truckdiagnostics
Platinum Member
We put soft start on the geo compressor. Helped with starting amps. Maybe time to consider new well pump with a soft start. Then you can use smaller generator. Lot there would depend on age of your well pump.
Ive never have Seen a diesel generator that uses only 1 gal of fuel a day, and I致e been around generators for 20 years. I could sell a million of those. Heck I壇 cut the utility feed and power my house 24/7 at a cost of $2.50 a day
With a well, I壇 go with a minimum of 6500-7500 running. Besides, I doubt a 4000 watt unit will have a 4 wire 240 outlet to power the house. Ive never have Seen a diesel generator that uses only 1 gal of fuel a day, and I致e been around generators for 20 years. I could sell a million of those. Heck I壇 cut the utility feed and power my house 24/7 at a cost of $2.50 a day
Also - as with almost any equipment, it痴 good to have too much capability as opposed to too little, so if it were me, get a generator that is larger than the max you think you'll need.
We put soft start on the geo compressor. Helped with starting amps. Maybe time to consider new well pump with a soft start. Then you can use smaller generator. Lot there would depend on age of your well pump.
With a well, I’d go with a minimum of 6500-7500 running. Besides, I doubt a 4000 watt unit will have a 4 wire 240 outlet to power the house.
A 4,000 watt gen is only providing 16 amps at 240. Really hard on a well pump motor. Also the 4,000 watt units generally have a 120v 30 Amp rv outlet, not 240....at least the ones I’ve seen at Home Depot.I agree that something in the area of 6500 watts (continuous output rating) is a good size range to be in for a typical home in the Northern US, if you are willing to do some load management, you can get by without a large air conditioning system, and don't have a whole lot of heavy electrical loads (electric heat or electric hot water, for example). I get by with 5500 watts continuous with an acceptable (to me) amount of ongoing load management. Were it not for the starting current of the deep-well pump, I could get by without much ongoing load management at all. I just shut down non-essential circuits at the beginning of an outage. I'll generally leave the well pump off until needed, just to be on the safe side. I calculated that I'm probably OK as long as both fridge and freezer are not running (or especially, starting up) as the well pump starts, but I prefer to stay on the safe side. When I was running off a 4000 watt generator, I had to be much more active in my ongoing load management. Even then, were it not for the generator's unusualy large surge capability I may have struggled
I see a 240V outlet on just about every generator over about 3000 watts continuous or so. This is probably because there is not a commonly used outlet rated for more than 30 Amps (there is a 50A 120V NEMA standard outlet, but it's not very common). The common household outlets are rated for either 15 or 20 amps (generally 15 amp outlets on a 20 amp circuit breaker in most modern homes). So the generator would require multiple separate 120v outlets and cords to deliver that power. You just can't easily deliver more than that through one circuit.
Can get average kw loads from you electric bills. From those, I could tell that the Isuzu would be running lightly loaded most of the time, about 2.5 kw vs. 12.5 kw capacity.
Come on over and I will give you a demo. This gen set was purchased IN JAPAN with a load of yanmar tractors.
You can stand next to it and talk while its running.
Its both 3ph and single
3 cylinder engine
yanmar ag12s-2 - Google Search
A 4,000 watt gen is only providing 16 amps at 240. Really hard on a well pump motor. Also the 4,000 watt units generally have a 120v 30 Amp rv outlet, not 240....at least the ones I’ve seen at Home Depot.
Those pesky electric heat strips are my nemesis. Hate them with a passion. i use Generac load shed modules for them unless client wants to spend big bucks for a liquid cooled generator.One thing the electrician ran into when he was planning what to include in that 200 amp generator box was the backup heat coil for the heat pump upstairs. It's only 2 ton, but the backup electric coil was a bunch of amps. He rigged something with a couple solenoids that would run it off when the generator kicked on.
Have since changed out that whole unit, and the control allows you to lock out the coil: heat pump only all the time. Luckily, it runs this way fine down to around 10 F that we've gotten down to since then.
The ductless heat pump system for the basement has no backup coil. It's on the generator, too.
Ralph