I need to run wire in underground conduit for a run of 140 feet from a meter/panel (on pole) to a 200-amp subpanel on a house daughter is building. We are doing some of the work - the project is 'permitted'.
My calculations are that we can use 3/0 copper wire in 2" conduit - given the distance and amps. Three wires in the conduit - appropriately tape-tagged.
The meter and the subpanel are in, appropriately grounded, and the County inspector has signed off on both. The trench is being dug on Tuesday. I will be ordering schedule 40 2" conduit and two 2" x 36" sweeps (for each end) and will use schedule 80 coming out of the ground.
I am posting to confirm that the wire size (3/0) and conduit size (2") that I intend to use are correct - out of an abundance of caution - before I order everything. And seeking any other advice that may be helpful, e.g., re pulling the wire in consecutive 10' conduit sections, and laying in the trench. I have done this before but suggestions welcome.
I am not an electrician but also not a novice and am very aware of the need to be accurate and careful. I ran underground service to our home when I changed out the overhead service and have run underground service to sub panels on other buildings on the property and have - over the years - managed a number of electrical projects, always mindful of a need to be accurate and careful.
As always - this is my go-to resource. Appreciate any input.
   / Confirming Wire and Conduit size #2
You are pulling a ground wire also, I assume, since you said subpanel. The ground won't need to be as big but I don't know the charts for sizing that. That is going to be a brutal pull with copper. Hopefully one of the electricians will chime in @grsthegreat
   / Confirming Wire and Conduit size #3
For a 200 amp subfeed you can use either 4/0 4/0 4/0 1/0 Aluminum wires ( some locals allow 4/0 4/0 2/0 2 aluminum for primary feeders) usually xhhw rated in 2 inch conduit or you can use 3/0 copper. If you choose copper, youll need a loan.
Aluminum4/0 is currently $1.22 per foot
3/0 copper $4.85 per foot.
At 140 feet if it was me, id upsize the aluminum to 250 mcm to account for voltage drop. But then youll also have to increase pipe size to 2.5” you might be able to squeeze it into 2” if you install pipe and wire at same time, but it would be tight. But 140’ wont make much of a voltage drop issue on the 4/0. Probably not worth the added expense.
Absolutely no issue running aluminum feeders to subpanel. All utility wires are aluminum. Todays aluminum feeder wires arnt like your grandfathers wires.
Ive been an electrical contractor for 35 years, and have never run copper subpanel feeders. Ihave for things like hottubs and such, just not for subpanels.
Even on my own house. Everything feeding house and sub panels in outbuildings is aluminum. It is all aluminum in pvc conduit. I HATE direct bury.
My own house is 29 years old no issues ever.
You do have to run a ground with the hots and neutrals for all subpanels.
   / Confirming Wire and Conduit size #4
Also, if possible lay out the wires on ground and slip the conduit onto it one stick at a time and run it down wires. Youll hate trying to pull 140’ by hand.
I have a Greenlee wire puller myself, but i doubt anyone rents one of those.
Mine uses a cordless drill to exert 1,000# + pulling strength.
   / Confirming Wire and Conduit size #5
The only time we arnt required to run a ground with the feeder wires is if the meter was posted away from the house AND there is no panel or shut off device at the meter. This would allow 3 wires run to the house with the house hosting the first disconnecting device. This is only allowed in certain circumstances in my local, as fire departments want a disconnect at meter now days.
Thanks to everyone. Very useful information!
There will be shut offs at the meter panel - one main shutoff to shut off the power coming in from overhead to the breaker bar, and another to shut off the lines running from the meter panel breaker bar to the house subpanel.
The comments about needing a ground were valuable as I was not certain about that aspect and had not given that full attention.
I was concerned about using aluminum wire (based on older horror stories) so it is good to know that today that will work. Thanks for that. Clearly save a lot of money. I will check code to make sure that is okay - assume so. I will rethink this given this information.
BTW - the way that I ran wires through conduit to go in a trench before was 1) have extra help, 2) run the wire through the conduit one stick at a time (sliding the next stick all the way down and gluing - taking care to have cardboard or tarps laid out to prevent debris etc.) and leaving the initial pieces on top next to the trench 3) after I have done that - stick by stick - for the length of the run, I add the sweeps at each end (having calculated how much wire I need to leave out at each end for the requisite connections - and being generous) and matching their vertical rise so the sweeps are vertically parallel, 4) then attach the schedule 80 vertical pieces, 5) slip all into the trench with help and rope, and then - topside - size it all up and wriggle it into the panels. For smaller conduit I have laid it into the trenches leaving the last piece out with the end on a board running across the trench and then moving on down the line. I'll have to think about which way to do this.
I think the punch out at the meter panel is 2 inches max.
Again, Thank you all so very much.
   / Confirming Wire and Conduit size #7
That was how I did it, but I was also going 400' and as a result had huge conductors (alum, 500 mcm IIRC...hmmm it might have been even bigger than that...). I also used 20' sticks of 4" conduit. 20' for fewer joints.
You can use bigger conduit and then just step it down at the meter or panel with a fitting or two if you need to. Makes life easier.
One trick I used was to take one of those wobble-style deburring tools and run it around the inside of the conduit to knock off the sharp edge so it didn't gouge the insulation. I noticed it shaving the insulation on the first stick as it slid along, so on the next one I used the tool to chamfer the inside of the end of the tube on the end I was feeding through. Takes 2 seconds to run a quick zip around the tube. Worked like a charm.
Don't forget the antioxidant paste on alum connections.
   / Confirming Wire and Conduit size #8
Also, check your local power company. Here, we have to install expansion fittings between the ground and the power box. This allows for expansion and contraction of the pipe in summer or winter. May not be necessary in your neck of the woods.
I also deburr all pvc pipe. Sharp edge will damage wire coatings if pulling 1 stick at a time.
   / Confirming Wire and Conduit size #9
My only experiences with underground have been problematic due to water intrusion.
In Washington the direct burial PSE cable has been repaired several times but the conduit from the transformer vault to the basement panel became Niagara Falls during a heavy week of rain… vault is at higher elevation and filled with water and the conduit became the overflow.
In Oakland utility pole work damaged my conduit at ground level and rain water puddled and had a straight shot to my panel… at least panel was outside…
Having your panel or meter base flooded is never a good thing!
I used closed cell foam to seal in both cases and so far so good.
   / Confirming Wire and Conduit size #10
I'm no electrician. but have read about placing electrical wires underground/ in conduit, and consider heat dissipation and how it related to wire size
49" X 74" EXPANDED METAL RAMP GATE (A51247)
49" X 74" EXPANDED...
Scag Mower (A50324)
Scag Mower (A50324)
UNUSED CFG INDUSTRIAL MH12RX EXCAVATOR (A51247)
UNUSED CFG...
UNUSED FUTURE STP45 HYD BREAKER HAMMER (A51248)
UNUSED FUTURE...
2020 John Deere HPX615E Gator 4x4 Utility Cart (A51691)
2020 John Deere...