Extension Cord for welder

/ Extension Cord for welder
  • Thread Starter
#41  
I got an electrician at work to hook me up with his supplier. I'll let them figure it out. I gave them my specs and I will not go above 6 gauge but if they tell me 10 gauge is sufficient then I'll tell them I want 8 gauge. It'll be 8 or 6 and at a savings of $30-40 I may as well end up getting the 6.
 
/ Extension Cord for welder #42  
Have you priced a breaker, wire and outlet for your garage? This may be your best option. It is a pain to use wife's oven outlet, door cracked, dirt, noise and bugs get in :mad: Been there and done that!:D I've found it to be cheaper to do it right the first time.
 
/ Extension Cord for welder #43  
So here is what the NEC book said in 1995. "Each welder shall have an overcurrent protection (breaker) rated or set at not more than 200% of the rated primary current of the welder" For conductors: "Conductors that supply one or more welders shall be protected by an overcurrent device rated or set at not more than 200% of the conductor rating"

The way I read that is your cord would need to be able to carry 1/2 of the 50 amp breaker rating or 25 amps, which would allow you to use a 10 gauge cord.

Kim
 
/ Extension Cord for welder
  • Thread Starter
#44  
Have you priced a breaker, wire and outlet for your garage? This may be your best option. It is a pain to use wife's oven outlet, door cracked, dirt, noise and bugs get in :mad: Been there and done that!:D I've found it to be cheaper to do it right the first time.

I've thought about it but don't plan on living in this house too much longer. My main breaker panel cannot support additional breakers. It has 6 double pole breakers. It is also on the opposite side of the house from the garage.

Yes, I'd rather do it right but I am not willing to sink $1000 into it and let it go to waste when I move in a year (I hope).

Kim: Both of those statements appear to be for the breaker and imply not to use bigger than a 100amp breaker in the case of a 50 amp rated load.
 
/ Extension Cord for welder #45  
My welder is rated at 230 amps and I use an extension made of #10 household heater wire. (red cable).
Face it, you probably won't use greater than 5/16 rods an generally only 1/8. and if you look at the current settings to use those rods and convert back to the amperage draw at 220volts you will find that #10 gauge covers your needs.

Now to err on the safe side I would ONLY use #10 as an extension and not permanently wired in the walls.
As in all cases be sure that the breaker is properly rated for the wire used as that is your protection.

With the setup described, a buddy once split his excavator bucket and repaired it using my rig. Probably welded for a solid hour non stop using 5/32 rod and the extension never even felt warm!
 
/ Extension Cord for welder #46  
Maybe best explained this way.
It is all in the watts drawn. Watts is voltage x amperage. A given rod uses X amps at the welder secondary and we know the amps range required for any given rod.
Most welders run in the 30/40 volts secondary X the current needed for a specific rod.
Convert that to watts and calculate what you need at 220 and you'll find that if you run 1/8 rods you can weld all day on a #10 extension. (well perhaps not 500 ft long due to voltage drop, but 20-30 ft should be no problem)
Just be sure that the proper rated fuse/breaker is used.
One downside might be that it be a bit more difficult to strike the ark at first if there is some voltage drop.
Shucks I have welded using 3/32 rod on a 24 volt 25 amp transformer. Tricky to do but the welds held.
 
Last edited:
/ Extension Cord for welder #47  
Welders commonly used transformers. Their output rating is not the same as their draw. Find out the maximum current draw and size the dedicated branch circuit wiring and overcurrent protection accordingly.
 
/ Extension Cord for welder #48  
This is something that gets recycled here periodically, so I'll just weigh in with my own experience. I have a Lincoln 180 wire welder. I've run it hard enough from time to time that it has shut down from exceeding the duty cycle. I have it on a 30 amp circuit with #10 wiring and have never tripped a breaker. I made up a 50 foot extension cord with #10 motor wire I bought cheap off Ebay and added ends. When the welder shut down, I checked the cord and could not detect any increased temperature at all. It would have to be a pretty big welder before I would worry about using my #10 extension cord. The NEC wiring standards established for wire running in enclosed spaces with constant full load where the heat builds up.
 
/ Extension Cord for welder #49  
Kim: Both of those statements appear to be for the breaker and imply not to use bigger than a 100amp breaker in the case of a 50 amp rated load.

Thats right. But it says to not use a breaker rated at more than 200% of the conductors ampacity. If the ampacity of a 10 gauge wire is 30 amps, 200% of that is 60amps, so 10 gauge should be OK for the 50 amp breaker he has. Am I reading that wrong?

Kim
 
/ Extension Cord for welder #50  
All of this sounds interesting and, at times, confusing. I still don't see the point of extending the welder power cords and having to lug a welder in and out of the garage when you can extend the welding cables much easier and leave the welder where it sits - unless you are using a wire welder.
 
Last edited:
/ Extension Cord for welder
  • Thread Starter
#51  
Qapla said:
All of this sounds interesting and, at times, confusing. I still don;t see the point of extending the welder power cords and having to lug a welder in and out of the garage when you can extend the welding cables much easier and leave the welder where it sits - unless you are using a wire welder.

The power cord that came with the welder is all of 6 feet long, not enough to even get into the garage. Why not get really long leads? Because 50 feet of 1/0 cable is $200 and that would only make me two 25 foot leads. I do still want longer leads but I will wait for a good price on craigslist.
 
/ Extension Cord for welder #52  
This is like the 4th post in this site that has debated welder circuits.
I am an electrical contractor and all i can say is were required to provide a #6 cord for a 50 amp rated draw per NEC requirements. For 100 foot run you dont need to worry about voltage drop.

Where the problem lies in on the manufacturers end. They arnt burdened by the NEC. Why else do you find lamp cord wire used on a light fixture that has 20 - 60 watt light bulbs burning. the manufacturers can care less. Same with welders. Ive seen new units with 50 amp rated nameplates that have #10 pigtail wires on them. A #10 wire is rated at 30 amp continuous load. The thing about a 50 amp welder, it will peak at 50 amps for 1/10 of a second during ark start...then it drops off drastically as welding continues. The NEC has entire sections allocated to derating factors on welders. Its a real mess. All i know is i have to ... by law.. wire welder circuits & welder extension cords RATED to the nameplate... not to what the pigtail is.
 
/ Extension Cord for welder #53  
Everyone is entitled to an opinion but lets not suggest the OP violate the NEC.

If you are feeding a circuit with a 50 amp breaker the wire needs to be sized for at least 50 amps and within reasonable limits bigger wire is better (no more than a few gauges bigger.) Otherwise the wire will burn up and set the house on fire before the breaker gets close to tripping.

Pat

The question was why could a welder use a smaller gauge cord than what the national electrical code requires for wiring a house. For that the NEC doesn't apply.
 
/ Extension Cord for welder #54  
grsthegreat said:
This is like the 4th post in this site that has debated welder circuits.
I am an electrical contractor and all i can say is were required to provide a #6 cord for a 50 amp rated draw per NEC requirements. For 100 foot run you dont need to worry about voltage drop.

Where the problem lies in on the manufacturers end. They arnt burdened by the NEC. Why else do you find lamp cord wire used on a light fixture that has 20 - 60 watt light bulbs burning. the manufacturers can care less. Same with welders. Ive seen new units with 50 amp rated nameplates that have #10 pigtail wires on them. A #10 wire is rated at 30 amp continuous load. The thing about a 50 amp welder, it will peak at 50 amps for 1/10 of a second during ark start...then it drops off drastically as welding continues. The NEC has entire sections allocated to derating factors on welders. Its a real mess. All i know is i have to ... by law.. wire welder circuits & welder extension cords RATED to the nameplate... not to what the pigtail is.

Thanks!
 
/ Extension Cord for welder #55  
Where the problem lies in on the manufacturers end. They arnt burdened by the NEC. Why else do you find lamp cord wire used on a light fixture that has 20 - 60 watt light bulbs burning. the manufacturers can care less. Same with welders. Ive seen new units with 50 amp rated nameplates that have #10 pigtail wires on them. A #10 wire is rated at 30 amp continuous load. The thing about a 50 amp welder, it will peak at 50 amps for 1/10 of a second during ark start...then it drops off drastically as welding continues. The NEC has entire sections allocated to derating factors on welders. Its a real mess. All i know is i have to ... by law.. wire welder circuits & welder extension cords RATED to the nameplate... not to what the pigtail is.


I agree with everything except the #10 at a continous 30 amps. For romex cable, sure. Not so much with 3 or 4 strand SO cable. 30 amps continous will burn the neutral.

I work for a generator company that provides distro along with cabling. We use 10/5 SO (90c) with our 21-20 plugs (20amps) even at a full 20 amps you can see the neutral cable charred inside the insulation.

Another thing to remember (for all the guys not electrical savy) is that a breaker has two purposes. It will trip when it heats up. A 50 amp breaker is a thermal breaker and is only good for 80% for a continuous load. It will only trip once it exceeds that 80% for an extended period. The other purpose is to provide a break point in case of a direct short (phase to phase or phase to ground). If you are using cable inadequate for the load, the breaker doesn't know, doesn't care.. So if the cable is on fire from over amperage, the breaker isn't going to trip until the insulation melts and two lines cross... We see it on a lot larger scale with our 400 amp rated 4/0 cable. The weak link is in the connection points (cam lock ends similar to stick lead extensions). If we are pulling 350-380 amps (digital breakers rated for 100% continous) and there is a weak connection point heat is created. We had a couple cam lock catch fire (just smoldering) at this years super bowl with only 200-220 amps on cable rated for 400...

Just keep that in mind.. Don't cut corners when it comes to electricity. No one here wants to see anything happen to anyones shop, house or barn
 
/ Extension Cord for welder #56  
I agree with everything except the #10 at a continous 30 amps. For romex cable, sure. Not so much with 3 or 4 strand SO cable. 30 amps continous will burn the neutral.

I work for a generator company that provides distro along with cabling. We use 10/5 SO (90c) with our 21-20 plugs (20amps) even at a full 20 amps you can see the neutral cable charred inside the insulation.

Another thing to remember (for all the guys not electrical savy) is that a breaker has two purposes. It will trip when it heats up. A 50 amp breaker is a thermal breaker and is only good for 80% for a continuous load. It will only trip once it exceeds that 80% for an extended period. The other purpose is to provide a break point in case of a direct short (phase to phase or phase to ground). If you are using cable inadequate for the load, the breaker doesn't know, doesn't care.. So if the cable is on fire from over amperage, the breaker isn't going to trip until the insulation melts and two lines cross... We see it on a lot larger scale with our 400 amp rated 4/0 cable. The weak link is in the connection points (cam lock ends similar to stick lead extensions). If we are pulling 350-380 amps (digital breakers rated for 100% continous) and there is a weak connection point heat is created. We had a couple cam lock catch fire (just smoldering) at this years super bowl with only 200-220 amps on cable rated for 400...

Just keep that in mind.. Don't cut corners when it comes to electricity. No one here wants to see anything happen to anyones shop, house or barn

???? For a 220-240v welder? If you are cooking the neutral you have got major problems. Something is trying to run on 120. CJ
 
/ Extension Cord for welder #57  
???? For a 220-240v welder? If you are cooking the neutral you have got major problems. Something is trying to run on 120. CJ

Amen, brother, just what was going to say. If the welder is powered by 220-240 then why is there any current in the neutral conductor? I suppose it is possible a panel lamp or maybe a fan could run on 120 but not take enough power to heat the neutral.

I think the poster related his experience and his observations are valid but they are for a different situation where 120VAC was being supplied so don't apply here.

Pat
 
/ Extension Cord for welder #58  
Here's what my manual for my Lincoln 255 MIG welder recommends. The 255 is about as big of a mig welder that I think you'll ever need. But I wouldn't rule out finding a Lincoln tombstone 250 or 300 amp stick welder for cheap.
cord.jpg

I think you'll be safe with 8 gauge wire, even for a large stick welder. I went with 6 because it's not that much more, the only draw back to larger wire is weight and stiffness, and if I ever need to make a second cord in the future so I can weld something further way (maybe can't get close enough to my garage) I can just plug it into the extension cord I already have. I'm sure it's over kill 99% of the time.
 
/ Extension Cord for welder #59  
Here's what my manual for my Lincoln 255 MIG welder recommends. The 255 is about as big of a mig welder that I think you'll ever need. But I wouldn't rule out finding a Lincoln tombstone 250 or 300 amp stick welder for cheap.
cord.jpg

I think you'll be safe with 8 gauge wire, even for a large stick welder. I went with 6 because it's not that much more, the only draw back to larger wire is weight and stiffness, and if I ever need to make a second cord in the future so I can weld something further way (maybe can't get close enough to my garage) I can just plug it into the extension cord I already have. I'm sure it's over kill 99% of the time.
 
/ Extension Cord for welder #60  
Amen, brother, just what was going to say. If the welder is powered by 220-240 then why is there any current in the neutral conductor? I suppose it is possible a panel lamp or maybe a fan could run on 120 but not take enough power to heat the neutral.

I think the poster related his experience and his observations are valid but they are for a different situation where 120VAC was being supplied so don't apply here.

Pat

Sorry, yes... On a typical 208-240 single phase welder, you should not even have a neutral, just normally two hots and a ground.

Since the thread was welder ext cords...I threw in some personal experiece as there are plenty of 110 buzz boxes and plasma cutters out there and DIY people don't always know the hazzards...

I should have been more clear with what I meant
 
Last edited:

Marketplace Items

KUBOTA X1140 CREW RTV (A52706)
KUBOTA X1140 CREW...
SKID STEER ATTACHMENT AUGER (A58214)
SKID STEER...
2005 Wacker Neuson PDT3A Portable Diaphragm Pump (A59228)
2005 Wacker Neuson...
2009 Arco Trailer T/A 6,000 Gallon Tank Trailer (A59230)
2009 Arco Trailer...
2020 DRAGON ESP 150BBL ALUMINUM (A58214)
2020 DRAGON ESP...
2022 Brush Wolf 4800X Severe - Duty Excavator / Backhoe Brush Cutter (A57024)
2022 Brush Wolf...
 
Top