hot and don't draw more than 15 amps. Touch paper to one of those elements, and it will ignite.
 
/ Electrical problem might have ended badly #14  
SnowRidge said:
Absolutely. Think of the elements in a old style electric heater or a toaster oven. They glow red hot and don't draw more than 15 amps. Touch paper to one of those elements, and it will ignite.

Very good example. Thanks.
 
/ Electrical problem might have ended badly #15  
Would one of the newer Arc-Detection breakers have detected this?
 
/ Electrical problem might have ended badly
  • Thread Starter
#16  
Chris I would think that a good question for the inspector. Is he still actively posting?
 
/ Electrical problem might have ended badly #17  
PineRidge said:
Mike it's #14 wire w/a 15 amp breaker at the panel. All the receptacles are also rated at 15 amps as well.

Don't think a breaker will trip unless an over-current condition exists. Loose connections can cause enough heat to start a fire without an over-current situation to the best of my knowledge.

That's true. Perhaps the outlet was defective or installed incorrectly. Now I'd be worried about the condition of all the outlets in the house. Or at least the ones installed by the person that installed that one. Or the breaker could be defective.
 
/ Electrical problem might have ended badly #18  
I know the one on my porch appeared to have just a bit of the wire under the screw terminal... it was hanging on by just a thread of what was left of the solid wire. I wondered if it was not completely under the screw or the screw was not tight enough.
 
/ Electrical problem might have ended badly
  • Thread Starter
#19  
Moss in my case the solid wire was still wrapped completely around the screw on all the connection points.
 
/ Electrical problem might have ended badly #20  
PineRidge said:
Moss in my case the solid wire was still wrapped completely around the screw on all the connection points.
It doesn't have to be the terminals. It can be the where one of the plug blades and the receptacle contacts meet. If they do not make good electrical contact because of corrosion or other factors and a high current is drawn, it can go up in smoke.

I have personally experienced four of these failures and only one was due to a loose terminal.
 
 