All correct, and a good explanation. But careful with confusing the word "phases" for "legs". Residential panels, with rare notable exceptions, are all single-phase. But we use two legs to make a phase, with a center tap (neutral) to split the phase.Because the neutral at the sub-panel may not be at ground potential.
This would be true if the load on the two phases in the sub-panel is not equal, so there is some current flowing in the neutral. With current flowing, and some small resistance in the neutral conductor, there is a voltage difference between the neutral buss in the sub-panel and the one in the main panel. Probably small, but some.
You want the ground busses in all panels to be a ground potential.
Single phase = 2 legs = residential
Three phase = 3 legs = utility & commercial
The only reason this matters is that there are actually two-phase systems out there. Was a lot more popular 100+ years ago, in fact I think only Philly and maybe Chicago have any two-phase buildings left today, but it's out there. I believe all 2-phase systems have the two phases at 90° to one-another, whereas three phase is usually at 120° between phases.